Emersion/Gas Boiler problems

Options
  • 07-06-2006 11:36am
    #1
    Closed Accounts Posts: 199 ✭✭


    Living in the Wood and our emersion has never worked. Has not been a problem till recently when the gas boiler started playing up. The pilot light fires up for about a minute and then goes out. Cold showers begining to get to me now. Has anyone else had a similar problem and how did you get it fixed. Thanks in advance.


Comments

  • Closed Accounts Posts: 47 FVC


    after it shuts down, a code should display on the front of the boiler that identifies the problem. Then refer back to the user manual and take it from there.

    i would guess that low water pressure is causing the problem and the solution to this is in a previous thread


  • Registered Users Posts: 240 ✭✭Plenty


    Ditto to FVC response.

    We got the gas bolier serviced by Bord Gáis in April as we had problems with the water pressure as well. It's running smoothly now!


  • Registered Users Posts: 14,942 ✭✭✭✭loyatemu


    if the water pressure drops below 0.6 the boiler won't light - there's a valve somewhere in your house for repressurising the system (in mine its in the hotpress)

    as for the immersion not working - there may be a reset button on it - take off the cap and have a look (you might want to turn off the power before doing this)