  • Registered Users Posts: 4,748 ✭✭✭Do-more


    brickee wrote: »
    Not sure if this is right place - anybody got advice on insuring your home is covered for the future and what they must install at the start of the build like cabling would love to have the sound and vision in majority of rooms and help and advice appreciated.

    Regarding the smart homes preparation, if you do a search on this forum you should find a number of threads discussing it.

    Lots of things can run satisfactorily on wireless, but video and computer gaming really benefit from being wired so FWIW what I will do myself is to install two cores of Cat5e to the kitchen and each bedroom and 5 or 6 cores to the main TV all from a point under the stairs, I'll wire about 4 cores of Sat antenna cable from there up to the roof. I'll also wire the living room for 7.1 surround sound speakers in the walls and ceiling and wire the kitchen for a few ceiling speakers. Hopefully that should give me flexibility for the future to distribute sound and vision around the house.

    Beyond that it's only a question of where you want to stop, heating controls, video surveillance, alarm systems can all be wired if you want.

    invest4deepvalue.com



  • Registered Users Posts: 21 brickee


    fclauson wrote: »
    Unfortunatly I am finding the Price vs meeting regs is weighted on the regs side (this pushing up the price)

    To meet the current Part L means you have to spend money - sometimes more than you think is fare.

    I have a challenge to meet regs I am going to have to go some Solar plus HP - as just one or the other will not do - or I have to go lots of Solar plus large thermal store - again which is epensive.

    I am balancing to meet regs and not balancing to meet the heating demand of my property.

    Remember you have to do you DEAP calcs to show Part L - and the more you insulate the harder it is. My build is currently using just 4% heat demand agains the referece build in DEAP - but unless I can convience my local building compliance officer that I meet part L but not as shown in DEAP then I have to spend money on delivering renewables I will probably not actually use - which defeats the whole object :mad:

    Looks like I have alot of reading to do much more than I thought :mad:


  • Registered Users Posts: 1,691 ✭✭✭fclauson


    brickee wrote: »
    Looks like I have alot of reading to do much more than I thought :mad:

    never a truer word spoken :eek:


  • Registered Users Posts: 21 brickee


    Ok with plenty of patience I think I have a very rough estimate as to what my u values might end up being. I am not really to sure how accurate these will be because I am not an expert but can calculate area squared and cubed quiet accurate i hope;)

    I Received a 1.88 average U Value on one of the on-line calculators. Is this achievable. I will still be getting a BER accessor to go over it.


  • Registered Users Posts: 1,691 ✭✭✭fclauson


    You urgently need an expert :confused::confused::confused: - the max permitted U-value is 0.21 for a wall

    check the Part L regs for minimum elemental values


  • Advertisement
  • Subscribers Posts: 41,585 ✭✭✭✭sydthebeat


    brickee wrote: »
    Ok with plenty of patience I think I have a very rough estimate as to what my u values might end up being. I am not really to sure how accurate these will be because I am not an expert but can calculate area squared and cubed quiet accurate i hope;)

    I Received a 1.88 average U Value on one of the on-line calculators. Is this achievable. I will still be getting a BER accessor to go over it.

    looking at elemental u values is completely futile.

    the house needs to be assessed holistically.

    DEAP, and a good experienced BER assessor will save you hours of torment.


  • Moderators, Home & Garden Moderators Posts: 10,140 Mod ✭✭✭✭BryanF


    fclauson wrote: »
    You urgently need an expert :confused::confused::confused: - the max permitted U-value
    : depends on the house:)


  • Registered Users Posts: 4,748 ✭✭✭Do-more


    Just got word this evening that our planning has been granted without the need for any alterations. Huge relief!

    Here are some impressions of the house, very similar to an Irish dormer bungalow but with a 45 deg pitch on the roof and very small overhangs in keeping with the vernacular in the area.

    FrontHouse.jpg

    Front of house.

    Backhouse.jpg

    Rear of house.

    Here is a Google street view of our site, one of the last green field sites in the area within a stones throw of the beach, the site is 1050sqm and goes as far as the red bush, it's a divestment from the existing house you see in the background, so we are not frontline but only a 75m walk to a sandy beach.

    invest4deepvalue.com



  • Registered Users Posts: 5,422 ✭✭✭just do it


    Do-more wrote: »
    Just got word this evening that our planning has been granted without the need for any alterations. Huge relief!

    Here is a Google street view of our site, one of the last green field sites in the area within a stones throw of the beach, the site is 1050sqm and goes as far as the red bush, it's a divestment from the existing house you see in the background, so we are not frontline but only a 75m walk to a sandy beach.

    Congrats Do-more. Looking forward to following the build. I'd say race you but it will be an easy one for you to win!

    On the initial look on street view it looks like it could be in Ireland! Zooming out then you realise you're the same latitude as Derry! I'm sure you've described it before, but what is the climate like there?


  • Registered Users Posts: 4,748 ✭✭✭Do-more


    Cheers, looking forward to getting stuck in.
    just do it wrote: »
    what is the climate like there?

    Well my parents in North Longford have had more snow this winter than us so far! :D

    Generally more stable weather than in Ireland, much less rain all year round and considerably better summers most years but not absolutely guaranteed. It's about 4 good summers out of five here rather than the opposite in Ireland.

    The high last summer was around 30 deg C and the low last winter was around -17 deg C.

    Hoping that the weather will be kind to us, so that we can break ground in February but it could be the end of March.

    Looking at having the frame up early May if possible with a target of moving in by the end of August. But having been there before I know that that is probably being rather optimistic, especially as I intend to do quite a lot of the internal work myself.

    invest4deepvalue.com



  • Advertisement
  • Registered Users Posts: 21 brickee




  • Moderators, Home & Garden Moderators Posts: 10,140 Mod ✭✭✭✭BryanF


    1. why have you got sun room with windows facing north?
    2. have you carried out a provisional BER, what is your expected kwhr/m2/y
    3. how much insulation have you in the slab?
    4. and what is your heat source?
    5. have you or your architect taken the 2008 part L regulations and all the other Bregs for that matter into consideration
    6. have you dealt with any of your thermal bridges?
    7. are you aware of how poorly dormer bungalows can be as regards air-tightness. I would recommend you do a brief course. especially before you get to the first floor slab...
    8. I cant see any pop-ups for heat water or waste?
    9. your drawings need a F load of detail on them, for instance 100mm walls??
    10. and you could really make a few alterations to improve the layout - start with the GF WC, consider the GF flow a bit more and think out the light + improve solar gain provisions at GF & FF around front lobby..


  • Registered Users Posts: 21 brickee


    Hi ByranF

    1. Thats what the other half wants am thinking of blocking thru the north facing windows on the sunroom.
    2. I will be contacting a BER this week or next depends on when they are free to get upto speed.
    3. No insulation in the Slap will be putting insulation on concrete floor then screed, let us know what you think.
    4. Will be installing a Boiler Stove in the main Kitchen Dining area which is one room now.
    5. Will be installing a Boiler Stove in the Sitting room aswell one of those flush face ones built into chimney breast.
    6. I kept standard stainless steel wall ties and kept a decent size cavity 180mm.
    7. Got rid of the Dormers and we are installing Velux or Similar windows also because of cost and we have see views at front of house and think Dormer views are more limited.
    8. Waste and water can be hidden in subfloor and boreing holes out of the walls were needed because we knew we would be making changes to existing plan to make more use of space.
    9/10. Agree with your views on detail in that plan have 5 others with more detail that we have changed and changed again. We have already changed the walls regarding GF WC for instance got rid of hall by moving BED1 wall to meet stair wall got rid of closet and left entrance to bathroom that side.


    Hope that makes things better for me will keep posting thanks.


  • Moderators, Home & Garden Moderators Posts: 10,140 Mod ✭✭✭✭BryanF


    3. I think you should be considering 200mm of insulation, can this amount be provided?
    4. renewable requirements? solar? thermal store? have a read of fclauson's posts recently on his proposed house and Part L issues..
    5. back boiler? rads? central heating?
    6. wall ties is not what i meant by thermal bridges, think floor and wall junction, around opes, first floor slab level, how the flat roof extension connects, internal rising walls etc.
    7. air-tightness in dormer structures is a major problem, are you for instance going to wrap the FF slab with a membrane and seal to the FF internal Vapour barrier? on this point are you having wall vents or MVHR?
    8. each too their own.. i presume you've a sump installed?
    10. you are aware of the new part M 2010?


  • Registered Users Posts: 1,691 ✭✭✭fclauson


    BryanF wrote: »
    .... Part M issues....

    slip of a letter - he means Part L


  • Registered Users Posts: 21 brickee


    3. Can't provide 200mm cavity 180mm is my max have 2000 blocks built so won't be changing and the wall ties that I used imho would not be suitable for anything bigger.
    4. Will think about Solar or wind renewable energy when they give grants are pay a decent rate for electricity not used until then I am not aware of anyone policing this so not bothered.
    5. Boiler Stove using my own supply of willow timber turf and logs to heat rads.
    6. Will be making sure to the best of my ability and wallet that the house is as good as I can make it for thermal bridging are lack of thermal bridging.
    7. Talked to a BER lad today recommended a foam insulation that breaths and can have it between the rafters?
    8. Yes sump installed and another point on pre installed waste pipes if they leak for what ever reason the smell can be a problem and major issue and it does happen.
    10. Read the Part L regs but still a bit lost but getting there.


  • Moderators, Home & Garden Moderators Posts: 10,140 Mod ✭✭✭✭BryanF


    3. you asked me for my opinion on your floor:confused:
    4. i was referring to you renewable requirements under the BER


  • Registered Users Posts: 46,082 ✭✭✭✭muffler


    Guys, please quote the post that you are replying to otherwise the responses just look like s***

    Thanks.


  • Registered Users Posts: 21 brickee


    BryanF wrote: »
    3. you asked me for my opinion on your floor:confused:
    4. i was referring to you renewable requirements under the BER

    BryanF

    Thanks for your opinion and anybody else's for that matter cause I'm learning a bit more every day and is invaluable when lookin for info on the different stages of the build.

    I just think the BER requirements leave more questions than answers when you start and there is no real problem if you can follow the highest standard and that standard is going in the right direction towards the general area.:cool:


  • Advertisement
  • Subscribers Posts: 41,585 ✭✭✭✭sydthebeat


    brickee wrote: »
    I just think the BER requirements leave more questions than answers when you start .......
    brickee wrote: »
    .................. if you can follow the highest standard and that standard is going in the right direction towards the general area.cool.gif


    im not sure how you can marry those two statements.

    if the BER is throwing up questions as to what you need to do to comply with "minimum standards"....... and you dont know the answer to these questions, then theres no way of knowing what the "highest standards" are.

    In all due respect to tradesmen, do not expect them to versed in the 'highest standards'. There has to be a root and branch change from the 'cheap as chips' house construction which wa sdone during the boom... and many tradesmen have picked up some very bad habits because of this.


  • Registered Users Posts: 107 ✭✭Tifosi


    fclauson wrote: »
    Unfortunatly I am finding the Price vs meeting regs is weighted on the regs side (this pushing up the price)


    I have a challenge to meet regs I am going to have to go some Solar plus HP - as just one or the other will not do - or I have to go lots of Solar plus large thermal store - again which is epensive.

    I am balancing to meet regs and not balancing to meet the heating demand of my property.

    Remember you have to do you DEAP calcs to show Part L - and the more you insulate the harder it is. :mad:

    I am having the same issue's in trying to meet this Part L requirement, how do you intend to deal with this in the end?


  • Registered Users Posts: 1,691 ✭✭✭fclauson


    My current approch will be
    Solar
    Thermal Stove
    backed up by Gas LPG boiler (want clean heat source inside build)


  • Registered Users Posts: 107 ✭✭Tifosi


    fclauson wrote: »
    My current approch will be
    Solar
    Thermal Stove
    backed up by Gas LPG boiler (want clean heat source inside build)


    Thanks, I seriously need to rethink my approach in this regard, I was kind of hoping that I could achieve this with just solar.


  • Registered Users Posts: 1,504 ✭✭✭BarneyMc


    fclauson wrote: »
    My current approch will be
    Solar
    Thermal Stove
    backed up by Gas LPG boiler (want clean heat source inside build)

    What's a thermal stove?


  • Registered Users Posts: 1,691 ✭✭✭fclauson


    BarneyMc wrote: »
    What's a thermal stove?

    whoops - :D Thermal store not stove


  • Registered Users Posts: 3 toolittletime


    where can i learn more about Part L requirements


  • Registered Users Posts: 558 ✭✭✭beyondpassive


    where can i learn more about Part L requirements

    Here's some info to start with, looking at Part L 2011

    Part L Feb 10th Presentation_Integrated.pdf


  • Registered Users Posts: 3 toolittletime


    Here's some info to start with, looking at Part L 2011

    Part L Feb 10th Presentation_Integrated.pdf

    Tks for this


  • Advertisement
  • Registered Users Posts: 1,504 ✭✭✭BarneyMc


    Here's some info to start with, looking at Part L 2011

    Part L Feb 10th Presentation_Integrated.pdf

    Thanks beyondpassive. It's interesting to see the following as the optimal wall construct for a large, cavity wall, block built house:

    Walls - U Value of 0.14
    2x100mm block cavity wall with 275mm graphite infused bonded blown polystyrene bead.

    Is 0.14 achieved using standard or special wall ties?