U-Values

  • 18-01-2008 10:58am
    #1
    Registered Users Posts: 342 ✭✭


    I'll be using PIR insulation to give the following U-values on a standard block house
    Ground floor 0.21 W/m²K
    Cavity wall 0.22W/m²K
    Warm Roof 0.18 W/m²K
    Cold Roof 0.14 W/m²K

    Do you think I should bring these down further ?


Comments

  • Subscribers Posts: 41,942 ✭✭✭✭sydthebeat


    How have you calculated then slates??? did you use the SEI calculator?

    what construction are you planning??


  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    those are good values

    Step 1

    in context ...........

    DRAFT TGD 2007 Part L requires ( actual TGD 2008 expected any time soon )

    walls 0.27
    floors 0.25
    roofs 0.22

    SEI Passive house guide

    walls 0.175
    floors 0.15
    roofs 0.15
    with an almost total elimination of cold bridging ( very important when you insulate very highly )

    Insulation is the easiest measure to demonstrate a cost benefit gain

    Next sort windows ( TGD 2.2 SEI PH 0.8 )

    Step 2

    Ventilation / air tightness

    Consider HRV . ( Heat recovery ventilation whole house system (

    Factor in an air tightness test
    ( TGD n50<10 SEI PH n50<.6)

    Step 3

    boiler inefficiency + heating controls

    Step 0 ( first thing to do )

    Get a preliminary BER cert . Take advice from an assessor .
    Get a good architect or architectural technician to implement the strategy after that


  • Registered Users Posts: 342 ✭✭Slates


    sydthebeat wrote: »
    How have you calculated then slates??? did you use the SEI calculator?

    what construction are you planning??


    Standard Irish.......

    Flood
    150mm slad
    60mm PIR with 20mm upstand
    Radon
    Sand
    Hardcore

    Walls
    Render
    100mm Dense block
    40mm cavity
    75mm PIR
    100mm Dense block
    Render

    Warm Roof
    Slates
    50x25 battens
    50x25 Cbattens
    Breather membrane
    Trusses @ 600cc
    100mm Pir
    38x12.5mm pir/plasterboard laminate
    Skim coat


  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    Slates wrote: »
    Standard Irish.......

    Flood
    150mm slad
    60mm PIR with 20mm upstand
    Radon
    Sand
    Hardcore

    Walls
    Render
    100mm Dense block
    40mm cavity
    75mm PIR
    100mm Dense block
    Render

    Warm Roof
    Slates
    50x25 battens
    50x25 Cbattens
    Breather membrane
    Trusses @ 600cc
    100mm Pir
    38x12.5mm pir/plasterboard laminate
    Skim coat

    I get u values ( assuming lamda for ins of 0.023 ( kingspan )

    floor 0.38 - need to double insulation to floor to get 0.2

    wall 0.26

    roof 0.18


  • Subscribers Posts: 41,942 ✭✭✭✭sydthebeat


    just remember with these new revised u values that they are NOT target u values...
    they are minimum u values allowed when the dwelling complies with 40% efficiency compared to the MPCDER...

    In practise if your dwelling has these u values its very likely that it wont comply with Part L as it wont be 40% more efficient.
    In practise the current u values or better will have to be achieved.....


  • Advertisement
  • Closed Accounts Posts: 495 ✭✭ardara1


    sinnerboy wrote: »
    I get u values ( assuming lamda for ins of 0.023 ( kingspan )

    floor 0.38 - need to double insulation to floor to get 0.2

    wall 0.26

    roof 0.18

    Can't calculate the floor u-value without the floor area and exposed perimeter - can u post them for me.

    roof - 100mm unbroken might get a good value but I'm assuming you're putting it BETWEEN rafters? - this won't meet regs - about 0.35 at a guess -

    Give me the make-pu and I'll calculate them for you.

    Just ran 5 house type thru the new part L - NO wall below 0.22 passed

    The smaller the property is the more difficult to pass.


  • Registered Users Posts: 342 ✭✭Slates


    The U-values were given to me by the insulation provider................:eek:


  • Registered Users Posts: 342 ✭✭Slates


    Please see bellow calc's


    Construction typeElement: Solid Ground floor - Ground Floor InsulationSolid ground floorInternal surface emissivity: HighExternal surface emissivity: HighConstructionBridge DetailsThickness ThermalThermalPitchConductivity Resistance (º)(mm)(W/mK)(m²K/W)--0.040Inside surface60.01.4010.043Screed - cast (BS5250)60.00.0222.727Quinn Therm QF---Polythene,1000 gauge (0.25mm) (BS5250)--0.170GroundGround Floor DetailsCalculation method : EN ISO 13370 Perimeter: 48.60mArea: 121.00m²P/A: 0.402m Floor type: Solid floorEdge insulation: VerticalInternal surface resistance : 0.140m²K/W External surface resistance : 0.040m²K/WInsulation thickness: 25.0mmInsulation conductivity: 0.022W/mKInsulation depth: 150mmU-value - 0.21W/m²KU-value, Combined Method : 0.21 W/m²K (upper/lower limit 2.980 / 2.980 m²K/W, dUf 0.0000, dUg 0.0000, dUp0.0000, dUr0.0000, dUrc0.0000)(Correction for mechanical fasteners, Delta Uf = 0.000W/m²K)(Correction for air gaps, Delta Ug = 0.000W/m²K)


  • Registered Users, Registered Users 2 Posts: 39,671 ✭✭✭✭Mellor


    ardara1 wrote: »
    Can't calculate the floor u-value without the floor area and exposed perimeter - can u post them for me.

    roof - 100mm unbroken might get a good value but I'm assuming you're putting it BETWEEN rafters? - this won't meet regs - about 0.35 at a guess -

    Give me the make-pu and I'll calculate them for you.

    Just ran 5 house type thru the new part L - NO wall below 0.22 passed

    The smaller the property is the more difficult to pass.
    Thats one of the biggest downfalls to the BER system. As its based on a per m2 value. Smaller buildings suffer.
    It makes perfect sense that reducing, or keeping the area low will improve total energy used. But the per m2 value is higher due to constant energy users, ones not related to floor area. There may be other reason for the falloff also.

    Slates wrote: »
    The U-values were given to me by the insulation provider................:eek:

    The provider most likely provided a floor u-value based on average P/A ratio. But ardara is spot on, the actually floor value can't be calculated.


    I edited the post above to highlight perimeter, area and P/A ratio


  • Closed Accounts Posts: 495 ✭✭ardara1


    Hi Slates -

    Results were difficult to read.
    Theres a floor and a bit of pitched roof mixed up here -
    I noticed the calcs used a lambda of 0.022 for PUR - I think all boards are 0.023 - I got these results

    Wall - 0.23
    Floor - 0.22
    Sloped roof - 0.25

    Roof will definately need to be improved - I'd aim for
    Walls 0.20 Floor 0.18 - roof 0.11 (difficult on slope) - with these I'm able to get most designes to the new 40% improvement asked for in the new Part L

    Same values will work to get an A rated - BUT the detailing is CRITICAL - would need to use details that will achieve a Y-value of 0.04 (Basically drylining everywhere!)


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 39,671 ✭✭✭✭Mellor


    Would insulation on the outside of the rafers improve the detail by much. ie no cold bridges. Even say, 50/50 between and on top,.
    Do you think is viable to dry-line past the floor. To dryline, then install floor, breaking the drylining only at the wedges. I've been thinking over these details recently. Going to start a tread on details later today I think.


  • Closed Accounts Posts: 495 ✭✭ardara1


    Putting the full 100mm OVER the rafter would achieve 0.20 (Current regs) you'd need to be careful about wind upload and shear - the proper fixings should be specified (Helifix in Eng will do the calcs for you before supplying fixings)
    I was at a passive house in Germany recently where the put 160mm over and filled the 150mm rafter (The designer preferred it to be ALL over) - they called it a 'Thin' roof!!!!!


  • Registered Users, Registered Users 2 Posts: 39,671 ✭✭✭✭Mellor


    What support did the Germans have over the insulation. I imagine that has some sort of OSB before the battons. Seams to be common over there. I imagien it would greatly help support re uplift.


  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    My experience with roofers is they hate insulation over rafters - they "can't" find the structure to nail their tiling battens on to ......

    Same with copper / lead roofs - make the insulation layer "too" deep over the structural timbers and prepare to hear some onions peeling .....


  • Registered Users, Registered Users 2 Posts: 1,282 ✭✭✭sas


    Not to ask a stupid question, but surely the weight of the tils\slates would compress any insulation not specifically designed for this purpose?

    I just get the impression that the discussion is here literally about sticking sheets of kingspan on top of the rafters. Or am I jumping to conclusions.

    This is particularly relevant to me so I would really like to get more details on this.


  • Closed Accounts Posts: 495 ✭✭ardara1


    sinnerboy wrote: »
    My experience with roofers is they hate insulation over rafters - they "can't" find the structure to nail their tiling battens on to ......

    Same with copper / lead roofs - make the insulation layer "too" deep over the structural timbers and prepare to hear some onions peeling .....

    So true - it's difficult on site - so lets botch it!

    looking at the new part l - all roofs at 0.11 - things are going to have to change. How do you hit this with a 150mm rafter? - 125mm PUR between the rafters (allowing 25mm spave to allow membrane to sag) AND 100mm BELOW! They'll have the same problems hitting the rafters form the underside - and the residents will have to be vertically challenged


  • Registered Users Posts: 342 ✭✭Slates


    ardara1 wrote: »
    So true - it's difficult on site - so lets botch it!

    looking at the new part l - all roofs at 0.11 - things are going to have to change. How do you hit this with a 150mm rafter? - 125mm PUR between the rafters (allowing 25mm spave to allow membrane to sag) AND 100mm BELOW! They'll have the same problems hitting the rafters form the underside - and the residents will have to be vertically challenged
    What are the new part l u-values?

    Please see you pm


  • Registered Users, Registered Users 2 Posts: 39,671 ✭✭✭✭Mellor


    sas wrote: »
    Not to ask a stupid question, but surely the weight of the tils\slates would compress any insulation not specifically designed for this purpose?

    I just get the impression that the discussion is here literally about sticking sheets of kingspan on top of the rafters. Or am I jumping to conclusions.

    This is particularly relevant to me so I would really like to get more details on this.
    Rigid insulation is not easily compressed, the weight of the tiles is nowhere near the weight of a screed or full slab.


  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    ardara1 wrote: »
    looking at the new part l - all roofs at 0.11 -

    ..... know more then the rest of us A1 ? :confused::D

    just checked DOE site - no revised TGD yet


  • Registered Users, Registered Users 2 Posts: 890 ✭✭✭rejkin


    does anyone know a website where you can get updated u-values?


  • Advertisement
  • Subscribers Posts: 41,942 ✭✭✭✭sydthebeat


    rejkin wrote: »
    does anyone know a website where you can get updated u-values?

    Updated from what??

    if you are talking about the new Part l building regs (due to start for any dwelling applied for permission after 1st july 2008) then check the relevant thread....

    otherwise you need to give a bit more information....


  • Registered Users, Registered Users 2 Posts: 890 ✭✭✭rejkin


    yeah sorry,checked it and got the information,just needed accurate u-values for a college project


  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    u values are just part of a mix to achieve energy efficiency and limit co2 emmisions

    a good start point is this exercise on DOE website

    http://www.environ.ie/en/Publications/DevelopmentandHousing/BuildingStandards/FileDownLoad,15662,en.pdf

    9 different house types and measures ( including u values ) to achieve compliance with
    2005 regs ( 1 st 2 pages )
    current regs ( 2nd 2 pages )

    Very important also
    air tightness
    ventilation method
    detailing to eliminate cold bridging
    selection of heat source ( current regs require min amount renewable )
    user behaviour - current regs require end user information


  • Closed Accounts Posts: 8 mahoney.john


    Slates wrote: »
    I'll be using PIR insulation to give the following U-values on a standard block house
    Ground floor 0.21 W/m²K
    Cavity wall 0.22W/m²K
    Warm Roof 0.18 W/m²K
    Cold Roof 0.14 W/m²K

    Do you think I should bring these down further ?
    The following are some typical U-values of building components. (This may widely differ depending on the
    composition of each item, variations in conditions, variations in physical properties etc.)U Value of Glass = 5.68 W/m2degC (single glazing)U Value of a wall = 1.76 W/m2degC (Brick & Plaster)U Value of a Roof = 0.971
    W/m2degC (insulated concrete Roof Slab)

    It is apparent therefore a lower value in your building envelope saves you quite a lot in energy bills.