Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Air Tightness Specialist

  • 27-05-2008 3:57pm
    #1
    Registered Users, Registered Users 2 Posts: 689 ✭✭✭


    Hi,

    Has anybody here contacted an Air Tightness Specialist for their build. i.e. somebody to recommend a product to achieve the required airtightness, instruction on installation and then commission/test the system once it has been istalled.

    Please give details if you have.

    Who?
    Costs?
    Masonry/Timberframe?
    Satisfied with service?

    Thanks.
    Mike.


Comments

  • Closed Accounts Posts: 495 ✭✭ardara1


    Mike2006 wrote: »
    Hi,

    Has anybody here contacted an Air Tightness Specialist for their build. i.e. somebody to recommend a product to achieve the required airtightness, instruction on installation and then commission/test the system once it has been istalled.

    Please give details if you have.

    Who?
    Costs?
    Masonry/Timberframe?
    Satisfied with service?

    Thanks.
    Mike.

    Hi Mike - air tightness in a build can not be bought - it's down to detailing.
    There is an assumed performance of 7 at Q50 when using the Accredited details asked for in the new Part L regulations that are coming into force in July -

    U-values of arounf 0.22 in the wall 0.20 in the floor etc (as muted in the new part L) require a better detailing regime - Enhanced Details (Again UK)
    using these assume an air permeability of 4 at @ Q50

    Below 4 - and there probably isn't enough natural ventilation for the occupant - then MV is probably required.


  • Registered Users, Registered Users 2 Posts: 2,292 ✭✭✭RKQ


    <snip>they supplied me and advised on installation. They arrange a "blow door test". I was happy with their service and products - Solitex etc.The tapes are great!


  • Registered Users, Registered Users 2 Posts: 46,324 ✭✭✭✭muffler


    RKQ wrote: »
    Try <SNIP>, they supplied me and advised on installation. They arrange a "blow door test". I was happy with their service and products <SNIP>etc.The tapes are great!
    PM the OP with the details please.


  • Registered Users Posts: 25 Jill


    CAn you pm me the details also please


Advertisement