Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Concrete floor design

  • 29-06-2008 12:38pm
    #1
    Registered Users Posts: 25


    I am building an extension and have a question on the concrete subfloor/floor.

    The largest room on the ground floor will be 7M x 7M.

    I am using 100mm Kingspan insulation.

    What would be the min thickness slab necessary for a floor this size.

    The builder suggests compacted fill/ 75mm concrete slab / 100mm insulation /50mm screed.

    I am not an engineer but would think fill / 150mm slab / 100mm insulation / 75mm screed min.( I will be putting in UFH pipes).

    What would be the typical design?


Comments

  • Registered Users, Registered Users 2 Posts: 2,930 ✭✭✭Martron


    150mm slab is all i ever saw. you could probably get away with 100mm. depends on what type of traffic it will have. but 50mm screed should be grand


  • Registered Users, Registered Users 2 Posts: 1,550 ✭✭✭Slig


    150mm slab for a min 7M span:confused:

    Contact a pre-cast manufacturer, they usually have in house engineers to design these and give you a price so shop around. Alternatively if you have an engineer on board they could probably do up the calculations.


  • Registered Users, Registered Users 2 Posts: 39,615 ✭✭✭✭Mellor


    I think you mis read the OP Slig, its a ground floor, not first floor. At least, thats what it appears to me.


    Ryanrod, you right that you builders suggestion is too low. I would be going with your suggestion.
    I also disagree with Martron that 50mm screed is enough. For a bonded screed it is, but a floating screed with UFH needs to be bigger. 65mm min. 75mm to be safe, or as per manufacturers guidance


  • Registered Users, Registered Users 2 Posts: 1,550 ✭✭✭Slig


    Mellor wrote: »
    I think you mis read the OP Slig, its a ground floor, not first floor. At least, thats what it appears to me.


    Ryanrod, you right that you builders suggestion is too low. I would be going with your suggestion.
    I also disagree with Martron that 50mm screed is enough. For a bonded screed it is, but a floating screed with UFH needs to be bigger. 65mm min. 75mm to be safe, or as per manufacturers guidance

    Sorry your right, I misread it, 150 + 50 floating screed. any bigger than 100mm floating scred tends to crack especially if you have a large room.
    I would push for 100mm screed (on 100mm insulation on 150 floor slab) in this instance as the room seems be quite large.


  • Registered Users, Registered Users 2 Posts: 2,292 ✭✭✭RKQ


    150mm thick floor slab is minimum thickness in Building Regulations!
    100mm insulation and 65mm screen is fine, assuming ufh is oil or gas.

    I'd recommend a thicker reinforced screed if using geothermal ufl - cheap rate electricity at night, so heat slab at night to radiate during the day and minimise electricity use during day.( Thicker screen takes longer to heat up but also holds heat longer and can be "topped" up quickly)


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,550 ✭✭✭Slig


    RKQ wrote: »
    150mm thick floor slab is minimum thickness in Building Regulations!
    100mm insulation and 65mm screen is fine, assuming ufh is oil or gas.

    I'd recommend a thicker reinforced screed if using geothermal ufl - cheap rate electricity at night, so heat slab at night to radiate during the day and minimise electricity use during day.( Thicker screen takes longer to heat up but also holds heat longer and can be "topped" up quickly)

    I agree that the thicker slab will take longer to heat up but will also retain the heat longer. If using underfloor heating then response times will be slow anyway


  • Registered Users Posts: 25 ryanrod


    I think I will go for 150mm slab with UFH pipes tied to steel mesh.
    I will also be putting a couple of half inch pipes for possible solo rad if
    I ever need it.

    Thanks for your suggestions