Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Earthing

  • 11-10-2008 11:52am
    #1
    Closed Accounts Posts: 13,422 ✭✭✭✭


    i would of thought neutralizing was essential. If metal work in a house -eg kitchen sink comes in contact with a live cable then the earth rod alone would`t be a good enough connection to trip even a 10 amp mcb. And also the fault current path to earth only exists because the centre star point of 10kv transformer to 220/400v secondary side which is the neutral point is connected to earth with earth rods or earth grid. An individual earth rod at a house does little on its own - its connection to earth is quite poor on its own, but it is connected to all the other earth rods of other houses by means of the nuetralizing connection at each house, ie - all the earth rods are connected to each other in parallel by being connected to the neutral at each house and so they act as an earthing grid. And also the earth fault resistace is a lot lower by connecting the earth system in houses to neutral at the supply point.
    It does add a bit of a problem when neutral breaks at a point outside the house though.


«13

Comments

  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    i was in house recently where there was 350 volts between phase and neutral. there`s a brain teaser


  • Closed Accounts Posts: 1,712 ✭✭✭davelerave


    robbie7730 wrote: »
    i would of thought neutralizing was essential. If metal work in a house -eg kitchen sink comes in contact with a live cable then the earth rod alone would`t be a good enough connection to trip even a 10 amp mcb. And also the fault current path to earth only exists because the centre star point of 10kv transformer to 220/400v secondary side which is the neutral point is connected to earth with earth rods or earth grid. An individual earth rod at a house does little on its own - its connection to earth is quite poor on its own, but it is connected to all the other earth rods of other houses by means of the nuetralizing connection at each house, ie - all the earth rods are connected to each other in parallel by being connected to the neutral at each house and so they act as an earthing grid. And also the earth fault resistace is a lot lower by connecting the earth system in houses to neutral at the supply point.
    It does add a bit of a problem when neutral breaks at a point outside the house though.

    I think all the circuits are prot ected by an rcd in the uk system to detect fault current


  • Closed Accounts Posts: 1,113 ✭✭✭fishdog


    i would of thought neutralizing was essential
    In some rural areas in Ireland the TT earthing system is used i.e. neutralising is not permitted.
    If metal work in a house -eg kitchen sink comes in contact with a live cable then the earth rod alone would`t be a good enough connection to trip even a 10 amp mcb

    This is not correct. If it was the ETCI would simply not allow it. What you have to look at here is the earth fault loop impedance. If this is low enough the protective device can operate within the specified time (0.4 seconds for sockets or 5 seconds permenently connected equipment)

    By neutralising it can often be easier to get this impedance low enough. Sometimes multiple earth rods must be installed in a TT system to achieve the required earth fault current for the protective device being used, but it is possible to do it safley within the regulations. The ESB will determine if you neutralise or not.
    An individual earth rod at a house does little on its own - its connection to earth is quite poor on its own,
    This is why multiple earth rods are sometimes required in a TT system.
    And also the earth fault resistace is a lot lower by connecting the earth system in houses to neutral at the supply point
    This makes up part of the earth fault loop impedance and is the reason that most installations are neutralised.
    It does add a bit of a problem when neutral breaks at a point outside the house though.
    As you correctly point out neutralising has some serious disadvantages too. "Neutral inversion" can cause touch voltages in one installation to raise to dangerous levels if there is a neutral fault in an entirley seprate installation.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    earthing systems have to be connected to the neutral at some point, if not then rcd`s would`t work properly, because the earth fault current only flows because it eventually ends up flowing back to the star point on secondary side of ESB`s 3 phase transformer or to the neutral of single phase ones, which become neutral by the act of earthing one connection on secondary side. When a phase contacts the ground or earthed object, current flows not because its the ground, but because the earth forms pert of the neutral circuit.

    if a transformer was not earthed at secondary side it would be an isolated supply, like a shaver socket and there would be no earth fault current even if phase touched earth, might be tiny currents due to capacitance but thats more prevelant in medium to high voltage

    in practice the neutral is earthed at multiple points including at house meter position.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    Not true robbie - RCDs work on the difference between the phase current and neutral current. It doesn't matter where it goes, it'll still trip.

    Edit: sorry - I read that wrong, if the traffo star wasn't neutralised yes, there'd be no path but the line voltage could float up to high KVs and it would arc everywhere.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    well obviously its the difference between current in and back out that trips them. but to say it doest matter where it goes is a bit sort of vague,,, where do you think it goes



    well it does matter where it goes. go and buy a shaver socket. the secondary side wire through an rcd. and get either pole of the outgoing side of rcd and touch to earth, no chance it will trip


    and why is that?????


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    did`t notice you had seen i said about not earthing star point,

    but not earthing it would`t affect line voltages, there are plenty of installations with 3 phase isolated traffo`s with the secondary side star not earthed. last week a fella called asking why the earth loop impedence tester was`t workin properly, and thats exactly what it was,


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    if you don't earth some point on the system then the line voltage will float wherever it likes though.
    It's interesting because in theory you can touch a phase and nothing happens - unless someone else touches another one at the same time!


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    quote
    This is not correct. If it was the ETCI would simply not allow it. What you have to look at here is the earth fault loop impedance. If this is low enough the protective device can operate within the specified time (0.4 seconds for sockets or 5 seconds permenently connected equipment

    it is correct for sure. no single earth rod on its own provides much of a connection, its the collection at a group of houses. they form a collection by being connected to the neutral at each house.

    hammer one on its own into the ground in summer and try it,
    And the ETCI would`t allow it if was true???? well if the neutral breaks just to that house then the earth rod should keep the house working especially on light loads, but it wont, because one rod on its own does little


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    no the line voltages will remain constant whether star point is earthed or not, only the voltages across single phase loads will vary if they are not balanced loads and if no neutral wire is provided back to the star point from the loads, the neutral of all the single phase loads is a common point to that star point, if they are inbalanced and without a connection back they feed through each other and the voltages across each appliance or load will depend on their resistance. \if a shower was connected between L1 and neutral and a 100 watt light bulb between L2 and neutral, but there was no connection from that neutral to the supply star point then you`d have less than 10 volts across the shower and about 390 across the bulb, but the line voltages of supply would remain at 400 phase to phase


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    robbie, you can press the quote.gif button under someone's post if you want to quote them.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    the quote button, a sure its hardly a life changing event,

    have you tried the theory of touching a phase,


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    sorry man, just trying to help.

    Yeah but only on a small s/p traffo - I made damn sure it was isolated secondary first!!


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    a i was`t havin a go at ye,

    if you touch a phase you will feel nothing in dry conditions with boots or runners on, in damp conditions will feel a bit of a tingle or a good one, but if up to ankles in water then its dangerous, thats why the 110v traffos are around, centre tap earth so 55 volts to earth,

    the real dangers are phase and neutral hand to hand, or 2 phases,


  • Registered Users, Registered Users 2 Posts: 5,390 ✭✭✭DublinDilbert


    robbie7730 wrote: »
    no the line voltages will remain constant whether star point is earthed or not, only the voltages across single phase loads will vary if they are not balanced loads and if no neutral wire is provided back to the star point from the loads, the neutral of all the single phase loads is a common point to that star point, if they are inbalanced and without a connection back they feed through each other and the voltages across each appliance or load will depend on their resistance. \if a shower was connected between L1 and neutral and a 100 watt light bulb between L2 and neutral, but there was no connection from that neutral to the supply star point then you`d have less than 10 volts across the shower and about 390 across the bulb, but the line voltages of supply would remain at 400 phase to phase

    There's another very subtle problem with not earthing the star point in the 3 phase transformer.... If you don't earth the start point, and say one of the 3 phases some how connects to earth, no current will flow, but the following will happen:-
    1) all the neutrals in the system will rise up to 220v above ground
    2) the other two phases will also rise up 415V above ground

    The phase to neutral voltage will still be 220V so everything will still function.. but there would be serious safety issues...



    [From memory with a TT earthing system, do you not need to have a 300mA RCD protecting the entire board? (i've never ever seen this... ) ]


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    If it's isolated though you could sit in a bath and touch a phase, nothing would happen.

    Yeah the site traffos have saved many a life with the CTE.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    yes thats more or less what i said, although you could say its actually the ground thats rising 220 v above the neutral, the ground is actually becoming that phase that touched it, albeit not a great connection to it


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    [From memory with a TT earthing system, do you not need to have a 300mA RCD protecting the entire board? (i've never ever seen this... ) ]
    Yes, that's true afaik.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    yes its true, and i also never seen it, im not sure if you seen my earlier posts, i was saying what you said, neutralising is used for that exact reasons, if a line contacted the ground it would`t show until another phase contacted, or if neutral did, or someone got a bang from neutral,

    im at a loss as to how the other 2 phases to earth would go up to 415 though.

    in 10kv ESB system that is an isolated supply, if it was`t then every branch of a tree making contact would cause trip outs, but you would still be getting blasted bt touching a phase, theres one for ye


  • Registered Users, Registered Users 2 Posts: 5,390 ✭✭✭DublinDilbert


    robbie7730 wrote: »
    im at a loss as to how the other 2 phases to earth would go up to 415 though.

    Well the star point on the trafo will go to 220V above ground. The other two phases will then also rise up to what ever the phase to phase voltage is above ground...

    The other way of thinking about it is that a phase voltage is typically 220V greater than the star point. If the star point moves to 220V, the the phase voltage with respect to ground must also increase...


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    well if line voltage is 400 between phases then phase to neutral is 230 or 400 /root of 3

    if one phase touches ground on non neutralised neutral system then the ground is now 230v away from the neutral, and still 400 from each other phase assuming a good contact with the ground. Even if was neutralised the phase would still just sizzle on the ground, it would`t make a good enough connection to trip anything just lying on the ground assuming its an overhead ESB line etc

    the ground has no relevance and if a phase touched a person instead of ground then the person would be 230v above neutral and would be 400 volts difference still between the person and other phases.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    actually i just realised you wrote the other 2 phases go 415 above ground, your right,,, your taking a line voltage of 415 to start with,,, i was for some reason thinking you meant they would increase from 400 - 415

    my mis understanding, if you know what i mean


  • Closed Accounts Posts: 1,113 ✭✭✭fishdog


    Robbie:
    no single earth rod on its own provides much of a connection, its the collection at a group of houses. they form a collection by being connected to the neutral at each house.

    I never suggested that a single earth rod was enough for anything. You seemed to say that neutralising was essential, in fact it is not.
    i would of thought neutralizing was essential. If metal work in a house -eg kitchen sink comes in contact with a live cable then the earth rod alone would`t be a good enough connection to trip even a 10 amp mcb

    My point is:
    1) Neutralsiing is not essential. The ESB decide if you neutralise or not.
    2) Without neutralising a 10 amp MCB can operate as it should within the correct time.
    3) Without neutralising it is still possible to comply with the ETCI regulations.
    4) I never said that just one earth rod would be enough for a TT system, in fact I said
    Sometimes multiple earth rods must be installed in a TT system

    Robbie:
    And the ETCI would`t allow it if was true???? well if the neutral breaks just to that house then the earth rod should keep the house working especially on light loads, but it wont, because one rod on its own does little
    I dont understand what you are saying here. My point about the ETCI is that they would not allow any TT systems if protective devices would not operate properly. With a TT system if the neutral breaks everything using that neutral simply stops working, end of story. This is one of the advantages with a TT system.

    If you have a TN system (neutralised) and neutral inversion happens, you can then have a dangerous situation.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    on tt systems the entire installation is required to be protected by an rcd of 300ma differential.

    now if you have a live and neutral into a house on its own and the earthing within the house is connected to nothing but the earth rod, and a phase happens to contact an earth within an appliance, what is the earth fault path?? its path is down the earth rod and through the ground
    and back to the neutral via the neutral connection to earth at the ESB transformer. This fault path will not have a high current. The ten amp mcb was an example of the fact an earth rod forms a poor connection to the ground and a direct phase to earth fault will not draw a high current in a tt system. Thats why a tt system has RCD covering entire installation


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    if tt system is so good at tripping devices on earth fault why did those installations have 300ma RCD covering entire installation as a requirement.

    and if any ESB transformer is installed the 3 phase star point is always earthed. On single phase ones the 2 ends of windings has one connected to earth, the one deemed to be the lagging phase according to the 10kv 2 phases feeding it.

    Neutralising is simply connecting the neutral to earth. I have not seen any installation in my time being connected that doest have traffo neutral earthed.

    TT system refers to the actual house, and so depended soley on earth connection to the actual ground for its earth fault path. Its not a good low resistance path, so tn system came in,

    If you do a new installation and there is no connection between the house earth bar and the neutral at metering point then the earth loop impedence test will fail. I was actually at a house earlier this year where the neutralising point was left out, the ESB where there, and in their presense i had to neutralise the earth bar on the mcb panel.

    And the reason??? an external light had too big a bulb and melted the live into the earth. And the woman in the house was receiving small shocks from the sink. When i got there and connected neutralising cable between earth bar and ESB main fuse neutral the lighting circuit immediately tripped. And it took a while to then find the faulty light fitting.

    Now why did`t the lighting mcb trip before the neutralising was done??

    So this house was in effect in tt, but only because someone changed the MCB board and the neutralising wire did`t reach the earth bar in new board and they did`t even bother extending it. And a direct earth fault did`t trip a thing, which is why TT systems had 300ma rcd.

    All neutralising does is reduces earth fault path impedence.

    Its true on tt that if neutral breaks the earthing in house will not be as likelely to go up to the broken neutral voltage. But if the more likely phase to earth occurs as in house above, then tt will not trip except if has 300ma RCD covering it. Why the ESB would do it on one house and not another is new to me. And why not go with tt everywhere so. and where am i,

    and no neutralising is not essential for electrical systems, But it does help to show up faults. And as i said, try your earth loop impedece tester with no neutralising, it wont be up to ETCI standards for a new installation


  • Closed Accounts Posts: 1,113 ✭✭✭fishdog


    on tt systems the entire installation is required to be protected by an rcd of 300ma differential.
    You may be correct here, to be honest I cant remember for sure.
    if you have a live and neutral into a house on its own and the earthing within the house is connected to nothing but the earth rod
    (known as aTT earthing system)
    and a phase happens to contact an earth within an appliance, what is the earth fault path??
    It is as you correctly said:
    its path is down the earth rod and through the ground
    and back to the neutral via the neutral connection to earth at the ESB transformer.
    This fault path will not have a high current.
    Why???
    The fault current will depend on 2 things, the voltage with respect to earth (230 volts aprox) and the earth fault loop impedance.

    The earth fault loop impedance will depend on:

    1) The impedance of the phase conductor from the traffo to the fault (same as a TN system)

    2) The impedance from the fault to the earth bar (same as a TN system)

    3) The impedance of the earth cable to the earth rods (low because a 10 square is used)

    4) The impedance of the earth rods to earth (low because earth rods are being added until a suitable value is reached)

    5) The impedance from the earth rod through the ground back to the earth rods at the traffo. Again low because,

    = (resistivity of earth)x(distance)/(cross sectional area of earth)

    Because the CSA is so large this impedance value is very low.

    5) Impedance from earth rods at traffo to the star point, also very low.
    The ten amp mcb was an example of the fact an earth rod forms a poor connection to the ground and a direct phase to earth fault will not draw a high current in a tt system

    If the 10A MCB will not operate under fault conditions, why install it??

    You are correct in saying that a single earth rod can form a poor connection with the ground. I am saying that this is why with a TT system you often have to put down multiple earth rods to achieve a good connection with ground. This is why a TT systems are used in rural areas,you simply need space for lots of earth rods!


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Well your statement says your memorising stuff rather than analysing. A 10 amp mcb will trip on any short circuit fault, thats why its there. The earth fault current will take the path to earth rod if not neutralised as you say. But you can have 240 square to the earth rod and it wont help an earth rod make good connection to earth. The 300ma RCD is there for that reason, earth fault path is not reliable with just earth rods. Ask yourself why the 300ma RCD is used,,,, because its known the earth fault current wont be good. And why do the ESB use neutralising at all, becuase neutralising gives very low earth fault impedence.

    You can hammer down 50 earth rods and still wont be as good as a neutralising connection particularly if have weeks of dry weather.


  • Closed Accounts Posts: 1,113 ✭✭✭fishdog


    if tt system is so good at tripping devices on earth fault why did those installations have 300ma RCD covering entire installation as a requirement.
    If this is a requirement (and I think it is) I would guess that it is that if the earth cable were to break the RCD would offer some protection as a back up.
    if any ESB transformer is installed the 3 phase star point is always earthed
    True. But that does not mean a TT system can not be used!
    I have not seen any installation in my time being connected that doest have traffo neutral earthed.
    Me neither! That has nothing to do with TN or TT earthing system though.
    TT system refers to the actual house
    Correct
    Its not a good low resistance path, so tn system came in,
    Incorrect. It can be a very low resistance path. With the TN system it is simply easier to get a low resistance path, but it suffers from the danger of neutral inversion that the TT system does not suffer from. Why do you think the TT system is sometimes used??
    If you do a new installation and there is no connection between the house earth bar and the neutral at metering point then the earth loop impedence test will fail.
    With 1 earth rod only there is a high chance of this yes.
    I was actually at a house earlier this year where the neutralising point was left out, the ESB where there, and in their presense i had to neutralise the earth bar on the mcb panel.
    Because as you said the earth fault loop impedance was too high. The ESB decided that in that installation they wanted the TN system to be used. Just as in other areas they will say they want the TT system to be used. It is not the norm, but it happens.
    Now why did`t the lighting mcb trip before the neutralising was done??
    Because the earth fault loop impedance was too high. If this was low enough the MCB would have operated regardless of the earthing system.
    So this house was in effect in tt,
    Yes, without a good enough connection to earth!
    Why the ESB would do it on one house and not another is new to me.
    This is decided on several factors, but as you know they want TN in most places because multiple earth rods are often not an option.
    and no neutralising is not essential for electrical systems
    This is the opposite to what you said earlier, whice is why I responded in the first place!
    And as i said, try your earth loop impedece tester with no neutralising, it wont be up to ETCI standards for a new installation
    Then why do they allow it at all?? There are pictures of TT installations in the ETCI regs!


  • Closed Accounts Posts: 1,113 ✭✭✭fishdog


    Well your statement says your memorising stuff rather than analysing
    I am doing both! I am more than 10 years out of my time so I admit I can't recall every regulation! I did say that I thought you were correct about the RCD!

    I am in my final year of an electrical engineering degree, so I have to analyse a bit!

    I do know that the MCB will operate if the fault current is large enough and this depends on the voltage and the earth fault loop impedance. As you know, Ohm's law.
    A 10 amp mcb will trip on any short circuit fault, thats why its there

    No it wont. The fault current must be large enough. Not any current will do. In fact a B type MCB can take a current 1.5 times its rating and not trip for many hours. Look at the fusing characteristics and you will see.
    But you can have 240 square to the earth rod and it wont help an earth rod make good connection to earth

    You are 100% correct. This is why multiple earth rods often have to be used to achieve a good enough connection to earth in a TT system.
    You can hammer down 50 earth rods and still wont be as good as a neutralising connection particularly if have weeks of dry weather.

    In some situations it will not be as good as you say, but it will be good enough to comply with current regulations. TT also has another advantage as discussed earlier that we agree on.

    Are you suggesting that all TT systems in Ireland do not comply with the regulations???

    I agree that TN is the norm. But TT is used at times, is allowed, is shown in the ETCI Regulations and can give the required protection.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    yes i said as you keep quoting,,, i would of thought it essential, then said its not essential for electrical system to work. thats not the point here.

    you just said why are tt systems used,, have you seen any new instalations use it?

    and why is tn used at all so

    and earth is a low impedence because large csa,, but thats no good with very small earth rod area. You would need equally large surface area on earth rods,

    and why is 300ma rcd used

    and in that house i talked about fault in, it did`t trip on the light fitting earth fault because as you siad it did`t have a good low earth loop impedence. Is that not the point here. you wont get a reliable low impedence.

    The large earth cross sectional area sounds exactly like the stuff i heard as apprentice. High area low impedence. You should actually get a few earth rods and try it yourself. Get an earth rod and grip ameter and connect a 10 amp protected feed to top of the rod. If ground nice and wet you may trip it, but nice summers day not a hope

    Again why use RCD protecting the tt entire installation<<<


Advertisement