    when I plug in a 3.3kva transformer into some sockets it trips the circuit breaker - it works fine once the breaker is reset - what causes the trip?


Comments

  • Closed Accounts Posts: 9,463 ✭✭✭KTRIC


    That Optimus Prime is up to his old tricks again :rolleyes:


  • Closed Accounts Posts: 10,910 ✭✭✭✭RoundyMooney


    Inrush current most likely.

    Does it trip the relevant circuit MCB, or the ELCB (which is twice the width of the others FYI).


  • Closed Accounts Posts: 1,113 ✭✭✭fishdog


    This is normal, nothing to worry about. Large inductive loads such as a transformer will often do this. Here is a software simulation of an inductive load running for just over 1.8 seconds. The trace shows the current through the circuit. Notice how the current surges to about a peak of about 2 amps and then drops down and peaks to only 1 amp after about 1.5 seconds.

    This simulation is at 230 volts RMS and a frequency of 50Hz (similar to mains voltage)

    currentsurgeid3.png
    w800.png


  • Closed Accounts Posts: 1,712 ✭✭✭davelerave


    if you connect a load to the 110 side before you plug in the trafo it can prevent this happening.not a problem with industrial sockets just the domestic 'b' types


  • Banned (with Prison Access) Posts: 509 ✭✭✭bertie1


    jacaalis wrote: »
    when I plug in a 3.3kva transformer into some sockets it trips the circuit breaker - it works fine once the breaker is reset - what causes the trip?

    The breaker in a domestic installation is B rated , the load of the transformer is a C rated load. Nothing wrong only the domestic mcb is not suitable for the load being plugged in .