    Something that I am not familiar with

    How is this accounted for in the calculation for a wall element ?

    It is part of this particular detail :




    Thermal Transmittance (U-value) Calculation Report
    Calculation performed by Uvaluate, version 2.0.9 UK
    Xtratherm UK ltd
    Produced on 20-Jul-09
    Reference U value calculations
    Fax Unknown
    Site West of Bedford
    Assessed by Paschal Gallagher, Xtratherm ltd
    Comment All measurements must be verified on site
    If corrections for air gaps / mechanical fasteners are less than 3% of U (EN 6946), they are: Applied
    Element details
    PF Cavity Wall - XT/CW Plus L'weight Block 0.19 Dot & Dab
    Element type Exposed element
    Area [m2] 1
    U-value [W/m2 K] 0.22
    Layers Thickness Conduct'y Resistance
    [mm] [W/m K] [m2 K/W]
    Internal surface resistance 0.130
    Plasterboard 13 0.180 0.069
    Default air layer 15 0.096
    Concrete block Celcon Hi Seven 100 0.190 0.408
    Xtratherm XT Cavity Plus 60 0.021 2.857
    Cavity unventilated Low E 50 0.650
    Clay brickwork (outer leaf) 102 0.770 0.132
    External surface resistance 0.040
    Upper/lower resistance 4.512 / 4.383 W/m2 K
    Correction for air gaps / mechanical fasteners 0.000 W/m2 K
    Details of layers with thermal bridging or corrections for air gaps or mechanical fasteners are given
    below.
    Default air layer
    Is there repeating thermal bridging? Yes
    Bridging conductivity [W/m K] 0.43
    Bridging material Plaster adhesive
    Bridging thickness [mm] 15
    Fractional area of bridging [-] 0.2
    Correction for air gaps Not applicable
    Correction for mechanical fasteners Not applicable
    Concrete block Celcon Hi Seven
    Is there repeating thermal bridging? Yes
    Bridging conductivity [W/m K] 0.88
    Bridging material Mortar - protected
    Bridging thickness [mm] 100
    Fractional area of bridging [-] 0.08
    Correction for air gaps Not applicable
    Correction for mechanical fasteners Not applicable


    Also in the above would I be coorect in noticing errors for example in the underlined materials as in calculating the thermal resistance
    eg : Concrete block Celcon Hi Seven 100 0.190 0.408
    expressed as 0.100 / 0.19 = 0.408 (should be 0.526)

    Also this

    Plasterboard 13 0.180 0.069

    Whereas these are correct


    Clay brickwork (outer leaf) 102 0.770 0.132
    0.102 / 0.77 = 1.32

    Xtratherm XT Cavity Plus 60 0.021 2.857
    0.060 / 0.021 = 2.857

    This wall has according to those calcs a u value of 0.22
    Would you agree ?
    Where does the surface resistance come into play.


Comments

  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    Surface resistance ?
    Something that I am not familiar with

    How is this accounted for in the calculation for a wall element ?

    heat flow is slowed at the internal and external surfaces of an enclosing element

    the "rules" - as far as b regs are concerned are set out in BR 443 2006

    see page 7 for mandated figs for surface resistances

    http://www.bre.co.uk/filelibrary/rpts/uvalue/BR_443_(2006_Edition).pdf


  • Subscribers Posts: 41,644 ✭✭✭✭sydthebeat


    legs.... i think the concrete block resistance figure takes into account the mortar bridging factor as well.. thus the lower resistance....

    but on a point... is that an AAC block you are proposing to use??


  • Closed Accounts Posts: 32 legs_akimbo


    sydthebeat wrote: »
    legs.... i think the concrete block resistance figure takes into account the mortar bridging factor as well.. thus the lower resistance....

    but on a point... is that an AAC block you are proposing to use??

    if by AAC you mean an aereated concrete block (Quinnlite, Celcon, Thermalite) then yes Syd.
    This is not something I am working on but just something that I came across and caught my attention.