Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

insulating external walls of old house

  • 15-08-2009 8:13am
    #1
    Closed Accounts Posts: 2


    Hi,

    Looking at purchasing an old house that will need insulating, build around 1960's.
    Looking at two options:

    i) Dryline internally
    ii) Pump into cavity if possible, havent been able to check house yet.

    Has anyone any idea of approx costs for something like this.

    Its a 4 bed semi with converted garage circa 130 sqm

    Thanks


Comments

  • Registered Users, Registered Users 2 Posts: 1,569 ✭✭✭Builderfromhell


    Techie,
    Remember that SEI are offering grants for exteral insulation, dry lining as well as roof and new efficient boiler.
    There are loads of companies offering cavity fill insulation so it shouldn't be difficult to get a price.
    As for best system, a few photos would help.

    Good luck


  • Registered Users, Registered Users 2 Posts: 2,875 ✭✭✭MicktheMan


    Teckie wrote: »



    i) Dryline internally

    Be very careful ...

    My advice, don't do it.


  • Registered Users, Registered Users 2 Posts: 738 ✭✭✭hblock21


    MicktheMan wrote: »
    Be very careful ...

    My advice, don't do it.

    Why?


  • Registered Users, Registered Users 2 Posts: 2,875 ✭✭✭MicktheMan


    hblock21 wrote: »
    Why?

    In general, risk of (interstitial) condensation and mould growth is just too high.


  • Registered Users, Registered Users 2 Posts: 14,547 ✭✭✭✭Poor Uncle Tom


    Drylining inside is still an option, you just need to know what you are doing and the entire make up of the wall.

    Say, you're looking ar 100mm blockwork inner leaf, 60mm board insulation, 40mm clear cavity and 100mm blockwork outer leaf.

    If you wish to dryline then the general rule of thumb to prevent interstitial condensation is to insulate inside the wall with no more then half the thickness of insulation which is inside the cavity and ventilate tboth the room space and any dryline supporting timbers.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,875 ✭✭✭MicktheMan


    Drylining inside is still an option, you just need to know what you are doing and the entire make up of the wall.

    Say, you're looking ar 100mm blockwork inner leaf, 60mm board insulation, 40mm clear cavity and 100mm blockwork outer leaf.

    If you wish to dryline then the general rule of thumb to prevent interstitial condensation is to insulate inside the wall with no more then half the thickness of insulation which is inside the cavity and ventilate tboth the room space and any dryline supporting timbers.

    P.U.T., you're correct ... on paper.
    But the problems arise when
    a) the insulation in the cavity is not installed properly and you get thermal looping/cold bridging which negates cavity insulation effectiveness
    b) the occupants block up the hole in the wall vents when the cold winter winds blow


  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    Please expand on the problems Mick


  • Registered Users, Registered Users 2 Posts: 2,875 ✭✭✭MicktheMan


    sinnerboy wrote: »
    Please expand on the problems Mick
    Condensation / mould

    Localised areas (caused by ineffective insulation / coldbridging) where the wall temp behind the internal drylining falls below the dew point of the air. If room vents are blocked/non-existant then the RH rises and the corresponding dew point is higher. The condensate cannot easily dryout and then the mould starts growing behind the drylining.

    I just rarely if ever specify internal drylining because the risk of mould is too high. I see it very regularly in houses where scant regard has been given to building regs/ building physics and especially in existing/older (used to be) draughty houses who have had their old windows etc replaced with highly sealed pvc units etc. In no time at all mould appears on clothes, shoes, room corners etc etc not to mention the effect it is having on the building structure itself.


  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    Ah - but condensation will occur in any house which is not vented .

    Dry lining works in practice in 1000's of houses .


  • Registered Users, Registered Users 2 Posts: 14,547 ✭✭✭✭Poor Uncle Tom


    To get the ventilation element in a house right is very important, but I will not disregard drylining as an option just because someone cannot get another aspect of their building regulations correct. Drylining is a good low cost insulation alternative for older buildings provided ventilation is properly addressed.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,875 ✭✭✭MicktheMan


    sinnerboy wrote: »
    Ah - but condensation will occur in any house which is not vented .

    or inadequately heated houses.
    Yes SB you're right, to a point, but drylining masks the problem as condensation is at the back of the insulation. But the real problem arises when drylining is applied without any regards to ventilation.
    Heres the case I come across regularly. Existing house say 20 years old has never had a condensation/mould problem. Drylining is applied internally and within six months (over the winter) mildew smells start to be noticed in rooms which never had a problem before. Same family/living habits and same ventilation regime. This is the risk I'm speaking of.
    Sure, if you test airtightness and make appropriate changes to the ventilation system to account for increased condensation risk then yes drylining can be appropriate but how many "insulation contractors" (SEI registered for the grant) out there know how or have the equipment and training to be able to do such a calculation?


Advertisement