Balancing radiators

Options
  • 18-08-2009 9:08pm
    #1
    Registered Users Posts: 122 ✭✭


    If fitting TRV's to radiators do do you need to balance the radiators first or does it matter.
    Thanks


Comments

  • Registered Users Posts: 12,863 ✭✭✭✭crosstownk


    Yes - you'll need to balance first. Balancing ensures that each rad gets a similar supply of hot water so that all rads will heat up at (more or less) the same rate.


  • Registered Users Posts: 122 ✭✭oconnorw


    many Thanks


  • Registered Users Posts: 1,257 ✭✭✭Pete67


    It's always a good idea to balance the radiators, but you don't necessarily have to do it before you fit the TRVs. For example on a new system with TRVs installed you can remove the head from the valves which leaves them fully open. Then use the lockshield valve to balance each one, and refit the heads when finished.