Baxi Gas Boiler not working

  • 17-09-2009 11:13pm
    #1
    Registered Users Posts: 3


    I have a Baxi Solo 2 50PF gas boiler the fan led comes on but no pilot led follows.
    I checked for voltage at the Gas main and pilot valves but got nothing, looks like it might be the PCB. A new one is 300 quid. I don't want to spend that much on the boiler as it's fairly old. Anyone got any ideas? Thanks :)


Comments

  • Registered Users Posts: 45 L1979


    Had a similar fault a couple of years ago.
    Is the boiler clicking to try and ignite? you can see a slight spark through the little window.
    With mine it wasn't but i could hear a clicking from the main pcb.
    Which i found to be a dry joint on one of the relays, resoldered and jobs a goodin.
    Otherwise if you see a spark in the window you may need to clean the contacts to ensure spark is not impeeded.
    My fault occured on a friday morning so I purchased replacement PCB from HM before weekend and returned no questions asked Monday. No need for a cold weekend.
    Best of luck


  • Registered Users Posts: 171 ✭✭beldin


    Also a good crowd for pcbs is
    http://www.keeptheheaton.com

    Cheaper than buying locally and delivery is fairly fast. You just need the correct part number.


  • Registered Users Posts: 3 NRG_NRG


    Sorry I was away and only getting back online now. No L1979 I can't see any sparks. I was talking to a guy I met and he said to check the fan is running, even though the fan Led comes on, the fan may not be running he had a similar problem. He was right the fan was not turning I gave it a push and it ran for a couple of minutes very noisy though, I took the fan out but the connections on the pressure switch broke off, I could see nothing wrong with the fan so I connected it up to the mains it seem to run okay on the bench. Does anyone know, is the fan connected to the pressure switch and would a faulty pressure switch cause the fan to work intermittently. I'd appreciate any help thanks.


  • Closed Accounts Posts: 1 seancot


    hi ihave a baxi gas burner = 35/60 flame will ignite for afew seconds then go out
    and then repeats same thing
    app any help

    thanks sean


  • Registered Users, Registered Users 2 Posts: 11 pigeon 1982


    you shouldnt be going near the boiler unless your rgi regestered its the law, i know how you fix it you get an rgi engineer out to inspect it:P thats what there trained to do serves you right for breaking it more to many know it alls out there at the moment messin with gas!