Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

problem with baxi boiler

  • 08-01-2010 12:47am
    #1
    Registered Users Posts: 345 ✭✭


    have problem with baxi boiler only 5 years old and has been serviced regularly.
    first off i got a flashing error on 60 led so repressurised it was low under 0.5 cold now at 1.7 cold after represurizing.
    worked for a while but problem has reoccured any suggestions .thanks


Comments

  • Registered Users Posts: 647 ✭✭✭corcaigh1


    Hmmm..Checkout the giggling pin and the laughing shaft.


  • Registered Users Posts: 345 ✭✭curraghyid


    an expert


  • Posts: 0 [Deleted User]


    Sludge can get in to the low pressure safety device blocking it, so that when you refill it can't sense the pressure or the switch is just defective, the first i would think, but you would need a RGII http://www.rgii.ie/ anyway to identify, Gary.


  • Registered Users Posts: 345 ✭✭curraghyid


    hanks gary71. problem turned out to be the microswitch actuator stuck in on differential valve must have hapened when pressure dropped off.:D


Advertisement