    i replaced 2 ceiling rose light fittings in my dining room with 4 transformers and 12 spotlights. they are working fine but is the 1.5 sq cable feeding them enough?
    Thanks


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    you would run a separate 10amp cct. rather than 'up' the cable size if loading was an issue.

    you should be fine anyway.whats the total load there?.12*20watt?
    don't like to see the 12v 60va/70va trafos feeding 3 20watt mr16 spots as the bulbs can be 'upped' by accident later


  • Closed Accounts Posts: 394 ✭✭cantgetright


    M cebee wrote: »
    you would run a separate 10amp cct. rather than 'up' the cable size if loading was an issue.

    you should be fine anyway.whats the total load there?.12*20watt?
    don't like to see the 12v 60va/70va trafos feeding 3 20watt mr16 spots as the bulbs can be 'upped' by accident later

    12 spots, 3 spot per trafo, 20 watt mr11 bulbs. cant find any specs on trafo. You reckon they be grand once the bulbs are correct.
    cheers


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    trafos are usually marked with the VA rating.
    the electronic type usually have overload/short-circuit protection


  • Closed Accounts Posts: 394 ✭✭cantgetright


    M cebee wrote: »
    trafos are usually marked with the VA rating.
    the electronic type usually have overload/short-circuit protection

    30-60 va is stamped on trafo


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    prob electronic so.
    the only danger is the potential for overload later if bulbs are changed


  • Advertisement
  • Closed Accounts Posts: 394 ✭✭cantgetright


    thanks