Air permeability 5 is the magic number

Options
  • 25-02-2010 1:36pm
    #1
    Closed Accounts Posts: 5,433 ✭✭✭


    From

    http://www.environ.ie/en/Publications/DevelopmentandHousing/BuildingStandards/FileDownLoad,1647,en.pdf

    Air permeability of Q50/5 is a key datum .

    When using natural ventilation ( holes in walls )

    1.2.2.1 Where the air permeability is
    5m3/(h.m2) or greater, the minimum total
    equivalent area of background ventilators
    providing general ventilation should be 30,000
    mm2 with an additional 5,000 mm2 for each
    additional 10 m2 floor area above the first 70m2
    of floor area measured. For single storey
    dwellings situated at ground level or on any
    storey up to four storeys, an additional 5,000
    mm2 per dwelling should be provided. Where
    air permeability is less than 5m3/(h.m2) all
    equivalent areas stated above should be
    INCREASED by 40%.

    (I have edited the word "increased" to read in caps )

    When using MVHR

    1.2.3.2 The minimum capacity of a
    Mechanical Ventilation with Heat Recovery
    system should be based on the calculated
    general ventilation rate, adjusted to allow for
    air infiltration due to permeability of the
    building fabric. The calculated general
    ventilation rate is determined as the greater of
    a) 5 l/s plus 4 l/s per person, e.g. 25 l/s
    for a five person dwelling. This is based on
    two occupants in the main bedroom and a
    single occupant in all other bedrooms.
    This should be used as the default value if
    a greater level of occupancy is expected,
    then add 4 l/s per occupant.
    Or
    b) 0.3 l/s per m2 internal floor area, e.g.
    30 l/s for a 100 m2 dwelling.
    The adjustment to the calculated general
    ventilation rate to allow for air infiltration is
    0.04V (l/s), where V is the gross internal
    volume of the dwelling in m3.

    Where the air permeability is 5m3/(h.m2) or
    greater, the ADJUSTMENT IS DEDUCTED from the
    calculated general ventilation rate to give the
    minimum capacity of the Mechanical
    Ventilation with Heat Recovery system.
    Where the air permeability is less than
    5m3/(h.m2) NO DEDUCTION is made.

    (I have edited the words "adjustment is deducted" and "no deduction"to read in caps )


Comments

  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    ... if you plan an air permeability strategy to exceed Q50 /5 and you don't use HRV ..... your efforts will be rewarded by having enlarge your holes in walls . And you will be loose more heat .


  • Registered Users Posts: 2,489 ✭✭✭No6


    but take into account the transitional arrangements


    Transitional Arrangements
    In general, this document applies to works, or
    buildings in which a material change of use
    takes place, where the works or the change of
    use commence or takes place, as the case may
    be, on or after 1 October 2010. Technical
    Guidance Document F Ventilation dated
    2002, also ceases to have effect from that date.
    However, the latter document may continue to
    be used in the case of buildings
    - where the works or the change of use
    commences or takes place, as the case
    may be, on or before 30 September
    2010, or
    - where planning approval or permission
    has been applied for on or before 30
    September 2010, and substantial work
    has been completed by 30 September
    2011,
    - or a notice pursuant to Part 8 of the
    Planning and Development Regulations
    2001, has been published on or before
    30 September 2010, and substantial
    work has been completed by 30
    September 2011.
    “Substantial work has been completed” means
    that the structure of the external walls has
    been erected.

    At the rate things are going there will be no houses built under these regs at all!!!:eek:

    .


  • Subscribers Posts: 41,519 ✭✭✭✭sydthebeat


    these bloody transitional arrangements are ridiculous.

    just put a single date implementation, say 1st jan 2011.

    'substantial completion' before can be 2002 regs, anything after 2010. It never ceases to amaze me how convoluted DOE makes these things.