4 Sq NYMJ

Options
  • 13-08-2010 2:29pm
    #1
    Closed Accounts Posts: 11


    Does anyone know is it ok to use this to supply an oven and a hob from a cooker switch fed with 6sq twin and earth.
    thanks


Comments

  • Registered Users Posts: 463 ✭✭grousedogtom


    No for both oven and hob my advice would be 6 square , whats the total kw load of each appliance.


  • Closed Accounts Posts: 11 wquinn


    4.2kw for the double oven
    And 6kw on the hob


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    i'd normally run two 32amp circuits for a double oven and hob

    you'll prob get away with 1 32amp circuit allowing for diversity

    but you'll need a 6sq flex