cables size?

Options
2»

Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    so why should the meter be the 230v point
    Because:
    1) That is what the ETCI determine we should use for consumer volt drop calcs
    2) The ESB commit to supplying you 230 V (within a tolerance, I can't remember what the tolerance is to be honest)
    3) Only the ESB can select the cable sizes on their side of the meter

    The ESB can change tap settings on their transformers to compensate for the volt drop.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    Is it a different requirement when its outside the house?
    No, the disconnection times are the same.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    Because:
    1) That is what the ETCI require
    2) The ESB commit to supplying you 230 V (within a tolerance, I can't remember what the tolerance is to be honest)

    The ESB can change tap settings on their transformers to compensate for the volt drop.

    They can on their 38kv station transformers automatically for more regional load changes, but local estates is more fixed i`d say, but i take your point, i never suggested any different. But the ETCI saying our voltage point is the ESB meter as opposed to the MCB board?? Common sense is needed on that one. My original point was no need to take volt drop on MCB board tails for a 4 amp load, and i`d still stick with that, although you rightly say there may be a load already on. And also i suggested it would`t be taken into account when installing a 9kw shower, assuming 16 square tails of course.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    No, the disconnection times are the same.

    Yes but are the impedence requirements, just curious

    I suppose if the disconnection times are the same then the impedences must be.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    Yes but are the impedence requirements, just curious
    The impedance requirements are unchanged as the disconnection time is proportional to this.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    The impedance requirements are unchanged as the disconnection time is proportional to this.

    I know, i answered my own question there i think

    Although the tripping time is inversly proportional to the impedence possibly


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    But the ETCI saying our voltage point is the ESB meter as opposed to the MCB board??
    What I am saying is that you must calculate your volt drop from the ESB meter. This is because the DB may be some distance from there.

    For example:
    My background is industrial. A project that I have been working on the sub board is about 300m from the main distribution board and it is aprox 200m from the site transformer ( we have a 10 kV ring main on site). When sizing cables we allow for a 2% VD from the sub board.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    Although the tripping time is inversly proportional to the impedence possibly
    No. It is proportional. The greater the impedance the longer the time it takes to operate.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    Sorry Robbie, I have to put a child to bed!!

    Good to talk to you


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    What I am saying is that you must calculate your volt drop from the ESB meter. This is because the DB may be some distance from there.

    For example:
    My background is industrial. A project that I have been working on the sub board is about 300m from the main distribution board and it is aprox 200m from the site transformer ( we have a 10 kV ring main on site). When sizing cables we allow for a 2% VD from the sub board.

    Yes but the ESB meter in a domestic installation is usually a fair bit further from the mini pilar than from the MCB board, and the cable is the same size on both sides, my experience is all industrial more or less, so i see exactly what your saying, i was just thinking along the lines of it being a domestic installation and a tiny load.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    Sorry Robbie, I have to put a child to bed!!

    Good to talk to you

    Same here, always interesting which is the idea


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    robbie7730 wrote: »
    The fault impedence should be fine if the cable is within the 5 percent volt drop for the load scenario and the nearest size MCB is used.

    mceebe seems to have all the data on this. Is it a different requirement when its outside the house?

    afaik you can rcd the circuit if the Zl(loop impedance) was too high

    but it's preferable to meet the disconnection times


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    but it's preferable to meet the disconnection times
    If you want to comply with the regs you must meet the disconnection times.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    my mistake

    you have to meet the disconnection times

    you can supplementary bond(preferable)

    if not an rcd can be used for disconnection(according to rules)-but it's not standard practice afaik

    TT is all disconnected this way -obviously


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    No. It is proportional. The greater the impedance the longer the time it takes to operate.

    Yes your right again, too many glasses im lookin through tonight:)


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    robbie7730 wrote: »
    Although the tripping time is inversly proportional to the impedence possibly

    Ha ha i cant believe i wrote that bit, using boards with a few onboard is nearly as bad as texting in the same condition:)


  • Registered Users Posts: 301 ✭✭seaniefr


    M cebee wrote: »
    afaik you can rcd the circuit if the Zl(loop impedance) was too high

    but it's preferable to meet the disconnection times

    ZL fault loop impedance charts on page 316/317 ET101 2008
    example: MCB type 'B' 6 amp resistance measurement obtained would have to be under 6 ohms if measuring from f/b side with live & earth cores bridged at end of run. Value reduces down when size of mcb is increased. The value is the same for mcb's or rcbo's. If a 'C' type is used the value reduces to 2.5 Amps for a 6 amp mcb. So maybe locate a small mcb beside gates?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    i already corrected my error on the disconnection times:)

    anyway

    if you measure between L and E at the DB with the ends of the swa bridged that's your R1+R2 value(part of the fault loop)

    the unknown quantity is the external loop impedance measured at the DB

    the total fault loop impedance is the sum of the two(in theory anyhow)

    can't see any point to an mcb at end of the swa -in theory you could have a larger mcb at DB if you made the swa a 'distribution circuit' but the mcb on the final circuit would still be governed by the Zs at the end -so no benefit that i can see


  • Registered Users Posts: 27 e04bf097


    Also don't forget to pick the correct type of CB, it might be wise to use a C type as you will be powering motors that may require an inrush current.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    is there much inrush with those gate motors? i assumed there wasn't

    c type would send the Zl down more


  • Advertisement
  • Registered Users Posts: 280 ✭✭dave45dave


    Blah , blah , blah


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    can you spell any other big words:pac:


  • Registered Users Posts: 280 ✭✭dave45dave


    No but at least mine makes sense.


  • Registered Users Posts: 301 ✭✭seaniefr


    M cebee wrote: »
    i already corrected my error on the disconnection times:)

    anyway

    if you measure between L and E at the DB with the ends of the swa bridged that's your R1+R2 value(part of the fault loop)

    the unknown quantity is the external loop impedance measured at the DB

    the total fault loop impedance is the sum of the two(in theory anyhow)

    can't see any point to an mcb at end of the swa -in theory you could have a larger mcb at DB if you made the swa a 'distribution circuit' but the mcb on the final circuit would still be governed by the Zs at the end -so no benefit that i can see
    you could also factor in the need for pier lighting or any other use a power supply at a gate might get as for the external loop impedance it is a factor but is going to be a very small figure but i guess all of this means a very big cable! (or a few of them) just curious to know how the cable is going to be buried?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    dave45dave wrote: »
    No but at least mine makes sense.

    spit it out-what have to you got to say

    :pac:


    you seem to be just a sniper


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    seaniefr wrote: »
    you could also factor in the need for pier lighting or any other use a power supply at a gate might get as for the external loop impedance it is a factor but is going to be a very small figure but i guess all of this means a very big cable! (or a few of them) just curious to know how the cable is going to be buried?


    ya i figured after that's what you meant -the majority of the fault loop impedance is on the swa