Cold non-vented roofs - a discussion

2»

Comments

  • Subscribers Posts: 42,004 ✭✭✭✭sydthebeat


    I agree with you completely. There is a huge problem in this country with the way buildings are certified.The architect done the drawings but is narky if you ask for anymore detail.

    he didnt do much "drawing" if he never specified any insulation???

    is he an RIAI registered architect?


  • Registered Users Posts: 35 tobbslerone


    sydthebeat wrote: »
    he didnt do much "drawing" if he never specified any insulation???

    is he an RIAI registered architect?

    I am not sure about that.He has specified insulation in all areas but the roof. I think certification should be taken out of the hands of your architect anyway, its not working


  • Subscribers Posts: 42,004 ✭✭✭✭sydthebeat


    I am not sure about that.He has specified insulation in all areas but the roof. I think certification should be taken out of the hands of your architect anyway, its not working

    if he is certifying without a provisional DEAP assessment being carried out.... hes doing so blindly and dangerously.

    Ask to see the provisional assessment results which show the specification hes developed complies with the regulations, if he cannot provide this then id serious question his ability to provide final certification


  • Registered Users Posts: 35 tobbslerone


    sydthebeat wrote: »
    if he is certifying without a provisional DEAP assessment being carried out.... hes doing so blindly and dangerously.

    Ask to see the provisional assessment results which show the specification hes developed complies with the regulations, if he cannot provide this then id serious question his ability to provide final certification

    A BER will now be carried out before any works take place.
    Do you know if it is ok to put a foil back slab up against an airtight membrane.If i use 150mm of metac and a 50mm insulated slab then 40% is of insulation is on the warm side.Is this ok.I know the rule is 1/3 but it is difficult for me to do this.


  • Registered Users, Registered Users 2 Posts: 298 ✭✭tp25


    I have question about this roof and which approach to take (retrofit):

    Old:

    currently there are:

    - tiles similar to these: http://www.featurepics.com/online/Roof-Tile-Texture-791946.aspx
    - battens
    - felt membrane (white on the internal side and green on the external side, there are millions of little perforations dots like structures on the inner side of this membrane, it's softer on the inner side and harder on the external side) - I don't know the name of the top of my head.
    - 22cm rafters
    - no insulation between the rafters

    floor:
    truss joists (22cmX4cm every 60cm), currently 20cm isover/metac (itchy yellow product), foil backed plasterboard (there are bedrooms below that)

    New:

    Can someone advise if the following setup is advisable:

    - tiles
    - battens
    - felt
    - 15cm of Knauf earthwool in between 22cm rafters all way down until the concrete blocks (but not covering the eaves vents) and allowing 7cm of breathing space between Knauf and existing membrane
    - airtight membrane (tivek air guard control) or intello pro clima + sealing tape
    - 1''x2'' battens
    - osb boards over the battens, these will not be finished with plasterboard (less dust during the job than plasterboard slabs)

    floor:

    - retain existing 20cm of isover/metac,
    - battens (2''x4'')
    - osb 3 sheets 18mm
    - the junction of floor/roof to seal with sealing tape

    The following picture shows type of the membrane below the roof tiles as well as wall junction and eaves vents (on this picture there is no holes on this eave vent, however the next rafter would have holes in the eave vent).

    No HRV system, there is present ducting between the floor joist up to the roof level where special tiles accommodates the ducting (kitchen, toilets and WC)


  • Moderators, Home & Garden Moderators Posts: 10,145 Mod ✭✭✭✭BryanF


    what building regs are you working too? ill assume its the boom time ones and '08 or '11 don't apply?
    tp25 wrote: »
    I have question about this roof and which approach to take (retrofit):

    Old:

    currently there are:

    - tiles similar to these: http://www.featurepics.com/online/Roof-Tile-Texture-791946.aspx
    - battens
    - felt membrane (white on the internal side and green on the external side, there are millions of little perforations dots like structures on the inner side of this membrane, it's softer on the inner side and harder on the external side) - I don't know the name of the top of my head.
    - 22cm rafters
    - no insulation between the rafters

    floor:
    truss joists (22cmX4cm every 60cm), currently 20cm isover/metac (itchy yellow product), foil backed plasterboard (there are bedrooms below that)

    New:

    Can someone advise if the following setup is advisable:

    - tiles
    - battens
    - felt
    - 15cm of Knauf earthwool in between 22cm rafters all way down until the concrete blocks (but not covering the eaves vents) and allowing 7cm of breathing space between Knauf and existing membrane
    - airtight membrane (tivek air guard control) or intello pro clima + sealing tape
    - 1''x2'' battens
    - osb boards over the battens, these will not be finished with plasterboard (less dust during the job than plasterboard slabs)
    are the 2x1's for services? i assume this is a non heated space? if it is heated perhaps consider some insulation inside the rafters to bring up the 150mm to a more current regs standard. even 50mm in the service cavity would be something..

    floor:

    - retain existing 20cm of isover/metac,
    - battens (2''x4'')
    - osb 3 sheets 18mm
    - the junction of floor/roof to seal with sealing tape
    may i ask are you going to seal the area between the joists between lower walls and upper ceiling? a thick wood fibre insulation board might be a better option than osb, assuming you have the head height? 300mm is common enough, if we assume this attic space is non heated?
    The following picture shows type of the membrane below the roof tiles as well as wall junction and eaves vents (on this picture there is no holes on this eave vent, however the next rafter would have holes in the eave vent)
    shouldnt each rafter space have ventilation?


  • Registered Users, Registered Users 2 Posts: 298 ✭✭tp25


    BryanF wrote: »
    what building regs are you working too? ill assume its the boom time ones and '08 or '11 don't apply?

    Current ones
    The place was built during 2004/ 2005, completed in late 2005.
    BryanF wrote: »
    are the 2x1's for services?

    the 2x1's were purchased sometime ago and meant to be support for plasterboard, the plasterboard plan has been scrapped since
    BryanF wrote: »
    i assume this is a non heated space?

    the space under the roof will be occasionally heated
    BryanF wrote: »
    if it is heated perhaps consider some insulation inside the rafters to bring up the 150mm to a more current regs standard. even 50mm in the service cavity would be something..

    I thought 150mm of Knauf earthwool would suffice inside the rafters (allowing 7cm between insulation and roofing membrane for ventilation)?

    BryanF wrote: »
    may i ask are you going to seal the area between the joists between lower walls and upper ceiling?

    I'm not sure if I follow up ...
    BryanF wrote: »
    if we assume this attic space is non heated? shouldnt each rafter space have ventilation?

    this space will be occasionally heated, it may have sense that each rafter space have ventilation. Do I need to create few new openings in the eaves to allow for new vents?


  • Moderators, Home & Garden Moderators Posts: 10,145 Mod ✭✭✭✭BryanF


    tp25 wrote: »
    Current ones
    The place was built during 2004/ 2005, completed in late 2005.
    so yes is the answer
    the 2x1's were purchased sometime ago and meant to be support for plasterboard, the plasterboard plan has been scrapped since
    well then, why not install them and create insulation zone
    the space under the roof will be occasionally heated
    you seem to be splitting the insulation into two zones, one that is only occasionally heated, and not really providing current levels of insulation for either zone. id increase the floor insulation to 300mm mineral type min
    I thought 150mm of Knauf earthwool would suffice inside the rafters (allowing 7cm between insulation and roofing membrane for ventilation)?
    at '05 levels ye maybe, this wont meet current regs
    I'm not sure if I follow up ...
    you asked about air-tightness there's a flaw in your apprach: ie how do yo control the air-movement entering in the joist zone?
    Do I need to create few new openings in the eaves to allow for new vents?
    ye if i was overseeing the build you would


  • Registered Users, Registered Users 2 Posts: 298 ✭✭tp25


    BryanF wrote: »
    so yes is the answer

    yes this is correct
    BryanF wrote: »
    well then, why not install them and create insulation zone

    this is the plan to install them once insulation between the rafters and membrane on the warm side of insulation are installed.
    BryanF wrote: »
    you seem to be splitting the insulation into two zones, one that is only occasionally heated

    yes, am I going to create problems doing so?
    BryanF wrote: »
    id increase the floor insulation to 300mm mineral type min

    this would involve to re-build the entire floor from current 22cm depth of the joists to 30cm joists.

    I'm left with removal of current 20cm isover/metac. I would need to install 100mm PIR boards instead.
    BryanF wrote: »
    you asked about air-tightness there's a flaw in your apprach: ie how do yo control the air-movement entering in the joist zone?
    ye if i was overseeing the build you would

    this is something I tried to figure out, so far I didn't find answer
    BryanF wrote: »
    ye if i was overseeing the build you would

    I will create new vents where required.


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 10,145 Mod ✭✭✭✭BryanF


    tp25 wrote: »
    this would involve to re-build the entire floor from current 22cm depth of the joists to 30cm joists.
    I'm left with removal of current 20cm isover/metac. I would need to install 100mm PIR boards instead.
    that why i suggested a wood fibre board instead of osb maybe 100mm if the budget will stretch
    BryanF wrote: »
    a thick wood fibre insulation board might be a better option than osb, assuming you have the head height? 300mm is common enough,


    on the air-tightness between joists etc there are no easy solutions other than lots of type and membrane, but its a tough retro-fit. and its why there is such a need for good drawings, details and spec at design stage


    best of luck


  • Registered Users, Registered Users 2 Posts: 298 ✭✭tp25


    BryanF wrote: »
    that why i suggested a wood fibre board instead of osb maybe 100mm if the budget will stretch

    best of luck

    It's not easy to buy a wood fibre board here in Co. Wicklow. I will try to source elsewhere.

    Another problem is a bunch of electrical cables loosely laid over the existing floor (above bedrooms), thinking to use battens (12cm above the floor, so installing 100mm boards would leave gap of 12cm for services, however this approach would leave the services (electrical cables) under the insulation, this is a problem, however let's focus on the roof for the moment.
    BryanF wrote: »
    on the air-tightness between joists etc there are no easy solutions other than lots of type and membrane, but its a tough retro-fit. and its why there is such a need for good drawings, details and spec at design stage


    best of luck

    yes I agree there are no easy solutions.

    Would the following approach work on the roof?

    - roof tiles
    - counterbatten
    - breathable felt
    - 70mm ventilation gap
    - 150mm breathable insulation e.g. Knauf Earthwool Metstud 34 (MetStud 34 roll allows water vapour to pass freely through the insulation, therefore allowing the construction element to breathe. ) - 0.034W/m2K or earthwool building slabs which are 0.035W/m2K - 0.037W/m2K
    - proclima or similar VCL stapled onto the rafters
    - 50mm service battens filled with 50mm rigid breathable insulation
    - plasterboard finish over the battens

    I will deal with the floor once the roof is complete


  • Registered Users Posts: 33 Sandman777


    Hi guys..gonna jump into this thread to ask for some advice!

    Basically i have insulated my new build (2 story...9 months in) across the ceiling leaving a cold attic. I have 225 ceiling joists with the attic floored out with ply above!

    I have filled out the 225mm gap between the joists with:
    - 25mm kingspan cut to fit in between joists and kept up tight to plywood.
    - 200mm knauf earthwool between joists
    - Airtight membrane under joists
    - 62.5 k16 insulated board across the bottom of joists (incl. plasterboard)

    Also have HP and MHRV.

    My concern is should there be any gap left for ventilation in this detail?? Attic is ventilated at eaves as normal!

    Any advice appreciated!
    S


  • Registered Users, Registered Users 2 Posts: 2,875 ✭✭✭MicktheMan


    Sandman777 wrote: »
    Hi guys..gonna jump into this thread to ask for some advice!

    Basically i have insulated my new build (2 story...9 months in) across the ceiling leaving a cold attic. I have 225 ceiling joists with the attic floored out with ply above!

    I have filled out the 225mm gap between the joists with:
    - 25mm kingspan cut to fit in between joists and kept up tight to plywood.
    - 200mm knauf earthwool between joists
    - Airtight membrane under joists
    - 62.5 k16 insulated board across the bottom of joists (incl. plasterboard)

    Also have HP and MHRV.

    My concern is should there be any gap left for ventilation in this detail?? Attic is ventilated at eaves as normal!

    Any advice appreciated!
    S

    I don't see a need for ventilation


  • Registered Users Posts: 33 Sandman777


    MicktheMan wrote: »
    I don't see a need for ventilation

    Ok thats good! I came across this thread and was unsure if i had done the right thing!

    Thanks


  • Registered Users Posts: 67 ✭✭howman


    Syd, I'm not very well-informed on this, so please bear with me. A friend recently moved into his newly-built house, a dormer bungalow. He used a breathable "felt" (something like a TX membrane) and completely filled the space between his rafters with Icynene spray foam insulation. Does this make his method of construction a warm or cold roof? He didn't provide for any form of ventilation, didn't counterbatton and used an ordinary 2 x 2.5" slate lath and natural slate.

    do you not have the issue here of the face to the joists being exposed to the cold/moisture and the rest of the joist in a hot environment?


  • Advertisement
  • Subscribers Posts: 42,004 ✭✭✭✭sydthebeat


    howman wrote: »
    do you not have the issue here of the face to the joists being exposed to the cold/moisture and the rest of the joist in a hot environment?

    not only that, but the spray foam insulation pushes the felt outward creating a drainage channel directly over the roof joist... which is the worst possible location...


  • Registered Users Posts: 67 ✭✭howman


    sydthebeat wrote: »
    not only that, but the spray foam insulation pushes the felt outward creating a drainage channel directly over the roof joist... which is the worst possible location...

    right now Im looking at a curved Barn style roof.
    Curve is too tight for any pre-fabed type insulated panel.

    The roof is not exposed, therefore Im looking at insulating and sealing at ceiling level and going for a cold roof type design, with ventilation and no insulation
    will have the roof structure, with moisture barrier, plywood and corrugated panel

    what do you think?
    is this a little stone age?


  • Subscribers Posts: 42,004 ✭✭✭✭sydthebeat


    what do you mean the roof isn't exposed?? can you describe the structure more fully?
    where will the insulation layer be?


  • Registered Users Posts: 67 ✭✭howman


    auto correct kicked in there so not sure what point I was making! :)

    insulating at ceiling (floor of attic space) and air sealing at ceiling level

    the roof structure - beams, plywood, cross battens and moisture barrier with corrugated steel panels on top
    this is in it's early stages

    just going through design with builder


  • Subscribers Posts: 42,004 ✭✭✭✭sydthebeat


    howman wrote: »
    auto correct kicked in there so not sure what point I was making! :)

    insulating at ceiling (floor of attic space) and air sealing at ceiling level

    the roof structure - beams, plywood, cross battens and moisture barrier with corrugated steel panels on top
    this is in it's early stages

    just going through design with builder

    sounds fine, just ensure adequate cross ventilation


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,819 ✭✭✭✭galwaytt


    howman wrote: »
    right now Im looking at a curved Barn style roof.
    Curve is too tight for any pre-fabed type insulated panel.

    The roof is not exposed, therefore Im looking at insulating and sealing at ceiling level and going for a cold roof type design, with ventilation and no insulation
    will have the roof structure, with moisture barrier, plywood and corrugated panel

    what do you think?
    is this a little stone age?

    Who told you it was to tight for a prefabricated roof panel - where did you check ??

    Ode To The Motorist

    “And my existence, while grotesque and incomprehensible to you, generates funds to the exchequer. You don't want to acknowledge that as truth because, deep down in places you don't talk about at the Green Party, you want me on that road, you need me on that road. We use words like freedom, enjoyment, sport and community. We use these words as the backbone of a life spent instilling those values in our families and loved ones. You use them as a punch line. I have neither the time nor the inclination to explain myself to a man who rises and sleeps under the tax revenue and the very freedom to spend it that I provide, and then questions the manner in which I provide it. I would rather you just said "thank you" and went on your way. Otherwise I suggest you pick up a bus pass and get the ********* ********* off the road” 



  • Registered Users Posts: 1 newbuild__2014


    Hi Folks,
    I don't work in the industry and therefore don't know the details and would really appreciate a second opinion on some things. I am currently building a new bungalow with converted attic rooms. I have a contractor that is doing the build for me and they are planning to spray the roof with insulation soon but reading this post I am now slightly concerned.

    The make-up of the main roof is: (it is a cut A frame roof)
    -Slates
    -2x1 baton,
    -felt (I am not sure if it is breathable or not but will find out)
    -150mm rafters filled with with 50mm gap, cavity trap, 100mm spray insulation.
    There are eve ventilation trays and some vent slates used across one side of the roof. I am unsure if they have used any ventilation at all at the ridge.
    -80mm Insulated Plasterboard across small ceiling section and down the slopes to the knee walls and then insulated sheets on the remaining part to the eves.
    -Habitable room, ventilated by MHRV.

    From reading the post I assume that this approach is not ideal but I am wondering if it is a high risk and really bad approach or is it a common mediocre risk approach. And is there anything I could change to help the situation at this stage.

    I should mention one of the reasons for the spray is to aid in airtightness as it gets into all the awkward places.

    I am sorry for the long post but hopefully someone has some spare time to help.
    Thanks


  • Registered Users, Registered Users 2 Posts: 1,740 ✭✭✭hexosan


    Looking at my roof insulation at the moment.

    Currently I have
    - slates
    - 2x1.5 batons
    - Solitex felt
    - 225mm (9") rafters

    Roofer had half the roof completed before I realized it wasn't counter battened. I've spoke with felt supplier and they say because it's not counter battened I can't use cellulose as it'll force the felt against the slates and may cause them to pop. They've told me I can full fill the rafters with Metac glass wool as the Solitex is breathable, but I've read on here that that's a bad idea as a 50mm vent gap should still be left. I will be fitting an airtightness membrane (intello) to the rafters.

    Was talking to the Tegral rep and he stated that if the rafters are been full filled with insulation I MUST install a ridge vent roll which is basically a mesh that is rolled out under the ridge tiles as there been fitted, this then creates a 5-10mm vent along the ridge line which allows the warm air trapped beneath the slates to vent off keeping the back of the slates dry.

    Anyone have any thoughts I what I can do in this situation.


  • Moderators, Home & Garden Moderators Posts: 10,145 Mod ✭✭✭✭BryanF


    You didnt double batten so you your venting above the breather membrane is compromised. Leave 50mm gap between insulation & membrane and install the ridge vents. Also you need Over eaves vents


  • Registered Users, Registered Users 2 Posts: 1,740 ✭✭✭hexosan


    BryanF wrote: »
    You didnt double batten so you your venting above the breather membrane is compromised. Leave 50mm gap between insulation & membrane and install the ridge vents. Also you need Over eaves vents

    Can these over eaves vents be installed after the roof have been slated


  • Moderators, Home & Garden Moderators Posts: 10,145 Mod ✭✭✭✭BryanF


    Not ideal, what did your arch have to say? when the batten issue was spotted, what alternative eaves details were discussed?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson