Oil Boiler Supply Query

Options
  • 12-10-2010 10:50pm
    #1
    Registered Users Posts: 423 ✭✭


    Hi all,
    need to connect up an oil boiler for the folks next week, I'm a bit rusty on the regs!
    Q's
    1. should it be on the rcd
    2. what size mcb (10 amp?)
    3. does it have to be through a fused spur
    4. do i need a local isolation
    I am going to use a wireless stat/reciever to control boiler..

    Thanks in advance..


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    domestic pumps require 30ma protection so you'll have to rcd it.

    isolate all lives within 2m via a switched spur or rotary isolator


  • Registered Users Posts: 423 ✭✭billy_beckham


    Would an ip rated socket/plug suffice for the isolation?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    afaik a plug/socket is ok for 'local isolation'-couldn't see why not


    if there's a permanent feed you'd need an isolator or the heating switched spur


  • Registered Users Posts: 423 ✭✭billy_beckham


    Thanks again..

    Was just planning on controlling via a wireless stat, when would you have/need a permanent feed?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    some oil boilers have it

    over-run or frost protection