    Are there guidelines on running domestic wiring through insulation?
    I'm not refering to physical contact with polystyrene etc reacting with cable insulation but rather the downgrading of current carrying capacity and possible overheating.
    I'm concerned with the additional layers of insulation in attics and the running of cables in insulated stud work. Particularly because of the many new wall sections for timber frame due to our interest in better insulated homes.


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    ya-the ccc should be de-rated accordingly

    it'll be in the back of rules


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Cables hardly warm up at all once they have the proper rated breakers on them, so you would wonder is any de rating really needed.


  • Registered Users Posts: 68 ✭✭Mr Gumby


    I'm thinking in particular about say cables to storage heaters etc, where the cable size may have to increase even for a normally ok load or radial circuits where it may be necessary to downsize the breaker, run cables in metal conduit or limit the no. of outlets.
    I dont have a copy of rules, what is the max ccc of a 2.5 T&E run through insulation compared to run in air please?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    for sustained heating loads-you're normally concerned with the rating of switchgear
    it's mentioned in the rules



    don't get caught having to downsize breakers anyhow:)

    design current first---then breaker--and lastly cable
    http://www.tlc-direct.co.uk/Book/4.3.9.htm


  • Registered Users Posts: 68 ✭✭Mr Gumby


    Thanks for that link it looks like it has everything I will need.
    I see your point completely about cables.
    How about though were existing cables get buried with a new layer of insulation?

    Are there any areas that the Irish regs differ greatly from the British apart from say 1.5mm lighting rather than 1mm, or is that too complex a question?


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    ya that's a uk link but it's informative

    you'd have to check ET101 to be sure


    there's a good few differences on rcd'ing final circuits over there

    and they do the conversion from TN-C-S to TT for outbuildings -a lot of the time anyhow

    a lot would be similar