Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Supply to caravan

Options
  • 19-11-2010 4:09pm
    #1
    Closed Accounts Posts: 28


    Running a supply to a caravan, there's a ring circuit of sockets and a lighting circuit, sub board in van has a 40 AMP RCCB, a 33 Amp MCB and a 5 Amp MCB.

    supply is 50 metres away in a shed, so was going to run a NYMJ clipped along the beam inside of the shed then gland it into a metal junction box and continue outside the shed across the yard with a SWA.

    Just wondering what cable would do, I'm thinking 6 sq, the major loads in the caravan will be a heater 3KW, and a kettle. And what protection would I need in the main board, would a 40 Amp MCB do the trick

    Any help appreciated


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    i think there's a section in the rules covering this type of work

    i read it all a while back-can't remember much

    you need a sparkie by the sound of it anyhow


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    i think there's a section in the rules covering this type of work

    i read it all a while back-can't remember much

    you need a sparkie by the sound of it anyhow

    your almost as bad as me with that memory:)


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Running a supply to a caravan, there's a ring circuit of sockets and a lighting circuit, sub board in van has a 40 AMP RCCB, a 33 Amp MCB and a 5 Amp MCB.

    supply is 50 metres away in a shed, so was going to run a NYMJ clipped along the beam inside of the shed then gland it into a metal junction box and continue outside the shed across the yard with a SWA.

    Just wondering what cable would do, I'm thinking 6 sq, the major loads in the caravan will be a heater 3KW, and a kettle. And what protection would I need in the main board, would a 40 Amp MCB do the trick

    Any help appreciated
    You might get away with 6 sq if you had a 20 amp MCB in the main board. And that might just about do the loads you have,
    But a safer bet would be a 32amp MCB at main board and 10 sq to caravan. If you use a 40 amp at main board you will need 16 square to caravan for that size of breaker over that 50m run.

    And what sort of supply is supplying the 'main board' in the shed? Maybe it is to small to allow a sub circuit at 40 amps anyway.

    32 amp sub circuit with 10sq id say, and 32 amp rcbo in the caravan board instead of the 40.
    As M cebee says, a job for a sparks anyway.


  • Closed Accounts Posts: 28 americanpie


    I think it's 10sq supplying the shed from another board, will that manage with another 32 Amp supply taking off it?

    think your right, I'll have to use 10 sq SWA for the whole run with a 32 amp at either end.

    But should the 32 amp at the supply side be on the RCD or should I just leave an individual MCB


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Yea think your right, I'll have to use 10 sq SWA for the whole run with a 32 amp at either end.

    But should the 32 amp at the supply side be on the RCD or should I just leave an individual MCB

    Like M cebee said too, i forget the actual regulations on caravans myself, but i would think the RCD would be better at the sub board in the caravan with a 32amp MCB at the supply end because the RCD is more likely to trip from nuisance tripping etc, and to go all the way to the board in the shed would be a bigger nuisance.


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    ya -you won't be rcd'ing the swa submain at the supply side


    the rules might require 30ma outside i'll check later or someone might know


  • Registered Users Posts: 6,259 ✭✭✭Buford T Justice


    20A MCB would be plenty for the load going to the caravan. Cable sockets on the outside of the Caravan are rated at 16A


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Might be 5kw between the heater and kettle so 22.5 amps
    20 might just about do it though. Most mobiles i seen had gas heaters in them.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    don't know much about this

    asuming it's a permanent installation prob a DP main isolating switch/mcb and 2 DP RCBO's(with Zl within limits) for the final circuits


Advertisement