Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

bypassed the thermostat on boiler

  • 26-11-2010 9:43pm
    #1
    Registered Users Posts: 37


    The water thermostat on my boiler seemed to have stopped functioning properly tonight (power not going through thermostat to boiler) I by-passed it just to get the system going.

    Is there a chance that I could do some damage to the boiler...(i have turned it off till I find out)


Comments

  • Registered Users, Registered Users 2 Posts: 4,762 ✭✭✭meercat


    bit more info please
    is it oil or gas
    has the high limit stat tripped
    any chance if pic
    you shouldnt by pass stats as they may be your only safety cut out preventing boiler bursting


  • Registered Users, Registered Users 2 Posts: 2,672 ✭✭✭kay 9


    You won't do any damage to the boiler. But you could have your expansion pipe or vessel hopping if it's on constant too long. Just monitor it if you have no other form of heat until you get the stat going again. When you feel the cyclinder and rads have reached their normal operatinng temp just switch it off manually. If you have a balancing valve on cylinder close it almost fullway and leave the rads as the heat dump and not cylinder. Sooner ya get stat though the better.


  • Registered Users Posts: 37 Dylbag


    thanks for help - i hope to get new thermostat tomorrow - i dont think i have an expansion vessel - just a cylinder - sorry excuse my ignorance. Does this mean i have an open system...


  • Registered Users, Registered Users 2 Posts: 2,672 ✭✭✭kay 9


    It does and is safer for what you want to do. Don;t leave it on all night. Rads will dump the heat these nights anyway keep it on the timer...


  • Registered Users, Registered Users 2 Posts: 145 ✭✭Plombier


    kay 9 thats bad advise, Dylbag don't use your heating until you have this repaired.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,672 ✭✭✭kay 9


    If he needs heat that bad, it's not going to do any damage for one night just less economical. Most it can do is pitch


  • Registered Users, Registered Users 2 Posts: 145 ✭✭Plombier


    Look steam can drive a train, need I sy more.


  • Registered Users Posts: 251 ✭✭GopErthike


    kay 9 wrote: »
    If he needs heat that bad, it's not going to do any damage for one night just less economical. Most it can do is pitch

    Expansion might freeze, could be a combined f+e in GB which could be blocked, I wouldn't advise using it without seeing it.
    Always err on the side of caution when it comes to heating.


  • Registered Users Posts: 37 Dylbag


    Wish I had of listened to the advice...turned out I had a closed system...although i still haven't found the expansion vessel...anyway put the heat on for half an hour thinking I'd be alright...bad idea! Two pipes burst down in basement...bit of a mess!


  • Posts: 0 [Deleted User]


    Send kay 9 the bill.
    Your lucky, it could of been worse, i'v known people to get hurt.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 44,080 ✭✭✭✭Micky Dolenz


    You lost your stat two weeks ago??

    By passing any safety device is foolish, but you know that now.


  • Registered Users Posts: 251 ✭✭GopErthike


    Yeah it was crazy advice to give.


  • Registered Users, Registered Users 2 Posts: 6,260 ✭✭✭Buford T Justice


    You lost your stat two weeks ago??

    By passing any safety device is foolish, but you know that now.

    I agree, it shouldn't have been used without a stat, let alone for two weeks.

    Wouldn't the pressure relief valve have taken care of it?


  • Registered Users, Registered Users 2 Posts: 44,080 ✭✭✭✭Micky Dolenz


    I agree, it shouldn't have been used without a stat, let alone for two weeks.

    Wouldn't the pressure relief valve have taken care of it?

    It should have, but how's to say it wasn't faulty/seized. He took out two safety devices, the control and high limit stat. This is a high percentage of safety devices on the system.

    As Gary states, he is very lucky that nobody was seriously hurt/killed. He can forget about claiming anything on his home insurance either.


  • Registered Users Posts: 37 Dylbag


    I know....we got away well...and obviously can't claim on insurance! The plumber came out and replaced the thermostat and the two burst pipes but never mentioned the safety release valve... Should I check this somehow? There seems to be safety valve on the back of boiler...

    It actually burst the first night that I bypassed thermostat....I just wasnt on this till last night


  • Registered Users, Registered Users 2 Posts: 6,260 ✭✭✭Buford T Justice


    Dylbag wrote: »
    It actually burst the first night that I bypassed thermostat....I just wasnt on this till last night

    That would have been enough o a warning imo.


  • Registered Users, Registered Users 2 Posts: 145 ✭✭Plombier


    Wouldn't the pressure relief valve have taken care of it?

    If heated from 20 to 100 degrees the density of water will increase by about 4% so the temperature will most likley cause problems first.


Advertisement