How to check ESB timer signal

Options
  • 23-12-2010 12:38am
    #1
    Registered Users Posts: 709 ✭✭✭


    Like many people before me on this forum I have storage heaters and I have problems :)
    I took a look in the distribution board/breaker box in our apartment a few days to try and understand how exactly our storage heating works.
    Thanks to bunch of previous posts here I was able to figure things out, and fix the wiring on badly installed devireg 710-2.
    So now everything looks right, but the devireg does not kick in at night, and so the contactor controlling the heaters does not come on.

    Some things I've already checked:

    1. The contactor does work if I apply voltage to it directly.
    2. The heaters come on fine if I set the contactor to always on.
    3. The outdoor thermistor gives reasonable readings per the spec sheet.
    4. Setting the day dial to constant and the night dial to +4 doesn't help, even after 11pm (day light stays green, night light stays red).
    5. I shorted terminal 4 and 6 for testing per the spec sheet, and both lights went red as they should.
    6. I just checked the voltage to contact 2 on the devireg which is supposed to be the ESB timing control, and it's 0. Since it's past 11pm, and I know the ESB clock to the building has the correct time (checked earlier today), this should be live right?

    So basically I'm left wondering about the ESB timing signal. It's a brown wire that just disappears into the wall and I have no idea how to check it, or even check if it's the correct wire (given the mess the original installer made). Any tips?


Comments

  • Registered Users Posts: 709 ✭✭✭cianc


    Actually, it might be the devireg after all.
    I just checked the timing signal wire connected to terminal 2 on the devireg, and unconnected.
    Unconnected it reads live, connected it reads ground. So a short in the devireg.
    I'll double check tomorrow when I've had some sleep, but looks like I need to buy a new unit :( Anyone know where I can get one?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    you can search here-there's been plenty of similar questions


  • Closed Accounts Posts: 517 ✭✭✭JOHNPT


    Would be interested to know did you resolve problem with new Devi Reg. There should be a 6amp MCB on board with a single brown which feeds ESB timeclock and then a single brown from timeclock which feeds terminal 4 on Devi reg. No 4 and No 2 are connected together. No 1 is then connected to the contactor.
    Will you post outcome. Thanks


  • Registered Users Posts: 709 ✭✭✭cianc


    JOHNPT wrote: »
    Would be interested to know did you resolve problem with new Devi Reg. There should be a 6amp MCB on board with a single brown which feeds ESB timeclock and then a single brown from timeclock which feeds terminal 4 on Devi reg. No 4 and No 2 are connected together. No 1 is then connected to the contactor.
    Will you post outcome. Thanks
    I'll be sure to update when I get the new unit.
    As for the 6amp MCB on the board, there isn't one. There's single brown that comes from the wall behind the board, but I have no idea where it originates.
    When you buy a house/apartment they should come with full plumbing and wiring schematics :)


  • Closed Accounts Posts: 517 ✭✭✭JOHNPT


    Maybe they used a 10 amp - as far as i know there should be a signal wire from fuseboard to timeclock and a signal wire back.


  • Advertisement
  • Registered Users Posts: 709 ✭✭✭cianc


    New devireg fixed things, hurray, no more fiddling with storage heaters every day :)


  • Closed Accounts Posts: 2 tomtomsto


    I have the very same issue: the green light never turns red, so the Devi reg never triggers the contactors.

    I would be very interested to know where you bought a 710 replacement from, as it is impossible to find anywhere since discontinued.


  • Closed Accounts Posts: 517 ✭✭✭JOHNPT


    It may not be a problem with Devi Reg it could be the ESB time clock which is not working.


  • Closed Accounts Posts: 2 tomtomsto


    I think it is an issue with the Devireg, since I have also an electric boiler working during off-peak hours, and this is working fine, so the off-peak signal works.

    The issue with the Devi 710 is that there are absolutely no like-for-like replacements on the market, either from Devi or other suppliers. It is not possible to find something else to put on an electric board, so some extensive re-wiring would be required to replace a broken 710, if a replacement cannot be bought.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    you mean electric water heating?

    that prob does it's own timing

    there's a manual online for the devireg


  • Advertisement
  • Closed Accounts Posts: 1 gilligan


    Hi Cian,

    Can you provide the name of the place where you picked up the devi reg710-2? I have looked around and unable to get one...thanks


  • Registered Users Posts: 49 snnowwy


    gilligan wrote: »
    Hi Cian,

    Can you provide the name of the place where you picked up the devi reg710-2? I have looked around and unable to get one...thanks

    BUMP


  • Registered Users Posts: 8 daveve


    Has anyone replace a devi reg 710, If you did, can you let me know with what and is there any problems replacing it.