MCB rating for electric cooker

Options
  • 06-02-2011 5:08pm
    #1
    Registered Users Posts: 16


    1. What rating MCB should I use for a standard electric cooker with ceramic hob and 2 ovens (one with fan, one with grill)

    2. Should a radial circuit of 2.5mm2 be protected with a 16A or 20A MCB.


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    there's a section on cookers in back of rules -i think it's 10kw total connected load on a 32amp circuit

    you need to add up the cooking load and see if you need an extra circuit

    for a 16/20amp radial circuit -if you divide the 16/20 by any correction factors that'll give you the current rating needed
    http://www.tlc-direct.co.uk/Book/4.3.9.htm

    if you're starting with the 2.5 you can prob multiply by correction factors to calculate the mcb size


  • Closed Accounts Posts: 466 ✭✭beanie10


    Ovens can normally wired off a fused spur 2.5 20amp clean line from board, check the wattage of oven first. For the hob you should use a 6sq cable from the board to cooker switch protected by a 32amp mcb.
    If you are wiring the oven off the hob supply make sure to use proper fused protection on the flex to the oven.
    A 2.5 and a 6 sq cable will cover all angels as diversity is taken into account


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    sounds like he might have a single cooking appliance

    -if so that'll be one circuit anyhow of the appropriate size


  • Closed Accounts Posts: 466 ✭✭beanie10


    Misread that thought he had 2 separate ovens


  • Registered Users Posts: 16 mahargwa


    Its a free standing cooker rated at 10.8 kW so a 40A MCB should be ok. 10.8kW is 45A at 240 Volts - (The rating of the cooker was 240V as it's quite old) So a 40 A MCB should be ok as all of the plates and ovens won't be ON at the same time. The cable is ok 6mm2 I think and near to the consumer unit. Thanks for the advice.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    I think a 32amp breaker will do you for that. And best if its a 6 square cable.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    it's prob only 10kw at 230v -same as the showers

    http://www.tlc-direct.co.uk/Book/6.2.1.htm

    32 amp breaker

    short run prob 6sq

    the rules says 10kw total anyhow last time i looked


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Yea 9.9kw it would be.