    I have a new house and it seems to me that it may be down on power. Lights flicker when I am vacuming, recently a contractor complained his saw (110v via a transformer) was low on power in my house.

    I have also noticed the motor in my HRV system powering up and down a little as I switch appliances on and off. None of this seems normal to me.

    The unique thing is when building it we put the ESB meter is at the gate, 135meters from the main fuse board in the house. We used SWA 24mm cable. I measured the voltage at a socket using a multimeter and it is 232v.

    Is there something else I should measure? Should I be able to test amps? As far as I know the ESB fuse at the meter is a 63Amp supply.

    Suggestions and help welcome


«134

Comments

  • Registered Users Posts: 148 ✭✭sparcocars


    Kieran007 wrote: »
    I have a new house and it seems to me that it may be down on power. Lights flicker when I am vacuming, recently a contractor complained his saw (110v via a transformer) was low on power in my house.

    I have also noticed the motor in my HRV system powering up and down a little as I switch appliances on and off. None of this seems normal to me.

    The unique thing is when building it we put the ESB meter is at the gate, 135meters from the main fuse board in the house. We used SWA 24mm cable. I measured the voltage at a socket using a multimeter and it is 232v.

    Is there something else I should measure? Should I be able to test amps? As far as I know the ESB fuse at the meter is a 63Amp supply.

    Suggestions and help welcome

    The cable you used is too small and the voltage is dropping under load. Replacing the cable would be the only thing to do there. A minimum of 50mm square should of been used but even that would be on the volt drop limits outlined in the etci rules. 70mm square or over would of been the best option. You should of still put the meter box at your house and let the esb worry about running the bigger cable to your house but your best option now is probably to replace the cable with a bigger cross sectional area cable.


  • Registered Users Posts: 2,400 ✭✭✭evosteo


    Kieran007 wrote: »
    the ESB meter is at the gate, 135meters from the main fuse board

    We used SWA 24mm cable
    .
    :eek:

    who decided to use that size cable??????


  • Registered Users Posts: 2,400 ✭✭✭evosteo


    more than likely will also need a distribution board upgrade also due to the larger sized cables been terminated


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    evosteo wrote: »
    more than likely will also need a distribution board upgrade also due to the larger sized cables been terminated

    I wouldnt think the 70 square would have to be terminated into the DB. It could be terminated into some sort of minipillar and then 16 square brought in the last few meters.

    Realistically the meter should be moved to the house, as the meter is probably only supplied with 25 square as well.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    never came across this setup before


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    No it seems a bit mad. Hard to believe the ESB connected that setup.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    if the voltage drop is serious enough

    i'd look at bringing a esb service to house first alright

    voltage drop is pretty good in rural dom installations these days- with trafos close to houses usuallly


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    A very rough calculation:

    Maximum current: 63A (this is the size of the switch foes for a domestic installation)

    Length of run: 135m

    Cable type: 3 x 70 sq. mm XPLE/SWA copper conductors

    mV/A/m: 0.69 (for 3 x 70 sq. mm XPLE/SWA copper conductors)

    Volt drop = (0.69/1000) volts x 63 amps x 135 metres

    Volt drop = 5.87 volts which is a 2.55% volt drop = Good :)



    mV/A/m: 1 (for 3 x 50 sq. mm XPLE/SWA copper conductors)

    Volt drop = (1/1000) volts x 63 amps x 135 metres

    Volt drop = 8.51 volts which is a 3.7% volt drop = Not great :o




    mV/A/m: 1.9 (for 3 x 25 sq. mm XPLE/SWA copper conductors)

    Volt drop = (1.9/1000) volts x 63 amps x 135 metres

    Volt drop = 16.16 volts which is a 7.03% volt drop = FAIL :eek:


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    What voltage will a digital mulitmeter show on the cable with no load on it if its 100 miles long?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    What voltage will a digital mulitmeter show on the cable with no load on it if its 100 miles long?
    No load? In theory, full voltage. The voltage drop is directly proportional to the current drawn.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    I know, im just having a laugh, although a volt meter does have a load, just extremely small, especially a digital one.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    I know, im just having a laugh, although a volt meter does have a load, just extremely small, especially a digital one.
    :D:D:D


  • Closed Accounts Posts: 10,910 ✭✭✭✭RoundyMooney


    robbie7730 wrote: »
    No it seems a bit mad. Hard to believe the ESB connected that setup.

    Why? The customer's installation is the responsibility of the customer. The installation was certified, and any follow up should be with the contractor who thought a 135 meter run from the interface was a good idea. I'd bet the distance from meter to transformer is probably half that or less.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Why? The customer's installation is the responsibility of the customer. The installation was certified, and any follow up should be with the contractor who thought a 135 meter run from the interface was a good idea. I'd bet the distance from meter to transformer is probably half that or less.


    Obviously its the contracor who should of looked after a proper installation alright. I thought there would be some limit to the length of tails myself though. Limitless so is it, once there is a cert?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    Limitless so is it, once there is a cert?
    Pretty much, yes. The ESB are not really interested in anything beyond the meter. This was not the case in the past (pre ECSSA and RECI days). It is no longer their responsibility.

    In fact I even know of a case (large commercial installation) where a RECI inspector informed the ESB that a new installation did not comply with the regs and the ESB refused to disconnect or get involved.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    Pretty much, yes. The ESB are not really interested in anything beyond the meter. .

    No, but they have stated texting beyond the meter when the bill is overdue:eek:.


  • Registered Users Posts: 2,400 ✭✭✭evosteo


    robbie7730 wrote: »
    I wouldnt think the 70 square would have to be terminated into the DB. It could be terminated into some sort of minipillar and then 16 square brought in the last few meters.

    Realistically the meter should be moved to the house, as the meter is probably only supplied with 25 square as well.

    i was thinking with me industrial helmet on.:D

    jus sounds like a badly designed install.

    longest run iv ever heard of anyway from a meter to a board


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    robbie7730 wrote: »
    No, but they have stated texting beyond the meter when the bill is overdue:eek:.
    don't think there's any max length specified in rules

    but the 4% installation voltage drop would include the tails

    stick on an electric shower and you're dropping 10v on the tails alone here

    i reckon the op may get by-depending on the loads

    there should also be an mcb in cabinet at gate-if there isn't one


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    to upgrade the tails you'd prob parallel another 3*25 with the existing tails

    bringing the service to outdoor cabinet on house would be preferable though

    paying the extra for 'enhanced' usually ensures good quality supply even though in theory you're entitled to it


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    M cebee wrote: »
    to upgrade the tails you'd prob parallel another 3*25 with the existing tails

    I would not do this.

    Power cables in parallel should be exactly the same lenght and type. It would be difficult to ensure that this is the case.

    Also terminating two 3 x 25 sq. SWAs at both ends will be more hassel than it is worth!

    Personally I would install the ducting and get the ESB to move the meter.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    It sounds like it is already a 3x25 swa so it would be the same size and type.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    yes-can't see the problem at all

    the exact length isn't an issue here as the tails would be protected at cabinet with '63amp main ocpd'

    -they can be connected to 16's before the meter postion and DB in suitable boxes


    i was only theorizing but if for arguments sake you decided to upgrade tails for VD-the cost difference between paralleling another 25 and fitting a new 50 is prob well over 1200 euro!!!

    anyhow bringing the service to house is prob the way to go


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    There should be no problem with a couple of feet difference in length especially where the cables in parallel will not be loaded above what each cable on its own is rated at. Its only a volt drop problem. 25 square is not too small for the loading in the op`s case here, its only the length of run having too high a volt drop. The load wont be above the 63 amps or so, which each 25 Sq is capabable of carrying.

    Paralleling 2 4x120 cables to have the current carrying capacity of a 4x240 would be the same length, mainly because they are obviously run the same way. But equal length helps ensure both share the load equally. In reality though, i doubt a couple of feet would make much difference here either, as the difference in impedence would be tiny.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    anyhow it's not the preferred option

    i'd love to know why they thought this was good idea?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Im still surprised a meter can be put 135 meters from the dwelling. I know the supply company might say a cert was given to us etc, and they have nothing to do with anything beyond the meter, and thats fair enough, but i thought there would be some association made between a meter location and the metered dwelling in a domestic setup.

    Overall it sounds like a cost cutting measure in terms of getting the supply brought to the house, but its even more surprising a contractor thought a 25Sq cable would do the job.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    in fairness to ESBN

    the installation is the responsibility of the contractor

    they have enough to be doing


    hmm-now you got me thinking robbie

    this would never be a temp supply at perimiter of site and new installation connected to it ??

    nothing would surprise me


  • Registered Users Posts: 4,408 ✭✭✭ft9


    I'd love to know the reason or thinking behind why the meter was placed so far away?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,591 Mod ✭✭✭✭2011


    M cebee wrote: »
    yes-can't see the problem at all
    If cables are paralleled they must be exactly the same specification, insulation type, conductor type and size, length, routing, exposed to the same ambient temperature etc. Ideally even the manufacturer of the cable should be the same. That way the impedance of each cable is exactly the same, so the load is evenly split. If the load is not evenly split you could not treat two 3 x 25 sq. SWAs as though it were a 3 x 50 sq. SWA from a design point of view.

    It is not good enough to say they are both 3 x 25 sq. SWAs.
    For example, if one 3 x 25 SWA is XPLE and the SWA is PVC the XPLE (with all else being equal) the load will not be evenly distributed.

    You can argue that it would still work (and you would probably be correct), but it would not be done correctly or in a professional manner (as far as I am concerned).
    In my opinion when it comes to mains cabling it should be done 100% correctly or not at all.

    I have been involved in paralleling power cables several times for transformers (6 x 630 sq. singles), generators, and more recently very large motors.
    In all cases the design team went to a lot of trouble to ensure that all paralleled cabling was identical.
    ]the exact length isn't an issue here as the tails would be protected at cabinet with '63amp main ocpd'

    I am not arguing that the cables would not be adequately protected, they would be. The reason for paralleling is the same reason for installing a larger cable i.e. to deal with the volt drop issue.
    -they can be connected to 16's before the meter postion and DB in suitable boxes

    They could, but it would not be something I would like to do. I never ever like to join mains cables.

    i was only theorizing but if for arguments sake you decided to upgrade tails for VD-the cost difference between paralleling another 25 and fitting a new 50 is prob well over 1200 euro!!!

    I know, point taken.

    anyhow bringing the service to house is prob the way to go
    Agreed.

    Sometimes the only correct solution is a very expensive one!


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Doughal maguire from the esb put the meter in. He thought the house was small, but it was actually far away.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    That way the impedance of each cable is exactly the same, so the load is evenly split. If the load is not evenly split you could not treat two 3 x 25 sq. SWAs as though it were a 3 x 50 sq. SWA from a design point of view.

    This will be like the conduit arguement, but the 2 paralleled cables would not need the current carrying capacity of a 50 square, only the smaller volt drop, they are not the same thing precisely. The single cable is never going to be overloaded here, it just has too high a volt drop, so two in parallel will never have either cable carrying its rated capacity in the OP scenario here.

    Also, there will be differences in impedences even of a 100 meter length of cable cut in half.

    Two paralleled cables dont need to carry exactly half of the current each, but in practice they likely will be very close anyway. Also 2 smaller cables have a slightly higher capacity than a single big one anyway, so a slight variation in the split current is not a problem.