4th Edition advice please

Options
2»

Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    if you mean using 2.5 pvc singles and 1.5 pvc earth in conduit for a socket circuit?-that's not allowed
    They have to be same size


  • Registered Users Posts: 102 ✭✭antlyn


    It was brought up on a course recently they were arguing that the 1.5 single earth isn't strong enough under tension and were recommending 2.5 to be used


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    meercat wrote: »
    work started before 30 sept 2009 and in substantial advanced state can be completed and certified in accordance with 3rd edition

    http://reci.ie/Portals/0/14062%20RECI%20News_1.pdf
    Ya-thought it would have to be further advanced
    The changes mentioned already wouldnt be critical
    I'd fit cabinet mcb and rcd any pumps regardless


  • Registered Users Posts: 4,745 ✭✭✭meercat


    M cebee wrote: »
    I'd fit cabinet mcb and rcd any pumps regardless

    agree


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    reci can't ban 1.5 singles
    Cpc-same size as live conductors except for t+e
    Last time i looked anyhow

    Probably in terms of 1.5 being weak in terminals they are talking about, rather than fault capacity.


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    ya
    but i can't see the problem myself anyway


  • Registered Users Posts: 102 ✭✭antlyn


    M cebee wrote: »
    ya
    but i can't see the problem myself anyway


    Me either, but don't shoot me (the messenger)!!


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,595 Mod ✭✭✭✭2011


    M cebee wrote: »
    if you mean using 2.5 pvc singles and 1.5 pvc earth in conduit for a socket circuit?-that's not allowed
    They have to be same size

    As stated in the 4th edition of ET:101 ???


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    2011 wrote: »
    As stated in the 4th edition of ET:101 ???
    Yes its in the rules


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    my bad
    Its either same size off the table
    -or you can calculate it
    Always same size ime


  • Advertisement
  • Registered Users Posts: 36 stoneyxox


    Can I have one double pole isolator (20a) feeding two double sockets under the counter which supplies 4 appliances??


  • Registered Users Posts: 1,051 ✭✭✭Tuco88


    I'd say it's not ideal setup, say if there is an issue with one appliance all will have to be off I until it's un plugged.


  • Registered Users Posts: 4,745 ✭✭✭meercat


    stoneyxox wrote: »
    Can I have one double pole isolator (20a) feeding two double sockets under the counter which supplies 4 appliances??

    This is not permitted
    Each appliance must have a dedicated and labelled isolator.544.3.5