    does the lighting circuit for a bathroom have to be on its own dedicated circuit?


«1

Comments

  • Registered Users, Registered Users 2 Posts: 2,454 ✭✭✭cast_iron


    No. Though it must have RCD protection, and that must be a separate RCD from the sockets etc. The handiest way out would be a 10A RCBO. You could have 2 bathrooms on the one circuit, but I think upstairs and downstairs should be on separate circuits.


  • Registered Users Posts: 140 ✭✭Marcus_Crassus


    cast_iron is correct, I just looked it up in the ETCI rules.


  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    thanks for the responce, so am i correct in saying that if the bathroom is upstairs i can include it on the upstairs circuit once its protected by a 10a rcbo?


  • Registered Users, Registered Users 2 Posts: 4,755 ✭✭✭meercat


    evosteo wrote: »
    thanks for the responce, so am i correct in saying that if the bathroom is upstairs i can include it on the upstairs circuit once its protected by a 10a rcbo?

    much better to have it on its own dedicated rcbo circuit though


  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    whats the advantage of having it on its own circuit?


  • Advertisement
  • Registered Users Posts: 227 ✭✭paddymick


    evosteo wrote: »
    thanks for the responce, so am i correct in saying that if the bathroom is upstairs i can include it on the upstairs circuit once its protected by a 10a rcbo?

    Yes you are correct....And having the rest of the lighting circuit on the RCBO can only be a plus..


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    You cant put other lights on bathroom lighting rcd or rcbo

    you dont need if they're 12volt or outside zones


  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    so if they are 230v lights in the bathroom they need to be on a dedicated circuit protected by an 10a rcbo

    however if they are 12vspots/lights they can be just included on the upstairs circuit on a normal 10a mcb

    :confused:


  • Registered Users, Registered Users 2 Posts: 2,454 ✭✭✭cast_iron


    evosteo wrote: »
    however if they are 12vspots/lights they can be just included on the upstairs circuit on a normal 10a mcb
    :confused:
    That wouldn't be a great way to do it...as they may be 12v fittings today, but swapped to 220v in the future.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    Yes 12v. selv lites or lights outside zones dont need dedicated rcd

    if i recall the rule says any circuit in bathroom zone needs dedicated rcd
    -thats the amended version of the rule


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    jesus i wish they would stop dicking about with the rules,

    them etci boys muct get fierce bored, thinking about what to do next,

    has anybody every been electricuted by a bathroom light?


  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    i also see there was more ammendments made in july of this year fot the 2008 rules:rolleyes:


  • Registered Users Posts: 227 ✭✭paddymick


    evosteo wrote: »
    jesus i wish they would stop dicking about with the rules,

    them etci boys muct get fierce bord, thinking about what to do next,

    I agree, It wont be long before every circuit is on its own RCD anyway..

    It also says in the rules that a bathroom should have at least one light outside of zones thats on its own circuit and not on the RCD so that if the RCD trips you will still have light and avoid injury......I havent met any who does that yet!:rolleyes:


  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    sweet jesus,

    so the best bet for the bathroom is to have it on its own "dedicated" circuit, protected by a 10A rcd/rcbo, that would cover the bathroom fan and wall shaver light?

    and supply the bedrooms with there own 10a circuit


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    The light outside the zones was dropped for domestic in the amendment to the rules


  • Registered Users Posts: 227 ✭✭paddymick


    I just wire bathrooms and ensuites on their on circuits(inc lights,fans and mirror lights) and stick them on a 10A RCBO,Shaver sockets I wire on their own circuit and put them on their own RCBO.


  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    cheers for the info guys, its good to know the right way of doing things and letting others know

    mceebe whats the reason for not allowing say two external lights (ie two bedroom lights) to be on the same circuit as the bathroom?

    would it not just be extra protection for them extra two lights?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    if the cicuit is extended outside bathroom the risk of tripping is increased

    losing light in a bathroom is a hazard

    which is also why they kept the additional light source for commercial as users may not be familiar with bathroim layout


  • Registered Users, Registered Users 2 Posts: 1,017 ✭✭✭dazed+confused


    When did the RCD rule for bathroom lighting come in? In Fás in 2004 I was taught that the shaver socket was safer if it was not on an RCD. Its an isolating transformer anyway so there's no risk of shock.


  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    When did the RCD rule for bathroom lighting come in? In Fás in 2004 I was taught that the shaver socket was safer if it was not on an RCD. Its an isolating transformer anyway so there's no risk of shock.

    came in 2008 in the 4th edition or the regs i think, if heard many different twists on "how it should be done" even heard mentioned there should be an emergency back up light in the bathroom:rolleyes:

    think that was done away with though


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    Ya theres no benefit having a shaver socket on rcd

    In normal use


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    evosteo wrote: »
    whats the advantage of having it on its own circuit?

    It reduces the chance of being left in the dark in the bathroom, a hazzard in itself, and probably a bigger hazzard than not having an RCD on the bathroom light.

    The chance of tripping increases with more rooms besides the bathroom on the RCD/RCBO.


  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    sure if your in the bath and the bathroom door is closed would you not be in darkness anyways if the circuit trips?


  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    i can see emergency lighting slowly coming into the domestic scene soon,

    bathroom
    hall
    landing
    kitchen

    sure they are all dangerous places to be if the power goes no?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    You would be, but if you had the whole upstairs lighting circuit on an RCD, a trip is more likely than if the bathroom is on its own circuit.


  • Registered Users, Registered Users 2 Posts: 4,755 ✭✭✭meercat


    evosteo wrote: »
    i can see emergency lighting slowly coming into the domestic scene soon,

    bathroom
    hall
    landing
    kitchen

    sure they are all dangerous places to be if the power goes no?

    i agree
    no harm either
    also one near distribution board would be an advantage
    i would offer it to clients as an option(2d fitting with emergency pack)


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    i reckon there's going to be an awful lot of changes soon

    and a lot more than emergency lights

    upon reflection and in the light of this carry-on at those apartments

    i reckon the whole self certification business will have to go

    as it's not working anyhow


  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    hmmm do ya reckon if they bring in independent certification that would put reci and ecssa in trouble,

    sure isnt the reason they only exist is for the certification process

    contractors would only have to pay the independant certifier/ tester for a cert????


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    ive been reci member for 16yrs until recently
    as i'm on maintenance mostly now

    but it's a joke


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,400 ✭✭✭evosteo


    only interested in the money???


Advertisement