Earth leakage circuit tripping

2»

Comments

  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    meggering at 250v

    between L+N (linked) and E

    is how you test with appliances in situ afaik if you're troubleshoooting



    but still maybe better to play safe

    Yea you just beat me to that, but disconnecting all the neutrals and just meggar each one to earth, then each MCB out terminal to earth also(MCB off), saves linking the N`s and L`s.

    The meggar voltage wont really matter in this setup.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    I can't link L+N in my iMac or TV. I could only do this with the lead in which case I would not be meggaring the appliance.

    250V will be DC.
    I have no idea what impact (if any) this would have on different devices and would rather not take the chance!

    Your missing the point, L+N is linked at the MCB board, so you are testing insulation resistance of both the Live and Neutral conductor of the circuit to earth.

    But they can be tested individually as outlined already, by disconnecting all neutrals, and switching off all MCBs. So now we have isolated circuits, each of which can have their insulation tested to earth to find whats tripping the RCD.

    This will also test appliances insulation from their circuit conductors to earth.

    High voltages will only have a negative effect on sensitive appliances when applied to their L and N.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    Your missing the point, L+N is linked at the MCB board, so you are testing insulation resistance of both the Live and Neutral conductor of the circuit to earth.

    But they can be tested individually as outlined already, by disconnecting all neutrals, and switching off all MCBs. So now we have isolated circuits, each of which can have their insulation tested to earth to find whats tripping the RCD.

    This will also test appliances insulation from their circuit conductors to earth.
    I see what you mean. I have never done this. I am always nervous of meggars and electronic equipment (ever since a fellow apprentice caused untold damage!!)

    I would still be reluctant to do this with a computer, TV or similar although they are often double insulated.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    I see what you mean. I have never done this. I am always nervous of meggars and electronic equipment (ever since a fellow apprentice caused untold damage!!)

    I would still be reluctant to do this with a computer, TV or similar although they are often double insulated.

    Wont be any problem once you keep away from meggaring the L and N.

    Pc`s, tv`s etc wont usually be a problem anyway for RCD`s, and can be left out of the test anyway.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    fitting rcbos can help troubleshoot intermittent trips alright

    if it's practical to fit them

    if there's standing leakage from appliances it might spread it across the rcbos as well and cure the problerm

    10.5 mA is the recommended max leakage on a 30ma rcd

    and they can trip from 0.5 IdN(15mA)if im not mistaken


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Individual RCBOs would solve many problems. They will usually show the problem circuit without having to go testing all circuits.

    And they eliminate the accumulative leakage alright.

    This is one area where isolators on kitchen hidden sockets can help identify problems there also.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    the only thing with them is if there's occasional trips on say a B20 rcbo

    it could be overload ,leakage or even inrush or starting current in theory


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    Wont be any problem once you keep away from meggaring the L and N.
    Hmmmm.
    In theory, yes I agree.

    In practice I would be concerned.

    If it is electronic and I felt it was a problem, I would disconnect and see if the problem goes or put it on a dedicated RCD.
    Pc`s, tv`s etc wont usually be a problem anyway for RCD`s, and can be left out of the test anyway.
    Agreed, as they are often double insulated.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    M cebee wrote: »
    fitting rcbos can help troubleshoot intermittent trips alright

    if it's practical to fit them
    As a temporary measure to locate a problem it can always be done, it just may not look too pretty.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    10.5 mA is the recommended max leakage on a 30ma rcd

    The funny thing about that is, it can reduce the shock a person receives before they trip the RCD from contact with live and earth.


    A Neutral Earth short does the opposite, this can increase the shock a person would recieve before tripping the RCD, especially on a circuit that has nothing plugged into it.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    As a temporary measure to locate a problem it can always be done, it just may not look too pretty.

    Yea it would be a good idea if a circuit is suspected.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    2011 wrote: »
    As a temporary measure to locate a problem it can always be done, it just may not look too pretty.

    i wouldn't be taking them back out if i fitted them


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Once there is room in the board, and the RCBO has cured the problem.

    In the instance here, it looks like a problem on a circuit or appliance anyway.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    M cebee wrote: »
    i wouldn't be taking them back out if i fitted them

    What I mean is that if you have a distribution board that is too full to accommodate extra RCBOs and the customer will not pay/can't pay for a larger board or perhaps there are time constraints or other reasons you could fit several RCBOs on a temporary basis to find a fault.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    you can do that

    afaik it's also ok to use the single mod rcbos with solid neutral pole

    on TN 30ma circuits

    although they don't seem to be commonly used here
    i've never fitted one


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    M cebee wrote: »
    you can do that

    afaik it's also ok to use the single mod rcbos with solid neutral pole

    on TN 30ma circuits

    although they don't seem to be commonly used here
    i've never fitted one
    I have seen some Square D ones, but they required a very specific distribution board. Something tells me that single mod RCBOs would not be cheap or off the shelf, but I honestly don't know.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    i dont think they're expensive


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee




  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    M cebee wrote: »
    i dont think they're expensive

    Well they certainly aren't common and there must be a reason for it.
    I got the Square D ones and the board for free as a sample. It is very high quality and did not look cheap to me. The largest single mod RCBOs that I have seen are 20A. Perhaps there is a size limitation too.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    M cebee wrote: »

    I have not seen this model before.
    They may be single mod, but they look to me as though they take up extra space in terms of length. This is also a consideration if you were to purchase this type.


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee




  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    I like this one:
    http://www.etci.ie/docs/ET214.pdf

    Must ask Stoner to Sticky it


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    5.1.6 mentions the bit about neutral to earth shorts after the RCD increasing the shock hazzard. A very simple concept but worth noting anyway.


  • Registered Users Posts: 20 monkstowngirl


    :DHi everyone,
    Just wanted to write a quick thank you to everyone who replied and offered help. Really appreciate it!
    Turned out to be a faulty cable after all that and everything is right again with the world!
    Thanks again!


  • Registered Users Posts: 491 ✭✭MrThrifty


    :DHi everyone,
    Just wanted to write a quick thank you to everyone who replied and offered help. Really appreciate it!
    Turned out to be a faulty cable after all that and everything is right again with the world!
    Thanks again!

    Sorry for dragging this out, but out of curiosity was it a damaged house mains cable or just a damaged appliance cable, or maybe an appliance incorrectly wired to its plug?!


  • Registered Users Posts: 20 monkstowngirl


    Hi Mr. Thrifty. It was actually a faulty cable to a socket.


  • Registered Users Posts: 798 ✭✭✭Poulgorm


    I had a problem, a few years ago, with an ELCB tripping intermittently.

    My electrician concluded (eventually) that the ELCB itself was faulty - he replaced it with a new one and it solved the problem.