  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Comer1 wrote: »
    Could the problem be that somewhere on the cable going from the pull cord back to the panel, a socket or something has been added.

    If the electrician simply connects the supply to the RCBO to the non RCD BUS bar in the panel, that might in itself stop the tripping. '

    That was the first thing to do. Connecting it as it has been connected, did nothing to show the problem any clearer for anyone here, and was the incorrect way to connect it anyway.

    He could have been lucky and happen to put in an RCBO a bit more sensitive than the RCD, but that would have been luck, rather than the proper independent connecting of the RCBO.


  • Registered Users Posts: 1,070 ✭✭✭Comer1


    WikiHow wrote: »
    I thought you replaced the cable? :confused:

    I replaced the cable from the shower to the pull cord, not from the pull cord to the panel.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Comer1 wrote: »
    I replaced the cable from the shower to the pull cord, not from the pull cord to the panel.

    Have you access to inspect the cable from the board to the switch? i.e attic, side crawl attic?


  • Closed Accounts Posts: 460 ✭✭Cogsy88


    Push the test button for your socket rcd, then go try switch the shower on. If the shower doesent work and your rcbo isint tripped then it's clear what the problem is.


  • Registered Users Posts: 1,070 ✭✭✭Comer1


    WikiHow wrote: »
    Have you access to inspect the cable from the board to the switch? i.e attic, side crawl attic?

    No, but if need be, I could run a new cable. Strange that it trips only when the pull cord is on if the problem is from the pull cord to the panel.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Cogsy88 wrote: »
    Push the test button for your socket rcd, then go try switch the shower on. If the shower doesent work and your rcbo isint tripped then it's clear what the problem is.

    Interesting. What is it?


  • Registered Users Posts: 1,070 ✭✭✭Comer1


    Bruthal wrote: »
    Interesting. What is it?

    That the RCBO isn't connected independently of the RCD???


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Comer1 wrote: »
    No, but if need be, I could run a new cable. Strange that it trips only when the pull cord is on if the problem is from the pull cord to the panel.

    Have you tried the experiment in post #95?


  • Closed Accounts Posts: 460 ✭✭Cogsy88


    Comer1 wrote: »
    That the RCBO isn't connected independently of the RCD???

    So the rcbo is fed from the rcd.


  • Closed Accounts Posts: 460 ✭✭Cogsy88


    Bruthal wrote: »
    Interesting. What is it?

    Dat there's a phase or neutral mixed up in the board.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Did you run the shower for a minute or 2, or will that instantly trip the Rcd?


  • Registered Users Posts: 1,070 ✭✭✭Comer1


    Cogsy88 wrote: »
    So the rcbo is fed from the rcd.

    I don't know. I'm a teacher, and everybody knows those who can't do...teach :pac:

    I did the test in post 95 and yes, with RCD tripped, and the RCBO not tripped, the power is off to the shower.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Comer1 wrote: »
    I don't know. I'm a teacher, and everybody knows those who can't do...teach :pac:

    I did the test in post 95 and yes, with RCD tripped, and the RCBO not tripped, the power is off to the shower.

    The electrician you got to put in the RCBO for you is he qualified or is he someone from Mens shed?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Cogsy88 wrote: »
    Dat there's a phase or neutral mixed up in the board.

    Turning off the rcd won't prove that, as both phase and neutral might be through rcd to rcbo. But running the shower causing instant trip would strongly suggest it alright if the shower had previously been running at least for a few minutes at a time.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Comer1 wrote: »
    I don't know. I'm a teacher, and everybody knows those who can't do...teach :pac:

    I did the test in post 95 and yes, with RCD tripped, and the RCBO not tripped, the power is off to the shower.

    Turn on pull chord, then run shower.

    Does it run?


  • Closed Accounts Posts: 460 ✭✭Cogsy88


    Bruthal wrote: »
    Turning off the rcd won't prove that, as both phase and neutral might be through rcd to rcbo. But running the shower causing instant trip would strongly suggest it alright if the shower had previously been running at least for a few minutes at a time.

    Y would you connect an rcbo downstream of an rcd?


  • Registered Users Posts: 1,070 ✭✭✭Comer1


    Bruthal wrote: »
    Turn on pull chord, then run shower.

    Does it run?

    No, the RCD tripped immediately, not the RCBO.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Cogsy88 wrote: »
    Y would you connect an rcbo downstream of an rcd?

    You wouldnt, but it appears that is how it was connected today.

    A few earlier posts

    Bruthal wrote: »
    Did shower stay on when rcd tripped? If not then your sparks made a mess of adding dedicated rcbo.
    Bruthal wrote: »

    As I and others have said, the RCBO should have been connected independently of the RCD, so only the RCBO would trip with residual current problems.

    Adding in an RCBO onto the RCD was a pointless exercise if that is what has been done, in terms of stopping the RCD tripping if the shower was the cause.

    [


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Comer1 wrote: »
    No, the RCD tripped immediately, not the RCBO.

    And did the shower stop running then?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Comer1 wrote: »
    No, the RCD tripped immediately, not the RCBO.

    Looks like the electrician intended connecting the rcbo up independently alright, but connected into wrong neutral bar probably.

    The rcd tripping instantly bwhen you try to run it is a sign of that.


  • Advertisement
  • Closed Accounts Posts: 460 ✭✭Cogsy88


    Bruthal wrote: »
    You wouldnt, but it appears that is how it was connected today.

    A few earlier posts






    [

    Sorry should have read the whole thread first' my bad.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Bruthal wrote: »
    Looks like the electrician intended connecting the rcbo up independently alright, but connected into wrong neutral bar probably.

    The rcd tripping instantly bwhen you try to run it is a sign of that.

    But he said earlier it was running for a minute or two after the installation of the RCBO.


  • Registered Users Posts: 1,070 ✭✭✭Comer1


    Bruthal wrote: »
    Looks like the electrician intended connecting the rcbo up independently alright, but connected into wrong neutral bar probably.

    The rcd tripping instantly bwhen you try to run it is a sign of that.

    That grey capacitor is not in place ATM, would that make a difference?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    WikiHow wrote: »
    But he said earlier it was running for a minute or two after the installation of the RCBO.

    I think he may have said it tripped a minute or two after switching on the pullchord. I'm not sure though.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Comer1 wrote: »
    That grey capacitor is not in place ATM, would that make a difference?
    But you said in post #80 that it was running perfect without it connected :confused:


  • Registered Users Posts: 1,070 ✭✭✭Comer1


    WikiHow wrote: »
    But he said earlier it was running for a minute or two after the installation of the RCBO.

    Running the test that Bruthal suggested was the first time I tried running the shower since last week.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Comer1 wrote: »
    That grey capacitor is not in place ATM, would that make a difference?

    Probably not.

    So to clarify. If you put pull chord on, the rcd will stay on for a time. But if you try to run shower, it will trip instantly?


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Comer1 wrote: »
    Running the test that Bruthal suggested was the first time I tried running the shower since last week.

    How many different ways are there in pressing the on button?


  • Registered Users Posts: 1,070 ✭✭✭Comer1


    WikiHow wrote: »
    But you said in post #80 that it was running perfect without it connected :confused:

    My bad, I should have posted that there was no current through the earth when the capacitor was disconnected. I didn't actually try running the shower. Just turning on the pull cord after post 80 made me realize that I had been a bit premature with my optomism:rolleyes:


  • Advertisement
  • Registered Users Posts: 1,070 ✭✭✭Comer1


    Bruthal wrote: »
    Probably not.

    So to clarify. If you put pull chord on, the rcd will stay on for a time. But if you try to run shower, it will trip instantly?

    Yes