Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Socket and switches heights

Options
  • 06-04-2012 5:21pm
    #1
    Registered Users Posts: 27


    Hi,
    Can anyone tell me the height regulation for sockets and switches. Im in the middle of a selfbuild and doing the wall chasing myself but cant seem to find out the heights. Would appreciate any help..


Comments

  • Registered Users Posts: 4,745 ✭✭✭meercat


    sockets between 400mm-1200
    switches between 400mm-1200mm
    distribution board max height top 2.25mts/min height bottom 1.4mts


  • Registered Users Posts: 27 Selfbuilderx


    Hi meercat
    thanks for the reply
    Is that from the top or bottom of the sockets and switches


  • Registered Users Posts: 4,745 ✭✭✭meercat


    paddymick wrote: »
    Im sure its a typo but that should be between 900mm-1200mm:).

    no,not a typo

    530.6
    1. switches for permanently connected appliances between 400-1200mm
    above floor level

    2.switches for lighting equipment
    in dwellings,between 400-1200mm above floor level
    in public and similar buildings,between 900-1200mm above floor level

    i would keep the top of the switches/sockets below 1200mm


  • Registered Users Posts: 227 ✭✭paddymick


    meercat wrote: »
    no,not a typo

    530.6
    1. switches for permanently connected appliances between 400-1200mm
    above floor level

    2.switches for lighting equipment
    in dwellings,between 400-1200mm above floor level
    in public and similar buildings,between 900-1200mm above floor level

    i would keep the top of the switches/sockets below 1200mm

    Your right of course Meercat:). force of habbit we always worked with 900-1200.

    Deleted the inaccurate post..


  • Registered Users Posts: 10,952 ✭✭✭✭Stoner


    Hi meercat
    thanks for the reply
    Is that from the top or bottom of the sockets and switches

    you can look at it in different ways, but as it's a range one good way to consider is to say within it, accessories 100% above the lower limit and 100% below the upper, this would fit meercats advice too.


  • Advertisement
  • Registered Users Posts: 27 Selfbuilderx


    Thanks everyone,
    What i'm going to do so is have the top of the switches at 1200mm and the bottom of the sockets at 400mm and i should be fine for building regs then.
    Thanks Again


  • Registered Users Posts: 27 Selfbuilderx


    One more question could ye recommend the hight for sockets for behind a fridge and behind a built in double oven?
    thanks Again


  • Banned (with Prison Access) Posts: 15,858 ✭✭✭✭paddy147


    Dont forget about socket/tv point heights on walls where you may be mounting a TV on the wall.


  • Registered Users Posts: 4,745 ✭✭✭meercat


    One more question could ye recommend the hight for sockets for behind a fridge and behind a built in double oven?
    thanks Again
    Between 400-1200 again
    Put them on a 20amp double pole switch that you can isolate the power if the socket is inaccessible


Advertisement