Kitchen Sink Live

Options
24

Comments

  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    meercat wrote: »
    Turn main switch off and test for voltage
    If voltage not present then turn power back on
    Turn power back on and then turn tripswitches off individually to determine source

    This installation sounds like it possibly has a long term mistake or problem, now shown up by a faulty appliance.


  • Registered Users Posts: 4,745 ✭✭✭meercat


    robbie7730 wrote: »
    It sounds like the sockets are fed from another point besides their own MCB, or a ring main to 2 different MCBs. It would be a seperate problem to the earthing problem though.

    agree with this

    johnpt
    "Turned off all circuits except kitchen still getting 120 volts between earth and neutral"

    where have you tested between (ie where did you place the probes for the earth and neutral to get 120v)?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    yes should be easy enough to clear up

    fault/faults on the final circuit causing 120volt shock voltage

    maybe another problem if one breaker doesn't isolate circuit

    prob best to get a inspection


  • Registered Users Posts: 2,454 ✭✭✭cast_iron


    JOHNPT wrote: »
    Turned off all circuits except kitchen still getting 120 volts between earth and neutral.
    If that also means that the 120v dies when you kill the kitchen circuit while all others are on, then the problem is isolated to the kitchen circuit.

    By your description of 2 points having 230v even though you have all legs disconnected, you either missed a point of the circuit, or more likely, there is a joint somewhere hidden that splits to these 2 sockets.

    This joint is a likely cause of the problem, or a damaged cable upstream of the 2 remaining live points.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    There can be a few causes. 120v between earth and neutral would be a sign of an open earth on a circuit, with a faulty appliance connected to that circuit, or an earth fault in an installation on any circuit, with no neutralising connection at the meter.

    If you actualy get a digital meter and test from live to an open ended earth not connected to the earth bar in the DB, or a sink with no earth or copper pipes connected to it, 120v would easily be shown by the meter.

    So there are lots of permutations to this. But a socket circuit with a sound earth, and a neutralised installation, should show 0v Neutral to Earth at the socket. (even with reverse polarity at the meter)

    Now if the socket circuit itself has reverse polarity, and the CPC of the circuit is open, there is another scenario to read 120v Neutral to Earth at a socket (on a digital multimeter).


  • Advertisement
  • Registered Users Posts: 4,745 ✭✭✭meercat


    robbie7730 wrote: »
    There can be a few causes. 120v between earth and neutral would be a sign of an open earth on a circuit, with a faulty appliance connected to that circuit, or an earth fault in an installation on any circuit, with no neutralising connection at the meter.

    If you actualy get a digital meter and test from live to an open ended earth not connected to the earth bar in the DB, or a sink with no earth or copper pipes connected to it, 120v would easily be shown by the meter.

    So there are lots of permutations to this. But a socket circuit with a sound earth, and a neutralised installation, should show 0v Neutral to Earth at the socket. (even with reverse polarity at the meter)

    Agree
    That's why I asked where was he testing from
    If he has disconnected the sockets then he may have disconnected the localised bonding to the sink


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    meercat wrote: »
    Agree
    That's why I asked where was he testing from
    If he has disconnected the sockets then he may have disconnected the localised bonding to the sink

    If the socket circuit has an open earth, many assume a digital meter will read 0v live to earth. But it never will. It will be well up toward 100v and likely well above it, due to the meters very high impedence in a now high impedence circuit (open earth), but a person in contact with the same points would have almost 0v across them. And neutral to this earth will also read above 0v if there is a faulty appliance connected to this socket in the kitchen if it has an open earth, and/or no neutralising.

    So if this socket circuit is open, then the sink probably has no bonding anyway like you say. Thats if the sink ever had any.

    A loop impedence tester into the socket would be handy, but its simple to do quick tests to see if the socket has proper polarity, and a good earth back to the DB, two fundamentals needed to be checked there, as well as making sure only one MCB is supplying the circuit by the sounds of the other problem mentioned.


  • Registered Users Posts: 2,454 ✭✭✭cast_iron


    I's agree with robbie (don't we all:D)

    The short version is that there's highly likely to be a bad connection somewhere in the circuit.
    I've come across an identical problem before, with the meter giving the same seemingly strange readings. It was a matter of tracking it down to a failed connection at a socket, though could equally have been a bad connection at a joint.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    cast_iron wrote: »
    I've come across an identical problem before, with the meter giving the same seemingly strange readings. It was a matter of tracking it down to a failed connection at a socket, though could equally have been a bad connection at a joint.

    Last time i seen similar was when the house had over 300v at the sockets. So straight away i was onto the esb suggesting it was probably a neutral failure. It was the neutral gone at the mini pillar. Switching on a heavy item such as a cooker would transfer more of the voltage to another affected house. Not the problem here with 230v measured of course.

    Everything in the house was ruined.

    This type of problem is where the bonding of all metal is important, with neutralised installations.

    A good chance of a hidden joint as part of the problem in this thread alright.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    robbie7730 wrote: »
    There can be a few causes. 120v between earth and neutral would be a sign of an open earth on a circuit, with a faulty appliance connected to that circuit, or an earth fault in an installation on any circuit, with no neutralising connection at the meter.

    If you actualy get a digital meter and test from live to an open ended earth not connected to the earth bar in the DB, or a sink with no earth or copper pipes connected to it, 120v would easily be shown by the meter.

    So there are lots of permutations to this. But a socket circuit with a sound earth, and a neutralised installation, should show 0v Neutral to Earth at the socket. (even with reverse polarity at the meter)

    Now if the socket circuit itself has reverse polarity, and the CPC of the circuit is open, there is another scenario to read 120v Neutral to Earth at a socket (on a digital multimeter).

    problem is confined to kitchen

    he got a severe shock

    so obviously not phantom voltage or neutralizing

    there's usually a few permutations on the obvious alright


  • Advertisement
  • Registered Users Posts: 4,745 ✭✭✭meercat


    M cebee wrote: »
    problem is confined to kitchen

    he got a severe shock

    so obviously not phantom voltage or neutralizing

    there's usually a few permutations on the obvious alright

    wouldnt be too sure about that(most likely though)

    different potentials between earths

    there are probably no other locations in the installation where there are appliances that he could get different potentials between earths


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    dso neutral bad connection

    or no neutralizing+fault

    everything connected to met is live


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    problem is confined to kitchen

    he got a severe shock

    so obviously not phantom voltage or neutralizing

    there's usually a few permutations on the obvious alright

    I was talking about a few causes of the 120v between neutral and earth at the socket. And i mention the multimeter displaying a good voltage in some situations because it can add to the confusion.

    The socket circuit is the first place to look, and test, when there is a PD between that socket neutral and earth.

    A severe shock from 120v would be unlikely.

    No neutralising on a bonded system that should be neutralised (no main RCD) and an earth fault could leave up to the 230v between an earthed appliance and a non bonded but indirectly earthed sink etc.

    The kitchen is the only place the shock problem has been noticed. It may not be confined to there.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    I saw 39v on some 2 wayed led downlights today

    measured with fluke dmm
    flicker dissapeared when I stuck in 1 halogen bulb

    not quite sure ,i assume its induced voltage


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    If i was to just take a wild guess, id have a go at earth missing on socket circuit to kitchen, and earth fault appliance.

    But a few quick tests should find the actual problem, but the actual location might be harder to find, such as possible hidden JB etc.


  • Closed Accounts Posts: 3,327 ✭✭✭Merch


    While I'm not an electrician, I started reading the thread earlier and came back to see if a solution had been found,

    from an outside perspective, I assume other possibilities have been considered, maybe something an electrician wouldnt consider (or maybe they would?)
    so
    Has there been any recent work down, sockets? even lighting? maybe someone had previously powered lights through sockets or vica versa?? could try switch off the lighting circuit too to test? or maybe there is a fault in an individual appliance? maybe someone has changed a plug/socket and has been wired in correctly, re N, L, E? (that may have been discussed, I admit I didnt read the thread thoroughly, just giving my 2p's worth)


  • Registered Users Posts: 4,745 ✭✭✭meercat


    were all waiting for the solution:D

    good points merch but i would hope the op has ruled them all out by now


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    I saw 39v on some 2 wayed led downlights today

    measured with fluke dmm
    flicker dissapeared when I stuck in 1 halogen bulb

    not quite sure ,i assume its induced voltage

    Yea you will see that on cfl`s as well, or with no bulb fitted. The induced voltage in the strapper thats off appears on the live terminal of the bulb fitting of cfl`s and electronic fittings because the impedence through them to the neutral terminal is so high.

    Fit an incandescent and the impedence is now relatively very low, making a good connection between the switched off live terminal of the fitting (and the off strapper), and neutral. So it shows no induced voltage.

    Strappers show this induced voltage because they normally follow the same route, although because there is no current flow with the light off, capacitance is probably more likely. It is enough to sometimes dimly light phase testers too.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    robbie7730 wrote: »
    M cebee wrote: »
    problem is confined to kitchen

    he got a severe shock

    so obviously not phantom voltage or neutralizing

    there's usually a few permutations on the obvious alright

    I was talking about a few causes of the 120v between neutral and earth at the socket. And i mention the multimeter displaying a good voltage in some situations because it can add to the confusion.

    The socket circuit is the first place to look, and test, when there is a PD between that socket neutral and earth.

    A severe shock from 120v would be unlikely.

    No neutralising on a bonded system that should be neutralised (no main RCD) and an earth fault could leave up to the 230v between an earthed appliance and a non bonded but indirectly earthed sink etc.

    The kitchen is the only place the shock problem has been noticed. It may not be confined to there.

    ya I must go back and check thread

    maybe it was just a good tingle or a bad rattle


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    robbie7730 wrote: »
    cast_iron wrote: »
    I've come across an identical problem before, with the meter giving the same seemingly strange readings. It was a matter of tracking it down to a failed connection at a socket, though could equally have been a bad connection at a joint.

    Last time i seen similar was when the house had over 300v at the sockets. So straight away i was onto the esb suggesting it was probably a neutral failure. It was the neutral gone at the mini pillar. Switching on a heavy item such as a cooker would transfer more of the voltage to another affected house. Not the problem here with 230v measured of course.

    Everything in the house was ruined.

    This type of problem is where the bonding of all metal is important, with neutralised installations.

    A good chance of a hidden joint as part of the problem in this thread alright.


    ive seen it happen
    a lot to be said for external power supplies on equipment when this happens-a simple swop

    im sure a lot of undervoltage and overvoltage damage goes unreported


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    ive seen it happen
    a lot to be said for external power supplies on equipment when this happens-a simple swop

    im sure a lot of undervoltage and overvoltage damage goes unreported

    Yea id say it does.


  • Closed Accounts Posts: 517 ✭✭✭JOHNPT


    Problem fixed. There was a junction box in a cupboard in the bathroom - which was behind kitchen. See pictures. Cables were joined in this - hence one cable from fuseboard to junction box - was joined to seperate cables feeding kitchen sockets - cables probably damaged or cut too short initially. Earth connections were very bad hence what i was picking up was a floating earth. The earth connection you can see in picture is new connectors i put in

    Thanks for all the help and replies.


  • Registered Users Posts: 4,745 ✭✭✭meercat


    robbie7730 wrote: »
    If i was to just take a wild guess, id have a go at earth missing on socket circuit to kitchen, and earth fault appliance.

    But a few quick tests should find the actual problem, but the actual location might be harder to find, such as possible hidden JB etc.


    spot on robbie

    induced voltage as it seems the earth wire was not connected to the kitchen socket circuits


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    meercat wrote: »
    robbie7730 wrote: »
    If i was to just take a wild guess, id have a go at earth missing on socket circuit to kitchen, and earth fault appliance.

    But a few quick tests should find the actual problem, but the actual location might be harder to find, such as possible hidden JB etc.


    spot on robbie

    induced voltage as it seems the earth wire was not connected to the kitchen socket circuits

    I doubt it

    the induced voltge alone doesnt deliver shock

    an additional fault is needed

    pretty much as discussd


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    I doubt it

    the induced voltge alone doesnt deliver shock

    an additional fault is needed

    pretty much as discussd

    Indeed, open circuit earth with earth fault on appliance likely, if there where shocks being received.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    might still be fault current here
    dunno is rcd even working

    I would be advising complete inspection
    considering the cockups already found


  • Registered Users Posts: 2,454 ✭✭✭cast_iron


    meercat wrote: »
    spot on robbie
    Ah now hold on, I said it first :P
    cast_iron wrote:
    ...or more likely, there is a joint somewhere hidden that splits to these 2 sockets.

    This joint is a likely cause of the problem...
    Doesn't solve the shock issue though.


  • Registered Users Posts: 4,745 ✭✭✭meercat


    cast_iron wrote: »
    Ah now hold on, I said it first :P
    Doesn't solve the shock issue though.

    mea culpa


  • Closed Accounts Posts: 517 ✭✭✭JOHNPT


    You only got a shock when you touched dishwasher or washing machine and then touched the sink (which was bonded) at the same time. Is this not possible with induced voltage?


  • Advertisement
  • Closed Accounts Posts: 3,327 ✭✭✭Merch


    JOHNPT wrote: »
    You only got a shock when you touched dishwasher or washing machine and then touched the sink (which was bonded) at the same time. Is this not possible with induced voltage?

    Induced voltage? induction is when a a magnetic field is formed and collapses, a voltage is induced (in a coil), have to look it up to be exact (i should know)
    to me
    what you are saying sounds like an earth fault in either/both of those appliances?
    If there is an earth fault, shouldn't the main breaker trip?

    The earth of the plug of either of those devices should make continuity with the metal case (where there is bare metal or at the point an earth wire is connected),
    Possibly continuity of the earths at the sockets where these appliances are connected and some other earth should be checked?

    sounds dangerous,
    I've read of this before, where there is enough current to give a shock (and depending on the person, the effects vary) but not trip the breaker, is the right type of breaker installed?