Compressor plug

Options
  • 27-04-2012 9:18pm
    #1
    Registered Users Posts: 73 ✭✭


    Bought a compressor today but there are four wires for the plug black,blue,brown and green/yellow how do I wire this????


Comments

  • Registered Users Posts: 4,745 ✭✭✭meercat


    any chance of pic of the ratings plate(i.e voltage and amp)
    or a link to the compressor


  • Registered Users Posts: 73 ✭✭paul127


    It turns out it a three phase induction motor its a 3hp / 2 · 2kw volts 230 / 400 amps 9.0 / 5.3 can this be run by single phase?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    paul127 wrote: »
    It turns out it a three phase induction motor its a 3hp / 2 · 2kw volts 230 / 400 amps 9.0 / 5.3 can this be run by single phase?

    no I dont think so

    I think its probably 3 phase dual voltage


  • Registered Users Posts: 3,387 ✭✭✭glynf


    Yes you can run it off single phase, the easiest way would be using a Variable Speed Drive. most VSD's can convert 240V single phase to 240V three phase by rectifying the input 1phase into DC and then converting this to a 3phase output. AFAIK as a rule of thumb you need to double the rating of the VSD if you are using it for this, so you would need a 4kw VSD.

    Couple of things to consider though..

    Is it worth the hassle-can you return it & get a single phase model?

    Cost-even a bog standard VSD would set you back 200 minimum, plus cost to fit & setup. Know that all VSD's can be used to run a 3 phase motor, but some manufacturers lock out the option to do so in the setup menus. Last time I did this (a fair few years back) I used an ABB unit.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    yes the vsd will supply 230v 3-phase but not worth the expense probably

    2.2kw /3hp is a standard size

    the SP model runs off a 16amp plug if i recall