Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

nibe fighter 1245 running costs

13

Comments

  • Registered Users Posts: 18 pgkilro


    So Liamolaighin, for seven days of the week you have the schedule 1 set from 12.00am to 2pm at -1, schedule 2 set from 2pm to 6pm at +3 and schedule 3 set from 6pm to 12.00am at 0?


  • Registered Users Posts: 18 pgkilro


    Also, if anyone has their proposed schedules for the summer that would be great.....house has been very hot last few days with the sun. Average about 25 degrees. Have reduced the temp curve to -3. No schedules currently in place for either the heat or hot water, but electricity bills still not too bad. For two months (Feb & March) our total electricity bill was 340.00. Thats for everything, but I think it could be better if the Nibe wasn't running all day.

    One other thing, going on holiday for a week next month, should we turn off the Nibe altogether or just use the holiday scheduler?


  • Registered Users Posts: 651 ✭✭✭badgerhowlin


    PgKilro. I turn off the heating altogether for the summer, Mid May was when it was turned off last year.

    Like you my house has been low to mid 20s, so last night I truned the heat curve to 1 and -5.

    As for schedules. You will save a good bit if you put them on. Especially if you have your water heating on a timer.

    Below is my Schedules,

    Hot water
    Schedule 1
    mon 06:00 - 02.00 OFF
    Tues 06:00 - 02.00 OFF
    Wed 06:00 - 02.00 OFF
    Thurs 06:00 - 02.00 OFF
    Fri 06:00 - 02.00 OFF
    Sat 06:00 - 02.00 OFF
    Sun 06:00 - 02.00 OFF

    Heating
    Schedule 1
    mon 02:30 - 06.00 +4
    Tues 02:30 - 06.00 +4
    Wed 02:30 - 06.00 +4
    Thurs 02:30 - 06.00 +4
    Fri 02:30 - 06.00 +4
    Sat 02:30 - 06.00 +4
    Sun 02:30 - 06.00 +4

    Schedule 2
    mon 06:00 - 21.00 -3
    Tues 06:00 - 21.00 -3
    Wed 06:00 - 21.00 -3
    Thurs 06:00 - 21.00 -3
    Fri 06:00 - 21.00 -3
    Sat 06:00 - 21.00 -3
    Sun 06:00 - 21.00 -3

    Schedule 3
    mon 21:15- 02.00 +2
    Tues 21:15- 02.00 +2
    Wed 21:15- 02.00 +2
    Thurs 21:15- 02.00 +2
    Fri 21:15- 02.00 +2
    Sat 21:15- 02.00 +2
    Sun 21:15- 02.00 +2

    As for your holiday next month. If its late May I would turn off your heating altogether if i was you. And as for hot water if you have the water heating at night I would schedual it to be off untill the night before you come back.
    I have never used the Holiday scheduler.


  • Registered Users Posts: 18 pgkilro


    Thanks Badger...three quick questions:
    1) How do you turn your heat curve to 1 and -5? I only have the option to change one number? Hence I changed to -3.
    2) So you turn off the water heating from 6am to 2am. Do you not need to add a schedule 2 to come on again at 2.15am to 5.45am? Also, is there enough hot water for night time showers?
    3) Does the schedule override the actual heat curve settings e.g. I've set mine to -3 now, but if I follow your schedule this will be overridden by the schedule?


  • Registered Users Posts: 651 ✭✭✭badgerhowlin


    pgkilro wrote: »
    Thanks Badger...three quick questions:
    1) How do you turn your heat curve to 1 and -5? I only have the option to change one number? Hence I changed to -3.
    2) So you turn off the water heating from 6am to 2am. Do you not need to add a schedule 2 to come on again at 2.15am to 5.45am? Also, is there enough hot water for night time showers?
    3) Does the schedule override the actual heat curve settings e.g. I've set mine to -3 now, but if I follow your schedule this will be overridden by the schedule?

    Sorry havent be on page for a while.

    Ill try and answer your questions tonight wheni get home


  • Advertisement
  • Registered Users Posts: 651 ✭✭✭badgerhowlin


    Just finished my 2nd years running.

    Total cost of ESB for house was (€1039.97) down from last years bill(€1080.67)

    Total units used on hit pump was(2164) down from last year(2758)

    Total cost of running HP last year was €369.66. Detailed reading for this can be found on https://docs.google.com/spreadsheet/ccc?key=0Amy6xlLdiDpQdENDa0ZTdkM3S3hfc3BHeURYQ1ZWZkE&pli=1#gid=2

    SO
    (this is all guess work from here on)
    If I divide units used last year 2758 by total spent on heating last year €369.66. I get average cost per unit .13323.
    multiply average cost per unit by total units used this year 2164. I get €290.05


  • Registered Users, Registered Users 2 Posts: 12,134 ✭✭✭✭KCross


    pgkilro wrote: »
    Also, if anyone has their proposed schedules for the summer that would be great.....house has been very hot last few days with the sun. Average about 25 degrees. Have reduced the temp curve to -3. No schedules currently in place for either the heat or hot water, but electricity bills still not too bad. For two months (Feb & March) our total electricity bill was 340.00. Thats for everything, but I think it could be better if the Nibe wasn't running all day.

    One other thing, going on holiday for a week next month, should we turn off the Nibe altogether or just use the holiday scheduler?


    You should not need to mess with the schedules between winter/summer. Once you get settings that work for winter the summer is largely irrelevant because the HP will automatically stop space heating when the average outside temperature goes above a certain value. Changing the curve or heat schedules during the summer will have little effect because it will be off anyway except for hot water.

    For hot water, unless you use alot of it, I'd recommend a schedule that has ALL the hot water heating done at around 6am-8am. We have a house of 5 and we rarely use all the water so by limiting it to night saver electricity you get maximum savings on the water heating.


    To check the "summer cut off" settings look here...

    Under HeatPump-->advanced-->auto mode settings
    There are 3 settings in there....
    stop heating, stop additional heat, filter time

    My settings for those 3 are
    15,5,24

    If you want it to turn itself off sooner, change the 15 to a lower temperature.

    You can check the average outdoor temperature recorded by your Nibe under
    info-->service info-->avg. outdoor temperature



    In relation to holidays, I would use the holiday scheduler. You set the start and end date and it will mean that when you come back you will have hot water as you will set the end date to the day before you come back. If you turn it off completely you wont have any hot water when you come back.


  • Registered Users Posts: 222 ✭✭Rushy Fields


    Not sure is this correct thread but i have a problem with my underfloor system heated by a nibe fighter 1145 with 300ltr cylinder in hotpress. digital thermostats upstairs in each bedroom (4) One of the bedrooms is cold.... not as warm as other rooms all 4 rooms set at 22 degrees on the stats. Actuators wiring have been checked and they seem to work. When i take off all actuators from manifold the cold room gets warm but another room adjacent to this room gets too warm 25-26degrees. Anyone ave words of wisdom? Heat pump set at heating curve 4. Had guy out with thermal imaging camera to check for leaks and any heat loss but none found.


  • Registered Users, Registered Users 2 Posts: 12,134 ✭✭✭✭KCross


    nealger wrote: »
    Not sure is this correct thread but i have a problem with my underfloor system heated by a nibe fighter 1145 with 300ltr cylinder in hotpress. digital thermostats upstairs in each bedroom (4) One of the bedrooms is cold.... not as warm as other rooms all 4 rooms set at 22 degrees on the stats. Actuators wiring have been checked and they seem to work. When i take off all actuators from manifold the cold room gets warm but another room adjacent to this room gets too warm 25-26degrees. Anyone ave words of wisdom? Heat pump set at heating curve 4. Had guy out with thermal imaging camera to check for leaks and any heat loss but none found.

    Maybe actuators are on the wrong feeds and when you take all actuators off all rooms are getting their full flow and the room that is then getting too warm has simply got too high a flow rate. When the actuators are on, that hot room is still getting the full flow but the actuator for that room is stopping its flow so that it doesnt get to 25C.

    You said you checked actuator wiring. Does that mean you just checked that the stat was driving the actuator or did you also check that you have the actuator on the right feed of the manifold?

    I doubt the heat curve or HP settings matter here.


  • Registered Users, Registered Users 2 Posts: 64 ✭✭soundskin


    I Agree with KCross, make sure the right correct stat is connected to it's actuator and most importantly that actuator is on the right valve for that stat. So Master stat in onto actuator that feeds master bedroom. Sounds simple but is wrong so many times.

    Step by step method is turn down all stats but one, after a day then only that room should be warm.

    If the room heated up but not was warm as others when it was removed then up the flow rate to that room, flow rates are there to match heat loss. Balancing flow rates will result in even temps. I'd imagine this is your issue if you rule out the wiring and actuator locations.

    If your rooms are getting to 24-25 degrees then you may have to look at your heat pump, thats a very high temp (only to be limiting by the stats). You might be running your heat pump too high only to have the stats stopping overheating. That is bad.

    Do you have stats on the GF? what i is the temp like there?


  • Advertisement
  • Registered Users Posts: 222 ✭✭Rushy Fields


    soundskin wrote: »
    I Agree with KCross, make sure the right correct stat is connected to it's actuator and most importantly that actuator is on the right valve for that stat. So Master stat in onto actuator that feeds master bedroom. Sounds simple but is wrong so many times.

    Step by step method is turn down all stats but one, after a day then only that room should be warm.


    If the room heated up but not was warm as others when it was removed then up the flow rate to that room, flow rates are there to match heat loss. Balancing flow rates will result in even temps. I'd imagine this is your issue if you rule out the wiring and actuator locations.

    If your rooms are getting to 24-25 degrees then you may have to look at your heat pump, thats a very high temp (only to be limiting by the stats). You might be running your heat pump too high only to have the stats stopping overheating. That is bad.

    Do you have stats on the GF? what i is the temp like there?

    Have one stat and two actuators in one room downstairs. The remaining rooms have no stats. I know temps are too warm. How do i turn down or up flow rates? This is all new to me, should i get someone in to have a look? How do i check heat pump? Temp on heatpump set at 23. MY OH is a cold creature. Anything less than 22 is cold!!! Took actuators traced wires from actuators to stats then turned up room wiyh stat and actuator on valve to see did it move and it did. The cold room went up but room didnt get warm..... confused😩


  • Registered Users, Registered Users 2 Posts: 12,134 ✭✭✭✭KCross


    nealger wrote: »
    Have one stat and two actuators in one room downstairs. The remaining rooms have no stats. I know temps are too warm. How do i turn down or up flow rates? This is all new to me, should i get someone in to have a look? How do i check heat pump? Temp on heatpump set at 23. MY OH is a cold creature. Anything less than 22 is cold!!! Took actuators traced wires from actuators to stats then turned up room wiyh stat and actuator on valve to see did it move and it did. The cold room went up but room didnt get warm..... confused😩

    On the manifold where you connect the actuator, there should be a flow rate adjustment for each feed. Turn it one way and it will increase the flow and vice versa. More flow, more heat. You should turn it up a little at a time and see how it reacts after 24hrs.

    So, when the stat was turned up and the room got warmer, but not warm enough, it probably means that the flow rate is too low. Increasing the flow rate to that feed will pump more heat into that room.

    Maybe if you posted a picture of the manifold it would help to explain.

    To turn the HP down you need to reduce the heat curve in the HP settings. Thats in the heat pump menu, advanced, heating curve..... what is that set to in your system?

    Since it is all new to you I think you would benefit from someone coming onsite and giving you some training on it as it is likely you will need to tweak it some more in the months ahead to get it right. Having a full understanding of what you are doing is vital here.


  • Registered Users Posts: 12 Jackofaltrades


    Hi,
    I have a NIBE 1140 installed in 2007 and I cant say that I am all that happy with it.
    I have been playing about with the setting but I am still averaging €2p/d normal up to €8p/d freezing. (3000sqft 2 floors UFH + RADS 2nd flr).
    I have tried setting back the temp during the daytime and heating extra HW at night (on nightsaver) but no improvement on my bills.

    Would anybody have some recommended settings for the 1140 please, I think my heat pump should be better than this from reading this post.

    Thanks in advance for your help.

    Jack.


  • Registered Users Posts: 60 ✭✭Gunslinger99


    Hi Jack, sounds to me like you're doing ok. You're heating a 3000 sq foot house for approx € 1400 a year does that sound right ? How many tanks of oil would a house that size go through in a year ? 3 or 4 would be my guess. If you want some help with settings drop an email to Unipipe and they'll help you out ( after xmas id say they're very busy this time of year ). Good luck


  • Registered Users Posts: 12 Jackofaltrades


    Hi Gunslinger,
    Just from looking at badgerhowlins costs of €370 a year I thought maybe I should be doing a bit better!


  • Registered Users, Registered Users 2 Posts: 1,739 ✭✭✭hexosan


    Hi Gunslinger,
    Just from looking at badgerhowlins costs of €370 a year I thought maybe I should be doing a bit better!

    How well insulated and how airtight is your house.

    Have you 4" vents in the walls.


  • Registered Users Posts: 12 Jackofaltrades


    Hi,
    Yeah, 4" vents and 2 chimneys, need to do something about them!


  • Registered Users, Registered Users 2 Posts: 1,739 ✭✭✭hexosan


    Hi,
    Yeah, 4" vents and 2 chimneys, need to do something about them!

    You can't just go blocking them up but I'd say it's the reason your bills are higher.


  • Registered Users Posts: 5 villa fan


    Hello all,
    I've 1245 in for 4 years,I have it off for the summer, switched to manual and heating hot water only. I have a buffer tank and didn't want to be heating this at night if it not going to be used. I'm happy with the system so far, it works well during winter, heats up a reserve of heat for underfloor on night rate that feeds in to floor when necessary during the day.the problem I have now is that hp high pressure alarm 50 has been coming on this week. I reset it a few times but the red light started to come on more often so contacted installer Thursday but he didn't come out yet. When left with red light on the buffer tank has started to heatup? I put it standby mode but still the buffer has heated up today. Why is this happening? I don't want to cut the Power switch as I'd be afraid this could cause further damage with refrigerant or would it be okay to do so? Any help would be appreciated. I put the heat pump back on their now and set it to auto, see will it make any difference. A bit concerned that one of the pressure gauges is reading lower than usual also but not sure. Have found this forum beneficial in the past so thanks to all who post here.


  • Registered Users Posts: 12 Jackofaltrades


    Hi Villa Fan
    I have previously had this alarm also - I think it happens when you build up to much heat/pressure in the system and dont release it to the floor i.e using temp set back.
    Not sure how to fix it bar balancing your heat generation with your usage.


  • Advertisement
  • Registered Users Posts: 317 ✭✭hatchman


    What have temp have u set for "stop heating" in 4.9.2 auto mode setting ? If this is low enough the heatpump won't try to heat floor/buffer tank. I've mine set at 12 and filtering time 24 hrs. Set it this low to make sure pump didn't heat floor during our so called summer will up it a bit when days and nights get a bit colder.

    If u don't need it for domestic hot water power it down will do know harm AFAIK and wait for engineer.


  • Registered Users Posts: 12 Jackofaltrades


    Just to add, I have an 1140 and when I just want to the pump to heat the hot water I set the pump to summer mode and rarely/never get the HP alarm, when I do I just power off/on the heat pump.


  • Registered Users Posts: 222 ✭✭Rushy Fields


    Hi. Can anyone recommend someone to service my Nibe F1145 Geothermal heatpump and 300l cylinder. General overall service. PM me. Located near Galway Roscommon border.....


  • Registered Users Posts: 5 villa fan


    Hi all,
    Just wondering how lads are finding this system at present, how are you scheduling it now, have it in since 2012, found last year cost went up but have 3 kids and need for more heat probably the reason but would like to see if anyone has tweaked settings or scheduling in any way. Do ye change electricity supplier often or find one better than another? Had a few problems with stats failing, had to replace 6. Is this common? Servicing every 2 years? A simple question, where are filters situated to clean them, 2 I think isn’t it?
    Air to water heat pumps seem to be very popular at present.
    Thanks for any responses


  • Registered Users, Registered Users 2 Posts: 12,134 ✭✭✭✭KCross


    villa fan wrote: »
    Hi all,
    Just wondering how lads are finding this system at present, how are you scheduling it now, have it in since 2012, found last year cost went up but have 3 kids and need for more heat probably the reason but would like to see if anyone has tweaked settings or scheduling in any way.

    If your running costs have gone up and you havent changed anything, it might be worth getting a service and get stats and filters checked.


    villa fan wrote: »
    Do ye change electricity supplier often...?

    Yes, and you should do that regardless of having a HP or not. Its the only way to get the best electricity deals.

    The only difference between one provider and the other is customer service and if you do your own meter readings you will have no need for their customer service.... thats my experience anyway.

    I flip flop between airtricity and Energia as they seem to offer the best deals.

    Currently paying 16.41/8.12 inc vat for day/night.

    villa fan wrote: »
    Had a few problems with stats failing, had to replace 6. Is this common?

    I havent had any fail in 7 years. I have digital Salus stats.

    villa fan wrote: »
    Servicing every 2 years? A simple question, where are filters situated to clean them, 2 I think isn’t it?

    You'd need to post a pic of your plumbing to have that pointed out.

    If you are getting it serviced every 2 years not much need for you to mess with the filters as that will have been done anyway.

    You'd need to be careful you dont open the wrong nut and spill the contents of the system on your floor and have to repressurise it etc. Maybe get a service done and get the service guy to show you how to clean the filters without f*cking it up.


  • Registered Users Posts: 19 MikeKaiserBud


    Just a comment on using the thermostats. I have them in all rooms and hallway and used to set them carefully. Upshot was that the system was turning off and on alot - the compressor was being switched far too often as each stat 'called' it to come on. A couple of years ago I had a service visit and the guy recommended to ignore the stats completely and to set the conditions in the control unit itself. We like the temperature about 19 degrees and he used his gut instinct for choosing the heating curve etc. He disconnected the leads in the boxed off valves system. I can't be any more specific as I'm not an expert on the controller. The compressor switches less frequently (supposed to extend the life). I used to turn it all off over the summer months too but again he advised leaving it running all year as only the low power circulation pump is in use when the system is not heating. I found that there was hardly any change in the costs when these changes were made. Best of luck


  • Registered Users Posts: 95 ✭✭Tmurf


    Hey Villa,
    I change my supplier, I find the best supplier is the one with the best deal, you can knock a good few quid a month off the bill by changing.
    I have disconnected my stats as they had a manual dial and I found some rooms would be a bit colder as there was a 3 to 4 deg difference in the dial between switching.
    I have the heat curve at 3 but drop it to 2 sometimes.
    I have attached the heating schedules.
    I have a meter on the pump so I can work out the yearly price.
    Last 2 years coming in under €700
    20190114_173402.jpg

    20190114_173412.jpg

    20190114_173424.jpg


  • Registered Users Posts: 222 ✭✭Rushy Fields


    Hi,
    Does anyone have a contact for servicing a NIBE F1145 Geothermal Heat Pump? Location is Galway Roscommon Border Area. So anyone in counties Roscommon Galway Mayo Westmeath Longford or Offaly would be ideal.


  • Registered Users Posts: 651 ✭✭✭badgerhowlin


    Hi,
    Does anyone have a contact for servicing a NIBE F1145 Geothermal Heat Pump? Location is Galway Roscommon Border Area. So anyone in counties Roscommon Galway Mayo Westmeath Longford or Offaly would be ideal.

    Hope you find one. I cant find anyone to look at mine in wexford.


  • Advertisement
  • Registered Users Posts: 1 MartinHeather


    There's a chap called Alex Byrne who services NIBE systems in the north Connaught and Donegal areas (086 2625002) - maybe he'll have some info if he doesn' t go as far as Roscommon/Galway. If you haven't done so already you could try the NIBE suppliers Unipipe in Bray (01-2864888) as they may have a list of service companies. Best of luck


Advertisement