    Just checking a couple of points on the wiring of Point ID devices and linked contacts:

    1. When you're using Point ID devices, do you need to wire a tamper circuit or does the data wire carry tamper signals as well as alarm signals?

    2. If I wire additional contacts into a Point ID sensor, do the sensor's electronics pick up tampers on the contact circuits or do I need to wire those tampers separately?

    Thanks in advance.


Comments

  • Registered Users Posts: 11,719 ✭✭✭✭altor


    DartryK wrote: »
    Hi Folks,

    Just checking a couple of points on the wiring of Point ID devices and linked contacts:

    1. When you're using Point ID devices, do you need to wire a tamper circuit or does the data wire carry tamper signals as well as alarm signals?

    2. If I wire additional contacts into a Point ID sensor, do the sensor's electronics pick up tampers on the contact circuits or do I need to wire those tampers separately?

    Thanks in advance.

    Point id sensors just need a 12v supply and the a data core.
    If you wire additional sensors from the sensor alarm and tamper input on the id sensor then the sensor will do the rest.


  • Registered Users Posts: 16 DartryK


    Thanks Altor, much appreciated. I thought that was probably the case but no harm in checking.

    Rgds


  • Registered Users Posts: 11,719 ✭✭✭✭altor


    DartryK wrote: »
    Thanks Altor, much appreciated. I thought that was probably the case but no harm in checking.

    Rgds

    Your welcome, no hard in checking first :D


  • Registered Users Posts: 16 DartryK


    My electrician didn't follow my wiring instructions properly and I now have a problem with the wiring for tying in additional contacts to my ID sensors. In summary, I have a 6 core cable of which 3 cores will be used for the ID sensor power and data, leaving me with only 3 cores available to wire both contact inputs and tampers (inputs 1+6 and 3+4 on the ID sensor).

    Can I double up on the return lines for contact and tamper, ie can I use 1 core for output to contact, 1 for tamper output and the remaining core as a common return for both circuits? I know ideally there should be two wires for each but this seems a logical alternative assuming that both contact and tamper circuits are NC and operate on similar voltage and standby current.

    If I can get away with this configuration, then which terminals on the sensor do I need to loop together so that the sensor can tell whether the contact or tamper circuit has been broken (options would be 1 and 3, 1 and 4, 6 and 3 or 6 and 4)?

    Thanks again in advance.


  • Registered Users Posts: 6,827 ✭✭✭fred funk }{


    You only need three cores back to the panel. Power and data. The alarm and tamper inputs are for wiring additional detectors into that.


  • Advertisement
  • Registered Users Posts: 16 DartryK


    Thanks Fred Funk, but that's not quite answered my question. I know that I only need 3 wires for the ID sensor. I am talking about wiring in additional contacts as you mention. The problem is that my electrician has run the cables in such a way that I only have 3 spare cores available to wire the additional contact and tamper circuits instead of the usual 4 cores.

    What I am trying to find out is if I can use one of the three spare cores as a common return for the contact and tamper circuits and if so, how should I wire it back to the ID sensor.

    Thanks.


  • Registered Users Posts: 6,827 ✭✭✭fred funk }{


    Has he wired them all in single cables? Don't think the alarm and tamper inputs share a common negative. Can you not use an expander if they are wired singularly.


  • Registered Users Posts: 16 DartryK


    Hi Fred Funk,

    I asked the electrician to loop from one ID sensor point to the next and leave tails for each of the additional contacts. So I should have had 6 cores available for each contact to tie back to the relevant sensor.

    What he actually did was to run a single cable from the sensor point through each of the contact locations before continuing to the next sensor point, so I am forced to use 3 of the cores for the ID sensor power and data all the way through. This leaves me with only 3 cores everywhere to wire the contacts back to the sensors.

    As you say, normally the contact and tamper inputs to the sensor would be separate (terminals 1 and 6 for contact, 3 and 4 for tamper), but I'm just wondering if you could link them so the two circuits have a common return. If the two circuits operate in a similar way then it should work (just the same way that you would link up neutrals in a mains circuit), but I'm only guessing here...


  • Registered Users Posts: 6,827 ✭✭✭fred funk }{


    Why can't you put the ID sensor on at the first point on the cable run? then you'd have a six core back to the sensor.

    Most other systems use a common negitive on one side of the zone input but I don't think HKC works that way.