Question regarding american equipment to be used in Ireland. Volts etc

Options
  • 12-06-2012 1:55pm
    #1
    Registered Users Posts: 2,104 ✭✭✭


    Hi all,

    I am looking to purchase two pieces of equipment with the below specs:


    PHASE=1 VOLTS=208 AMPS=20.1
    PHASE=1 VOLTS=115

    What would it take to get this equipment working in Ireland?

    Many thanks,

    S.


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    you'll need a couple of trafos

    have they confirmed the equipment is ok on 50hz

    the first trafo will need to be a 5kva step down

    the second is a step down as well


    you can get them with a 400v or 230v primary


  • Registered Users Posts: 2,104 ✭✭✭Swampy


    It says the equipment can take 50/60.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    do you have any links?

    if they're definitely SP and not 3-phase or split phase machines it should be straightforward anyhow


    i didn't think 115v was a US nominal voltage

    afaik they use 120/240 for domestic and the 208 is a 3-phase line voltage over there


  • Registered Users Posts: 2,104 ✭✭✭Swampy


    They are 3 phase. I'll try and get the exact specs and post them here.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    sounds more like 7.5kva so.

    400v 3phase to 208 usa

    I think it should be 208/120 if thats the spec for each machine

    Kinda hard to tell with that info


  • Advertisement
  • Registered Users Posts: 2,104 ✭✭✭Swampy


    Machine 1:
    208/240V 50/60HZ/3ph KW:12/15.2 A:33.6/37.1
    Machine 2:
    208/240V, 50/60HZ/,1ph 10.3A 2.25K


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    It looks like the first machine would need a 400 to 208v 3 phase transformer of minimum 13kva for a 208v output.

    But it depends on what it is. If it was simply a 3 phase motor for example, with 240v windings, then it could be connected to 400v 3 phase, once the motor can be connected in star. But if its a machine requiring from 208 to 240v between phases, then a transformer will be needed.

    The second machine can be connected straight to a single phase supply here by the look of it.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    could be a motor

    I think it would connect to 230v(most readily available i'd say)) more than likely from a 3P trafo or inverter-about 15kva

    -would be handy alright as robbie said if it's a motor with 230v windings
    -might pay to re-wire motor etc.



    2nd machine should be ok on SP 230v alright


  • Registered Users Posts: 2,104 ✭✭✭Swampy


    That's great lads. Thank you.


  • Registered Users Posts: 270 ✭✭liveandnetural


    this might be wrong but that info looks like is from the lable of a belshaw donut machine????or may of some of there other bakery equipment if it is both machines will work perfect here in lreland the three phase one needs a 5 pin plug on it

    no trafos needed... it works on any voltage between ! 208v and 240v


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    i doubt the 208/240 3p will work
    without alteration

    Would be helpful to get all neccessary info upfront