Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back a page or two to re-sync the thread and this will then show latest posts. Thanks, Mike.

Cooker and hob question

  • 08-07-2012 9:28am
    #1
    Registered Users Posts: 1,494 ✭✭✭


    Was fixing a problem with a cooker on Tuesday, mcb was tripped and would not reset. The cooker and hob are on the same circuit both fed from the cooker switch. Kitchen was just fitted a few weeks ago and both the oven and hob are brand new. Disconnected everything and reset the mcb, and then connected the oven, then the hob and it didnt trip. This was wired by the kitchen fitter and the connections were terrible so thought it must have been a loose connection but its after tripping again last night. Have to get the power ratings of both but the hob is pre wired with a 1.5 flex so assumed it was grand to have both on 32 amp circuit. Any ideas what the problem could be?


«1

Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    doubt it's overload with hob and oven if they're up to about 10kw (total connected load )

    mcb faulty?

    test circuit and check joint

    fault with appliances?


  • Registered Users, Registered Users 2 Posts: 431 ✭✭Diggerdunne


    Find out what was on at the time.. It may have been only the hob or oven and at least then you have it narrowed down to one appliance as opposed to trying to fault find both....


  • Registered Users Posts: 1,494 ✭✭✭m.j.w


    cheers lads was talking to them there and it was just the hob they had on so will have to have a look at that


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    m.j.w wrote: »
    This was wired by the kitchen fitter and the connections were terrible so thought it must have been a loose connection but its after tripping again last night.
    MCBs will trip on overload or short circuit. A loose connection at the hop or oven will not cause an MCB to trip.
    Have to get the power ratings of both but the hob is pre wired with a 1.5 flex so assumed it was grand to have both on 32 amp circuit.
    1.5 is quite small, but it will have a higher current carrying capacity than a normal 1.5 flex as it is a heat resistant flex.
    cheers lads was talking to them there and it was just the hob they had on so will have to have a look at that
    It would seem that you have narrowed it down to the hob. I would suggest that you measure the current drawn by the the hob with a grip on ammeter. This will give you a clue as to what the issue is.


  • Registered Users Posts: 1,494 ✭✭✭m.j.w


    2011 wrote: »
    MCBs will trip on overload or short circuit. A loose connection at the hop or oven will not cause an MCB to trip.


    1.5 is quite small, but it will have a higher current carrying capacity than a normal 1.5 flex as it is a heat resistant flex.


    It would seem that you have narrowed it down to the hob. I would suggest that you measure the current drawn by the the hob with a grip on ammeter. This will give you a clue as to what the issue is.

    Can a loose connection not cause an overload as when the connection heats up this heat can make its way to the bi metal strip thus tripping it on overlaod or would the heat not travel that far? Dont think its that anyway as its tripping instantly when reset. Will be heading down tomorrow after work to have a look


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,755 ✭✭✭meercat


    possibly faulty mcb(as m cebee said)
    i would replace it to be sure

    check also that nothing else is tapped of the cooker circuit either(turn trip off and see whats not working)


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    m.j.w wrote: »
    Can a loose connection not cause an overload as when the connection heats up this heat can make its way to the bi metal strip thus tripping it on overlaod or would the heat not travel that far?
    No.

    The bimetal strip in within the MCB bends as it gets hot.
    The heat is generated within the MCB by excess current.
    This bending causes the MCB to trip.

    Heat generated from a loose connection several meters away will not cause the bimetal strip in the MCB to overheat.

    Dont think its that anyway as its tripping instantly when reset. Will be heading down tomorrow after work to have a look

    That sounds more like a short circuit condition.
    The source of this problem could be at the connection made by the kitchen fitter.

    When an MCB operates due to short circuit the bimetal strip is not used to make it trip, the magnetic properties of current are used.

    Or as cebbe says it could be a faulty MCB


  • Registered Users Posts: 1,494 ✭✭✭m.j.w


    cheers lads ill let ya's know tomorrow


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Is the MCB definitely a 32 amp one?

    Edit: Just noticed in your last post it sometimes trips instantly when reset, so too small a breaker is unlikely the problem. Sounds like a short somewhere, like a nick in a cable shorting to earthed box, dodgy juinction box etc, or faulty MCB. Kitchen fitter electrical work is not often very good.


  • Registered Users Posts: 1,494 ✭✭✭m.j.w


    Went down tonight, mcb tripping instantly when reset and flash visable under one of the dials on the hob. Checked the hob flex which was grand and remade the connections in the hob terminal box and the mcb would then reset. Left the hob on for 15 mins with all the hobs on and it was grand. If it trips again does that mean there is a problem with the hob?

    Yea 32amp Type c mcb so all grand there


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 5,416 ✭✭✭.G.


    It should be a Type B MCB. Type C will allow more current to flow before it trips on overload but that wouldn't be causing your problem since it was tripping instantly and not on overload. Possible it was a poor connection with strands of copper crossing over into N or E connection points.

    Since you've remade the connections and its staying on,If it does trip again it would presumably be a faulty Hob


  • Registered Users Posts: 11 chiefness


    1.5 is quite small, but it will have a higher current carrying capacity than a normal 1.5 flex as it is a heat resistant flex.

    Not true.

    1.5 mm also seems extremely small. Unless this is a tail from the hob then get rid of it immediately. Generally the oven would have a lower wattage. In any case you should use 6mm at min where the unit is not prewired.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    chiefness wrote: »
    1.5 mm also seems extremely small.
    Yes, extremely small would seem more accurate than quite small for a circuit protected by a 32A MCB. I agree with you, but the inspector from RECI that I dealt with told me that he had no issue with this at all.
    Unless this is a tail from the hob then get rid of it immediately.
    It is the tail from the hob according to the OP.
    Generally the oven would have a lower wattage. In any case you should use 6mm at min where the unit is not prewired.

    As far as I know ET101 states that a 4 sq. mm heat resistant flex is acceptable for the final part of the circuit.

    Cabling with heat resistant insulation has a higher current carrying capacity that standard PVC insulation.


  • Registered Users Posts: 11 chiefness


    Cabling with heat resistant insulation has a higher current carrying capacity that standard PVC insulation.

    Would not think so. It may have a different derating factor with temp. rise.

    Your point on the 4 mm heat resisting between the fixed outlet and appliance sounds sensible.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    4mm flex is ok from isolator afaik

    also afaik the smaller 1.5 flex on the 'light' hob should be ok connected to the 4sq flex from the isolator

    if manuf. instructions don't specify smaller mcb/fuse


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    chiefness wrote: »
    Would not think so. It may have a different derating factor with temp. rise.
    I can assure you this is the case.

    By using different types of insulation the current carrying capacity of a cable can be increased.

    For example:

    Refer to ET101

    Look at table A52-F1 for a 6 sq. mm PVC cable.
    Installation method C
    CCC = 46A

    Look at table A52-F5 for a 6 sq. mm MICC cable.
    Installation method C
    CCC = 57A

    Your point on the 4 mm heat resisting between the fixed outlet and appliance sounds sensible.

    Thanks, but I can't claim credit for that (it is in the regs).


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    M cebee wrote: »
    if manuf. instructions don't specify smaller mcb/fuse
    Yes, the key issue is that the MCB should operate before the maximum current carrying capacity of the cable is exceeded.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    chiefness wrote: »
    Would not think so. It may have a different derating factor with temp. rise.

    It would imo. A cable with heat resistant flex can carry a higher current before the insulation would be affected, compared to normal pvc. So regardless of whether the rules allow for it, the cable would have a higher capacity.

    Multi strand flexible cables also have a higher capacity than a solid one would.


  • Registered Users Posts: 11 chiefness


    2011 wrote: »
    chiefness wrote: »
    Would not think so. It may have a different derating factor with temp. rise.
    I can assure you this is the case.

    By using different types of insulation the current carrying capacity of a cable can be increased.

    For example:

    Refer to ET101

    Look at table A52-F1 for a 6 sq. mm PVC cable.
    Installation method C
    CCC = 46A

    Look at table A52-F5 for a 6 sq. mm MICC cable.
    Installation method C
    CCC = 57A

    Your point on the 4 mm heat resisting between the fixed outlet and appliance sounds sensible.

    Thanks, but I can't claim credit for that (it is in the regs).

    Excuse my ignorance but I've yet to see a cooker or hob wired in micc?


  • Registered Users Posts: 11 chiefness


    robbie7730 wrote: »
    chiefness wrote: »
    Would not think so. It may have a different derating factor with temp. rise.

    It would imo. A cable with heat resistant flex can carry a higher current before the insulation would be affected, compared to normal pvc. So regardless of whether the rules allow for it, the cable would have a higher capacity.

    Multi strand flexible cables also have a higher capacity than a solid one would.

    Solid cable/stranded will always have a higher ccc then flexiblle so you are incorrect there.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    Yes, the key issue is that the MCB should operate before the maximum current carrying capacity of the cable is exceeded.

    It depends on what you refer to as the current carrying capacity. The max current the cable can conduct, or the max it can continuously carry.

    In the case of flexes to appliances, it is possibly assumed they wont likely be subjected to a continuous overload, just a short circuit, in fault conditions.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    chiefness wrote: »
    Solid cable/stranded will always have a higher ccc then flexiblle so you are incorrect there.

    That would be news to me I must admit. I would be confident that multi stranded has a higher capacity for AC current, although probably negligible at 50hz. But solid certainly wont be higher.


  • Registered Users Posts: 11 chiefness


    robbie7730 wrote: »
    chiefness wrote: »
    Solid cable/stranded will always have a higher ccc then flexiblle so you are incorrect there.

    That would be news to me I must admit. I would be confident that multi stranded has a higher capacity for AC current, although probably negligible at 50hz. But solid certainly wont be higher.

    I suppose you are correct technically but it's a lot easier to lug two solids then one flex.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    chiefness wrote: »
    Excuse my ignorance but I've yet to see a cooker or hob wired in micc?
    I have not seen it either:D

    I was using this example to illustrate the fact that by using different types of insulation the current carrying capacity of a cable can be altered.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    That would be news to me I must admit. I would be confident that multi stranded has a higher capacity for AC current, although probably negligible at 50hz. But solid certainly wont be higher.
    I suspect you are correct as stranded conductors have more surface area than solids, thus increasing the cooling effect.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    chiefness wrote: »
    I suppose you are correct technically but it's a lot easier to lug two solids then one flex.
    Lugs are not permitted on solid core copper cables.


  • Registered Users Posts: 11 chiefness


    2011 wrote: »
    chiefness wrote: »
    I suppose you are correct technically but it's a lot easier to lug two solids then one flex.
    Lugs are not permitted on solid core copper cables.

    Have you ever wrapped a 120mm solid around a terminal?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    It depends on what you refer to as the current carrying capacity.
    I would consider the current carrying capacity of a cable to be the maximum current that it can sustain indefinitely.

    According to 433.1 of ET101, the design current of the cable shall be < or = the rated current of the protective device which shall be < or = the continuous current carrying capacity of the cable (according to 523).

    In other words, the protective device operates before the cable fails.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    chiefness wrote: »
    Have you ever wrapped a 120mm solid around a terminal?
    No, but I have terminated them by a suitable means that complies with the regulations.


  • Advertisement
  • Registered Users Posts: 11 chiefness


    2011 wrote: »
    chiefness wrote: »
    Have you ever wrapped a 120mm solid around a terminal?
    No, but I have terminated them by a suitable means that complies with the regulations.

    That sounds like a Vicky Pollard Yes/But No.


Advertisement