gene size required

Options
  • 17-07-2012 10:30pm
    #1
    Registered Users Posts: 463 ✭✭


    Hi
    I want to run 3 110volt power tools from a generator ,the total load of all 3 tools is 4650 watts,what kva rated generator would i need to run all 3 tools together?


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    Hi
    I want to run 3 110volt power tools from a generator ,the total load of all 3 tools is 4650 watts,what kva rated generator would i need to run all 3 tools together?


    4650 watts would be the total out put of the 3 drills.
    So if they are 90% efficient then the input (generator output) would have to be about 4650/0.9 = 5167 W.

    kVA = kW / Power Factor

    For a drill the power factor would be about 0.88

    ⇒ kVA = 5.167/0.88 = 5.872

    Therefore a 6kVA generator would be just about able to do it, but you would be better with a 10kVA unit. Starting currents can be high and you do not want to trip your generator all of the time.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    i would have thought the 4650 would be the actual usage and not output on tools
    If it's just tools prob a 6 or a 7.5 kva 'tool rated' trafo i would think


  • Registered Users Posts: 102 ✭✭antlyn


    2011 wrote: »
    Hi
    I want to run 3 110volt power tools from a generator ,the total load of all 3 tools is 4650 watts,what kva rated generator would i need to run all 3 tools together?


    4650 watts would be the total out put of the 3 drills.
    So if they are 90% efficient then the input (generator output) would have to be about 4650/0.9 = 5167 W.

    kVA = kW / Power Factor

    For a drill the power factor would be about 0.88

    ⇒ kVA = 5.167/0.88 = 5.872

    Therefore a 6kVA generator would be just about able to do it, but you would be better with a 10kVA unit. Starting currents can be high and you do not want to trip your generator all of the time.



    You need to multiply by 0.9 to get the percentage. Dividing has given you a number greater than the total load!


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    the va for genny sizing will be greater than kw


  • Registered Users Posts: 102 ✭✭antlyn


    Yeah I know was just saying about the equation used


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    my 110v bosch kango is 1350w rated input power,14.5 amps
    no pf supplied
    -so thats 1595 va


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    antlyn wrote: »
    You need to multiply by 0.9 to get the percentage. Dividing has given you a number greater than the total load!

    No.

    The power input will always be larger than the power output value unless the unit is 100% efficient (simply not possible).

    Remember

    Efficiency = (output / input) * 100

    as can be seen here:

    http://wiki.answers.com/Q/What_is_the_formula_for_calculating_efficiency


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    M cebee wrote: »
    i would have thought the 4650 would be the actual usage and not output on tools
    The kW rating of motors is the output AFAIK.

    If it's just tools prob a 6 or a 7.5 kva 'tool rated' trafo i would think
    This may be ok for the transformer, but the OP asked about the rating of the generator. I am not sure if the OP even requires a transformer, I would simply use a 110VAC generator if it were me.

    Transforemer will also introduce a further loss. AFAIK 96-98 % efficiency would typical for a transformer.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    my bad-didn't read question,it's a 110v genny

    Motor nameplate rating is output power so you need efficiency or line current for sizing
    Tools and appliances are rated input power


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    antlyn wrote: »
    You need to multiply by 0.9 to get the percentage. Dividing has given you a number greater than the total load!

    It hasn`t. His calculation is correct. The generator VA has to be equal to or greater than the kw load. It cant be smaller.

    If a motor takes 4kw to run at full load (forget efficiecy for this), and has a pf of 0.8, then the kva to power the 4000 watts is 4000/0.8 = 5000 va.

    To reverse the calculation, the generator supplies 5000va, but for a pf of 0.8, only 80% of the amps are doing any work, so the 5000 x 80/100 = 4000 watts. So while the generator is powering the 4kw load, it is outputting 5kva.

    Same with the efficiency. If the drill is outputting 1000 watts, and is 90% efficient, it will show as 1111 watts on a watt meter.

    1000/0.9 = 1111.


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    M cebee wrote: »
    i would have thought the 4650 would be the actual usage and not output on tools

    "Almost all manufacturers stamp the design full-load power output in horsepower on the nameplate"

    From this link:

    http://eeref.engr.oregonstate.edu/Systems/Motor_Systems/Motors/Performance_Relationships


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    yes for motors
    Nameplate Kw/hp is output

    my bosch110v kango for example is marked with rated input power


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    the amps will be marked on them anyhow-calculating va from that is simplest way imo


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    M cebee wrote: »
    the amps will be marked on them anyhow-calculating va from that is simplest way imo
    +1