Electrical question- power consumed calculation.

Options
  • 20-09-2012 10:50pm
    #1
    Registered Users Posts: 5,756 ✭✭✭


    Maybe one of you lads can help me with this.

    Three 12.5 ohm heating elements are connected in an industrial oven in a delta configuration to a 115/200V 3 phase supply.

    Determine:

    a. the current carried by the supply cables?
    b. total power consumed?

    My brain's not functioning at the moment. :o

    We're all in this psy-op together.🤨



Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    el diablo wrote: »
    Maybe one of you lads can help me with this.

    Three 12.5 ohm heating elements are connected in an industrial oven in a delta configuration to a 115/200V 3 phase supply.

    Determine:

    a. the current carried by the supply cables?
    b. total power consumed?

    My brain's not functioning at the moment. :o

    Let the phase current (current passing through 1 element) = Iph
    Let the phase voltage = Vph
    Let the phase impedance = Zph
    Let the line current = In (this is the current carried by the supply cables)
    Let the line voltage = Vn

    ⇒ Iph = Vph/Zph

    In this case the impedance = the resistance
    As the load is connected in delta configuration the phase voltage = the line voltage.

    ⇒ Iph = 200/12.5 = 16A


    In = √3 x Iph
    In = √3 x 16 = 27.71A

    Therefore the current carried by the supply cables is 27.71A

    As this is a resistive load Cosɵ = 1

    Power for a 3 phase load = √3 x Vn x In x Cosɵ

    ⇒ Total power consumed = √3 x 200 x 27.71 x 1 = 9600 Watts = 9.6kW


  • Registered Users Posts: 5,756 ✭✭✭el diablo


    2011 wrote: »
    Let the phase current (current passing through 1 element) = Iph
    Let the phase voltage = Vph
    Let the phase impedance = Zph
    Let the line current = In (this is the current carried by the supply cables)
    Let the line voltage = Vn

    ⇒ Iph = Vph/Zph

    In this case the impedance = the resistance
    As the load is connected in delta configuration the phase voltage = the line voltage.

    ⇒ Iph = 200/12.5 = 16A


    In = √3 x Iph
    In = √3 x 16 = 27.71A

    Therefore the current carried by the supply cables is 27.71A

    As this is a resistive load Cosɵ = 1

    Power for a 3 phase load = √3 x Vn x In x Cosɵ

    ⇒ Total power consumed = √3 x 200 x 27.71 x 1 = 9600 Watts = 9.6kW


    That's great. thanks for that. :)

    We're all in this psy-op together.🤨



  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    No problem.
    Does it make sense to you ?


  • Registered Users Posts: 5,756 ✭✭✭el diablo


    2011 wrote: »
    No problem.
    Does it make sense to you ?

    Yep, it does, cheers.

    It's coming back to me now.:)

    In star:
    I line = I phase
    V line = √3 x V phase.

    and the opposite in delta.
    And a p.f of unity (1) due it being a purely resistive load.

    So if it was connected in star (with 380V/220V 3 ph. supply) and three 44 ohm elements:

    Iph= Vph/Rph= 220/44= 5A.

    Total power consumed:

    P= √3 x 380 x 5 x 1= 3.3 KW.

    Am I correct? :o

    We're all in this psy-op together.🤨



  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    el diablo wrote: »
    Yep, it does, cheers.

    It's coming back to me now.:)

    In star:
    I line = I phase
    V line = √3 x V phase.

    and the opposite in delta.
    And a p.f of unity (1) due it being a purely resistive load.

    So if it was connected in star (with 380V/220V 3 ph. supply) it would be:

    Iph= Vph/Rph= 220/44= 5A.

    Total power consumed:

    P= √3 x 380 x 5 x 1= 3.3 KW.

    Am I correct? :o
    If the resistance is 44 ohms, then yes the above is correct.


  • Advertisement
  • Registered Users Posts: 5,756 ✭✭✭el diablo


    2011 wrote: »
    If the resistance is 44 ohms, then yes the above is correct.

    Yes, forgot to mention the 44 ohm elements.

    Thanks. :)

    We're all in this psy-op together.🤨



  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    el diablo wrote: »
    Yes, forgot to mention the 44 ohm elements.

    Thanks. :)

    No problem. It gets a little more complex when the loads are unbalanced.
    There are a few very helpful websites for this sort of thing. I will try to dig them out.

    Out of interest, is this for college or work ?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    Let the phase current (current passing through 1 element) = Iph
    Let the phase voltage = Vph
    Let the phase impedance = Zph
    Let the line current = In (this is the current carried by the supply cables)
    Let the line voltage = Vn

    ⇒ Iph = Vph/Zph

    In this case the impedance = the resistance
    As the load is connected in delta configuration the phase voltage = the line voltage.

    ⇒ Iph = 200/12.5 = 16A


    In = √3 x Iph
    In = √3 x 16 = 27.71A

    Therefore the current carried by the supply cables is 27.71A

    As this is a resistive load Cosɵ = 1

    Power for a 3 phase load = √3 x Vn x In x Cosɵ

    ⇒ Total power consumed = √3 x 200 x 27.71 x 1 = 9600 Watts = 9.6kW

    Or since the phase current has been calculated early on through knowing the load impedence/resistance, it is simply 200v x 16a x 3phases. Finding the line current by √3 x 16 and then multiplying by √3 again in the final line, is doing a double calculation. Although it is useful for getting an understanding alright.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    robbie7730 wrote: »
    Finding the line current by √3 x 16 and then multiplying by √3 again in the final line, is doing a double calculation.

    The reason that I calculated the line current was because it was asked for in part a of the question:
    Determine:

    a. the current carried by the supply cables?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    The reason that I calculated the line current was because it was asked for in part a of the question:

    True, I should of read it properly:o


  • Advertisement
  • Registered Users Posts: 5,756 ✭✭✭el diablo


    2011 wrote: »
    No problem. It gets a little more complex when the loads are unbalanced.
    There are a few very helpful websites for this sort of thing. I will try to dig them out.

    Out of interest, is this for college or work ?

    It's for trade recognition exams for another country. It's been ten years since I've studied this stuff in college.

    I might have one or two more questions for you over the next week or so. :P

    We're all in this psy-op together.🤨



  • Registered Users Posts: 5,756 ✭✭✭el diablo


    I've one more question. Maybe somebody can help.



    duelstopstart_zps8cb6a7d4.gif

    In a similar circuit with just one stop and one start the contact numbers would be 1 & 2 for the stop and 3 & 4 for the start and 95 & 96 for the thermal overload.

    Anyone know what the contact numbers should be on the stops and starts on a duel stop start circuit?

    We're all in this psy-op together.🤨



  • Posts: 0 [Deleted User]


    el diablo wrote: »
    I've one more question. Maybe somebody can help.



    duelstopstart_zps8cb6a7d4.gif

    In a similar circuit with just one stop and one start the contact numbers would be 1 & 2 for the stop and 3 & 4 for the start and 95 & 96 for the thermal overload.

    Anyone know what the contact numbers should be on the stops and starts on a duel stop start circuit?

    It would be still 1 & 2 for both stops (connected in series) and 3 & 4 for both starts (connected in parallel). Each button would be labeled X1, X2, X3 and X4 or whatever you want. The O/L is still 95 & 96 but only one would be used.


  • Registered Users Posts: 5,756 ✭✭✭el diablo


    shaaane wrote: »
    It would be still 1 & 2 for both stops (connected in series) and 3 & 4 for both starts (connected in parallel). Each button would be labeled X1, X2, X3 and X4 or whatever you want. The O/L is still 95 & 96 but only one would be used.

    Thanks for that. Just what I thought. :)

    We're all in this psy-op together.🤨



  • Registered Users Posts: 5,756 ✭✭✭el diablo


    el diablo wrote: »
    Thanks for that. Just what I thought. :)

    How about on a forward/reverse motor control circuit? What would be the contact numbers at the forward and reverse contacts (both normally open start buttons)?

    Is it also 3 and 4?

    We're all in this psy-op together.🤨



  • Posts: 0 [Deleted User]


    el diablo wrote: »
    How about on a forward/reverse motor control circuit? What would be the contact numbers at the forward and reverse contacts (both normally open start buttons)?

    Is it also 3 and 4?

    All N/C buttons (STOP) are 1 & 2 and N/O (START) are 3 & 4. For forward and reverse its 2 x N/O contacts (one for START forward and the other for START reverse) and a STOP connected to 2 separate contactors sometimes labelled KM1 & KM2 and an O/L sometimes labelled F1. Hope i'm helping you here!


  • Registered Users Posts: 5,756 ✭✭✭el diablo


    shaaane wrote: »
    All N/C buttons (STOP) are 1 & 2 and N/O (START) are 3 & 4. For forward and reverse its 2 x N/O contacts (one for START forward and the other for START reverse) and a STOP connected to 2 separate contactors sometimes labelled KM1 & KM2 and an O/L sometimes labelled F1. Hope i'm helping you here!

    Yes, you're helping.:) Would the thermal overload usually be connected after the stop button (ie. from contact "2" on stop to contact "95" on T. o/l?) rather that after the start buttons? It's been a long time since I've done motor theory. :P

    We're all in this psy-op together.🤨



  • Posts: 0 [Deleted User]


    el diablo wrote: »
    Yes, you're helping.:) Would the thermal overload usually be connected after the stop button (ie. from contact "2" on stop to contact "95" on T. o/l?) rather that after the start buttons? It's been a long time since I've done motor theory. :P

    I'm a bit rusty on this myself. I think it goes (MCB - 95, 96 - 1, 2 - 3, 3 - 13, 4 - 14, 4 - A1, A2 - N). Open for correction!


  • Registered Users Posts: 5,756 ✭✭✭el diablo


    shaaane wrote: »
    I'm a bit rusty on this myself. I think it goes (MCB - 95, 96 - 1, 2 - 3, 3 - 13, 4 - 14, 4 - A1, A2 - N). Open for correction!

    Ok thanks. I think it can be done either way. I've seen some diagrams with the "stop" before the "t.o/l." and vice versa.

    We're all in this psy-op together.🤨



  • Posts: 0 [Deleted User]


    el diablo wrote: »
    Ok thanks. I think it can be done either way. I've seen some diagrams with the "stop" before the "t.o/l." and vice versa.


    Something like this

    basicmotorcontrol.png


  • Advertisement
  • Registered Users Posts: 5,756 ✭✭✭el diablo


    The one I'm thinking of is similar to this, but with the t.o/l just after the stop button in the circuit.

    forwardreversemotor.png

    We're all in this psy-op together.🤨



  • Posts: 0 [Deleted User]


    el diablo wrote: »
    The one I'm thinking of is similar to this, but with the t.o/l just after the stop button in the circuit.

    forwardreversemotor.png
    Can't see anything wrong with that. The way I drew it is the way I learned it during my training. Although mine is just for one direction on the motor, you get the idea. Same thing really