Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back a page or two to re-sync the thread and this will then show latest posts. Thanks, Mike.

Emergency Lighting

  • 16-11-2012 1:26am
    #1
    Registered Users Posts: 853 ✭✭✭


    Hi all,

    Hoping someone can confirm something for me.
    I'm swapping out some fittings in a place and the Emer's have the Mains healthy LED, the new ones I'm fitting have an external sausage pack and as they're recessed fittings there's no way of seeing the LED status without hacking into the fitting.

    Called the supplier of the new fittings and he told me that Emer fittings just need to be highlighted against the rest of the fittings, ie a small red sticker indicating that that light is an Emer fitting will do...

    Is this correct or is he talking a load of

    Thanks
    Seán


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    Seanieke wrote: »
    Hi all,

    Hoping someone can confirm something for me.
    I'm swapping out some fittings in a place and the Emer's have the Mains healthy LED, the new ones I'm fitting have an external sausage pack and as they're recessed fittings there's no way of seeing the LED status without hacking into the fitting.

    Called the supplier of the new fittings and he told me that Emer fittings just need to be highlighted against the rest of the fittings, ie a small red sticker indicating that that light is an Emer fitting will do...

    Is this correct or is he talking a load of

    Thanks
    Seán
    Without seeing the LED there is no way to know that the batteries are charging when the light is switched off. I would be pretty sure that this would not comply with the regulations.


  • Registered Users Posts: 853 ✭✭✭Seanieke


    That be what I was thinking but I called the NSAI today and no one could tell me! I thought they set the standards!


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    nobody knows anything-always the way in these situations

    could he be right that the sticker to identify the emergencys will suffice

    does the led make any difference for EL
    test purposes ?


  • Registered Users, Registered Users 2 Posts: 706 ✭✭✭dolittle


    i`m nearly sure that the fittings led has to be visible now to get your cert


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    According to this Emergency Lighting Design Guide:

    "Function test:
    All emergency luminaires should be tested be breaking the
    supply to them and checking that they operate satisfactorily.
    The supply must then be restored and the charging indicators
    must be seen to be operating correctly
    . This test must be
    performed at least once per month and the results logged"



    To me the part that I have indicated in bold suggests that the LED is not optional as it is required as part of the normal testing procedure.


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    yes i was thinking of the latter test in my post
    but that also requires charging indicators to be checked
    and there would prob be the functional test also with the shorter interval

    The testing requirements in the code of practice are:
    • Function test
    All emergency luminaires should be tested be breaking the
    supply to them and checking that they operate satisfactorily.
    The supply must then be restored and the charging indicators
    must be seen to be operating correctly. This test must be
    performed at least once per month and the results logged
    • Discharge test
    The luminaires must be tested for their full rated duration period
    and checked for satisfactory operation. The supply must then be
    restored and the charging indicators rechecked. This test must
    be performed at least annually and the results logged


    is that a uk link-i'd say we'd have similar testing requirements here


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    M cebee wrote: »
    is that a uk link-i'd say we'd have similar testing requirements here

    I just found it from Googling to be honest. Although it mentions several EN and BS standards, so I would thin it is applicable.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    that would be the critical part alright after testing

    "to recheck the charging indicators after testing"

    -hard to see how the labels can comply then


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,602 Mod ✭✭✭✭2011


    M cebee wrote: »
    that would be the critical part alright after testing

    "to recheck the charging indicators after testing"

    -hard to see how the labels can comply then

    Indeed.

    I have been thinking about this since. It would seem to me that a lit LED does not necessarily mean that all is well with a particular emergency light, it just indicates that some components are functioning correctly and the fitting has a healthy mains supply. However an unlit LED immediately indicates to a casual observer that there is an issue.


  • Registered Users, Registered Users 2 Posts: 3,612 ✭✭✭Dardania


    I had a problem on a project with an exit sign, which I only found out about when I was function testing the firemans switch on the main incomer.

    The exit sign was maintained as it was a public space. It would indicate that it was charging with the green LED, and pressing the CTU would leave the fitting lit. All good.

    However, when I rocked up to the premises at 4am, so that we could hit the fireman's switch, to test the UPS', security systems etc, I noticed that the particular fitting didn't light :mad:

    Moral of the story for OP's scenario, you need to have the LED visible - refer to IS EN 3217 and 8138 (I think - been a while...) and test the emergency lighting by isolating power to the entire board if possible, to be sure to be sure. Also, the regs around 2005 I think outmoded red LEDs, so the red sticker is a complete red herring.

    Also, who is going to certify the commissioning part of the emergency lighting - make sure they're happy to do so, paritculary if, as it sounds, you have spearate inverters to fittings, as who holds the manufacutring warranty for the complete emergency light fitting?