RCBO fails trip time. Causes? How to speed it up?

Options
  • 15-12-2012 2:53pm
    #1
    Registered Users Posts: 65 ✭✭


    This is a brand new installation. Its small but there are plenty of circuits. All wiring is 100% and everything works as planned. ALL pre-connection tests were perfect. I havent done Zl ohms yet. My RCD trip time fine. But I have 5 fixed appliance powerd by 5 RCBO and these fail RCD max operating time. tripping at 0.46sec.

    :rolleyes:What are your thought on this?

    Causes?

    Solutions?!


Comments

  • Registered Users Posts: 378 ✭✭frankmul


    This is a brand new installation. Its small but there are plenty of circuits. All wiring is 100% and everything works as planned. ALL pre-connection tests were perfect. I havent done Zl ohms yet. My RCD trip time fine. But I have 5 fixed appliance powerd by 5 RCBO and these fail RCD max operating time. tripping at 0.46sec.

    :rolleyes:What are your thought on this?

    Causes?

    Solutions?!
    just wondering if your rcd tester is in calibration. any chance of getting a second tester to retest the circuit.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    they can't all trip at 0.46 sec on the 30mA tests anyway


  • Registered Users Posts: 378 ✭✭frankmul


    M cebee wrote: »
    they can't all trip at 0.46 sec on the 30mA tests anyway
    true, strange that they all had the same time. never thought of that


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,583 Mod ✭✭✭✭2011


    frankmul wrote: »
    true, strange that they all had the same time. never thought of that

    +1
    Very good point.


  • Registered Users Posts: 378 ✭✭frankmul


    Might it be 46msec instead of 0.46 sec. I have seen a few caught out by that


  • Advertisement
  • Registered Users Posts: 65 ✭✭alphonse mephisto


    Sorry it is 46msec but its still a fail? Its strange that its all of them, fair enough one or two but its five different circuits. Only thing they have in common is the same make and type of rcbo. Ive been doing the tests at the circuits spur on the feed side with the load disconnected.


  • Registered Users Posts: 65 ✭✭alphonse mephisto


    I can try the test across the rcbos terminals and see what happens,
    Any other thoughts other than rewire the board?


  • Registered Users Posts: 378 ✭✭frankmul


    Disconnection time is 0.3 seconds or 300msecs for the rated current. 46msec is well inside that.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    yes
    46ms is a pass anyhow for 30ma test


  • Registered Users Posts: 65 ✭✭alphonse mephisto


    I am in fact a cabbage. Was just looking at the manual off use rcd tester. It gives readings in milli seconds I miss read the regs! Worked out alright so! Zl Monday morning and hopefully an early drink so! :-)


  • Advertisement
  • Registered Users Posts: 65 ✭✭alphonse mephisto


    Can't believe that was so foolish! Even stranger now the times being. The same! A lot of stress relieved there!


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,583 Mod ✭✭✭✭2011


    frankmul wrote: »
    Disconnection time is 0.3 seconds or 300msecs for the rated current. 46msec is well inside that.

    Correct me if I'm wrong, but I think that the disconnection time is 0.2 seconds.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    wasn't it always 300ms

    and 40ms i think for 5x

    has it changed?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,583 Mod ✭✭✭✭2011


    M cebee wrote: »
    wasn't it always 300ms

    and 40ms i think for 5x

    has it changed?

    I am not aware of any change. It has been a while, I thought it was 0.2 sec


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    2011 wrote: »
    I am not aware of any change. It has been a while, I thought it was 0.2 sec

    i've had a few beers and don't have rules handy so i'm not much use:)


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    i've had a few beers and don't have rules handy so i'm not much use:)

    Dont be blaming the beers on that:pac:


  • Registered Users Posts: 378 ✭✭frankmul




  • Registered Users Posts: 65 ✭✭alphonse mephisto


    From et 101 2008 max operating times for general type rcds 1x In 0.3 sec.
    5x In 0.04sec


  • Registered Users Posts: 378 ✭✭frankmul


    Did you test in both half of the cycle


  • Registered Users Posts: 65 ✭✭alphonse mephisto


    I did indeed, my higher readings seemed to be on the 180side! Ill do couple more anyway to be sure but looks like a pass now anyway! :-)


  • Advertisement
  • Registered Users Posts: 65 ✭✭alphonse mephisto


    What would cause an rcd fail its tripping time anyway?


  • Registered Users Posts: 378 ✭✭frankmul


    Mechanical part of rcd slow to act could be one reason