Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

adey magnacleanse

  • 07-02-2013 7:05pm
    #1
    Registered Users Posts: 61 ✭✭


    just looking for a bit of information onthe adey magna cleanse.Does anyone use them? are they worth the money?. i have a job to flush about 18 radiators. i have the guardian power flushing unit but taught one of these might speed up the process. i can get one for about 400 incl VAT.

    thanks for any replies
    Pat


«1

Comments

  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    paddy_joe wrote: »
    just looking for a bit of information onthe adey magna cleanse.Does anyone use them? are they worth the money?. i have a job to flush about 18 radiators. i have the guardian power flushing unit but taught one of these might speed up the process. i can get one for about 400 incl VAT.

    thanks for any replies
    Pat
    Are they the add ons to the flushing unit? If they are I heard there meant to make life alot easier


  • Registered Users Posts: 61 ✭✭paddy_joe


    you dont need a power flushing unit,the circulating pump is supposed to be enough,but im sure the two could be combined if a system was bad.


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    paddy_joe wrote: »
    you dont need a power flushing unit,the circulating pump is supposed to be enough,but im sure the two could be combined if a system was bad.
    Oh I know now. Just using the circ pump isn't meant to be a great job


  • Registered Users Posts: 61 ✭✭paddy_joe


    yeah was wondering about that,but i already have pump so could combine the 2 then.


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    paddy_joe wrote: »
    yeah was wondering about that,but i already have pump so could combine the 2 then.
    I'd imagine you could. I did the cheaper option and mounted a standard magnaclean onto mine with a bypass so I can clean it ouy while the machine works away. But yours would be much better in fairness


  • Advertisement
  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    paddy_joe wrote: »
    yeah was wondering about that,but i already have pump so could combine the 2 then.
    Combined with a proper power flushing machine, fine but on its own a complete waste of time.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    paddy_joe wrote: »
    just looking for a bit of information onthe adey magna cleanse.Does anyone use them? are they worth the money?. i have a job to flush about 18 radiators. i have the guardian power flushing unit but taught one of these might speed up the process. i can get one for about 400 incl VAT.

    thanks for any replies
    Pat
    For that money I would be investing in the Fernox Powerflushing Filter @ €455 incl vat.


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    shane0007 wrote: »
    For that money I would be investing in the Fernox Powerflushing Filter @ €455 incl vat.
    Are they not the same thing?


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp79 wrote: »
    Are they not the same thing?
    Not same but similar. I don't know the strength of the Adey magnets but the Fernox is 11,000 gauss.


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    shane0007 wrote: »
    Not same but similar. I don't know the strength of the Adey magnets but the Fernox is 11,000 gauss.
    Adey don't say anywhere what strength their magnet is. Hmmmm


  • Advertisement
  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp79 wrote: »
    Adey don't say anywhere what strength their magnet is. Hmmmm
    Now you are just sounding like me, hmmmm.....


  • Closed Accounts Posts: 342 ✭✭spireland32


    shane0007 wrote: »
    but on its own a complete waste of time.

    Why do you think that?


  • Posts: 0 [Deleted User]


    Why do you think that?

    Your using a pump that can be sitting in sludge, no point having a flushing system that is only as good as the pump that's in the boiler, that's without taking in to account any blockage or restriction in the heat exchanger.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Why do you think that?

    Power flushing works & ONLY works on the basis of low pressure but with high velocity. You will never achieve high velocity with the system circulator.

    The other problem is that most "power flushing machines" if you can call them that only have between 250w & 350w motors. WOT IMO. Compared to the Fernox, it has an 1,100w motor. I powerflushed a hotel this week with no issues whatsoever.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Some pics


  • Registered Users, Registered Users 2 Posts: 2,409 ✭✭✭sullzz


    Are you using the powerflow unit Shane


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Yes, have been for past number of years. Excellent unit. Best on the market IMHO. I have yet to have a system beat me with it. I also use it alongside a thermal image camera. Another invaluable piece of equipment assessing, before, during & after the flush. Pricey though @ €2,600!
    JohnnieK picked up his new shiney MkIII today. It was a very proud moment for him.


  • Registered Users, Registered Users 2 Posts: 2,409 ✭✭✭sullzz


    shane0007 wrote: »
    JohnnieK picked up his new shiney MkIII today. It was a very proud moment for him.

    Lol ! Must be dying for the first flush job to come in .
    You get that extra bit of satisfaction with the thermal imaging camera when on a really dirty system , great to show the customer.
    Gotta love the amount of s**t you collected on the filters in your pics.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    That was the 3rd magnet clean out like that with that system. It was one floor of a hotel. Boiler was kaput. We changed it from oil to gas so installed the gas boilers but through a temporary cylinder to act as a buffer. Water in buffer was then pumped through the system to cleanse. Once finished, gas boilers were piped to a low loss header then set up for the different circuits.


  • Closed Accounts Posts: 342 ✭✭spireland32


    Ah I see, didnt think the adey used the existing water pump. So your setup shane is a powerflusher with magnets added on. Like having powerflusher and magnaclease together. Nice pics!


  • Advertisement
  • Registered Users Posts: 61 ✭✭paddy_joe


    @ shane

    is it the fernox power flushing filter you have? ill try find out tomorrow the strenght of the adey magnets. where did you buy your filter from?

    thanks for replied


  • Registered Users Posts: 61 ✭✭paddy_joe


    @ shane

    is it the fernox power flushing filter you have? ill try find out tomorrow the strenght of the adey magnets. where did you buy your filter from?

    thanks for replies


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Ah I see, didnt think the adey used the existing water pump. So your setup shane is a powerflusher with magnets added on. Like having powerflusher and magnaclease together. Nice pics!

    Yes I use the Fernox Powerflow in conjunction with their magnet.
    http://www.fernox.com/files/Fernox/Content/PDF/English/Powerflushing%20Filter.pdf
    I used to use the Flush Buddy but makes hard work of a dirty system. Never looked back when I upgraded to the Flushing Filter.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    paddy_joe wrote: »
    @ shane

    is it the fernox power flushing filter you have? ill try find out tomorrow the strenght of the adey magnets. where did you buy your filter from?

    thanks for replies

    I got it through Fernox.


  • Registered Users Posts: 61 ✭✭paddy_joe


    shane0007 wrote: »
    Yes I use the Fernox Powerflow in conjunction with their magnet.
    http://www.fernox.com/files/Fernox/Content/PDF/English/Powerflushing%20Filter.pdf
    I used to use the Flush Buddy but makes hard work of a dirty system. Never looked back when I upgraded to the Flushing Filter.

    what descaler do you use for best results?


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    DS40
    Just make sure you use the Neutraliser. Also be careful with aluminium heat exchangers.


  • Registered Users Posts: 61 ✭✭paddy_joe


    Just rang adey,they wont give out the information on strenght of magnet.....


    @ shane, Do you put the descaler in a week beforehand?


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    paddy_joe wrote: »
    Just rang adey,they wont give out the information on strenght of magnet.....


    @ shane, Do you put the descaler in a week beforehand?
    There magnet is probably not nearly as strong as the fernox and they know it!


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    paddy_joe wrote: »
    Just rang adey,they wont give out the information on strenght of magnet.....

    @ shane, Do you put the descaler in a week beforehand?
    It depends on how bad the system is but probably never a week, a couple of days max. I would be fearful of the acidity in the system for that length of time. I have a list of nearly all boiler heat exchanger material & refer to that to determine what my next action will be.


  • Advertisement
  • Registered Users Posts: 61 ✭✭paddy_joe


    Dtp79 wrote: »
    There magnet is probably not nearly as strong as the fernox and they know it!


    Yeah I would say so. She started on about the surface area of the magnet.
    Just waiting on price back and availability on the fernox one now.


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    paddy_joe wrote: »


    Yeah I would say so. She started on about the surface area of the magnet.
    Just waiting on price back and availability on the fernox one now.
    Women!!


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp79 wrote: »
    Women!!
    See it IS all about size and she told me that size didn't matter, it was the power behind it that counted!
    Sheesh, women.....


  • Registered Users, Registered Users 2 Posts: 2,526 ✭✭✭JohnnieK


    sullzz wrote: »
    Lol ! Must be dying for the first flush job to come in .
    You get that extra bit of satisfaction with the thermal imaging camera when on a really dirty system , great to show the customer.
    Gotta love the amount of s**t you collected on the filters in your pics.

    I've used it twice since since Monday and it's unreal lads. It make's my old Pulsar one look like a toy compared to it. I certainly had a horn on me when I used it for the first time.:D:D


  • Registered Users, Registered Users 2 Posts: 1,884 ✭✭✭Robbie.G


    Jesus johnnie you need to get out more when a power flusher gives you a stiffy.I heard the new one was good but I couldn't imagine it was that good


  • Registered Users, Registered Users 2 Posts: 2,409 ✭✭✭sullzz


    JohnnieK wrote: »
    I certainly had a horn on me when I used it for the first time.:D:D

    Sweet lord !!!!!


  • Advertisement
  • Registered Users Posts: 61 ✭✭paddy_joe


    JohnnieK wrote: »
    I've used it twice since since Monday and it's unreal lads. It make's my old Pulsar one look like a toy compared to it. I certainly had a horn on me when I used it for the first time.:D:D

    how much did new one set you back? did you use it on its own or with a fernox power flushing filter? i have the pulsar one myself too.looking to upgrade,found it slow on last couple of jobs.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    sullzz wrote: »

    Sweet lord !!!!!
    I did warn yeas!


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    JohnnieK wrote: »

    I've used it twice since since Monday and it's unreal lads. It make's my old Pulsar one look like a toy compared to it. I certainly had a horn on me when I used it for the first time.:D:D
    Jonnies idea of porn is watching the fernox powerflush tutorial on YouTube!


  • Registered Users, Registered Users 2 Posts: 2,526 ✭✭✭JohnnieK


    paddy_joe wrote: »
    how much did new one set you back? did you use it on its own or with a fernox power flushing filter? i have the pulsar one myself too.looking to upgrade,found it slow on last couple of jobs.

    It was €1100. Worth every penny, hadn't the budget to go for the filter yet but got the pump head adaptor. I had the pulsar one too and it's a toy compared to this one.

    I have three jobs for it this week, one is a system with a 2 year old boiler and no circulation what so ever I'll keep you posted on the outcome.


  • Registered Users Posts: 61 ✭✭paddy_joe


    JohnnieK wrote: »
    It was €1100. Worth every penny, hadn't the budget to go for the filter yet but got the pump head adaptor. I had the pulsar one too and it's a toy compared to this one.

    I have three jobs for it this week, one is a system with a 2 year old boiler and no circulation what so ever I'll keep you posted on the outcome.

    do you always use the fernox ds40?do you do much power flushing?


  • Advertisement
  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    I would only use DS40 on certain instances that warrant it, i.e. where the system is affected by limescale rather than sludge. F5 would be my most common choice for sludge. If I was Powerflushing GB, I would use F3.


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    shane0007 wrote: »
    I would only use DS40 on certain instances that warrant it, i.e. where the system is affected by limescale rather than sludge. F5 would be my most common choice for sludge. If I was Powerflushing GB, I would use F3.
    Is f5 the strongest for sludge and ds40 for lime?


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Yes but both will remove both, sort of speak!
    F5 is designed to remove sludge predominately but also contains lime scale removing properties & DS40 is designed to remove lime scale predominately but also contains sludge removing properties.
    DS40 is very acidic so extreme caution must be take when flushing boilers with aluminium heat exchangers & the DS40 Neutraliser must be used.


  • Registered Users Posts: 61 ✭✭paddy_joe


    JohnnieK wrote: »

    It was €1100. Worth every penny, hadn't the budget to go for the filter yet but got the pump head adaptor. I had the pulsar one too and it's a toy compared to this one.

    I have three jobs for it this week, one is a system with a 2 year old boiler and no circulation what so ever I'll keep you posted on the outcome.



    So how did the job go?


  • Registered Users, Registered Users 2 Posts: 2,526 ✭✭✭JohnnieK


    paddy_joe wrote: »
    So how did the job go?

    The Fernox machine shifted it in a jiffy.


  • Posts: 0 [Deleted User]


    JohnnieK wrote: »
    The Fernox machine shifted it in a jiffy.

    Then you shifted the fernox machine:eek:


  • Registered Users, Registered Users 2 Posts: 1,884 ✭✭✭Robbie.G


    Hey lads you's need to get out more there are very strange fetishes going on here we won't mention speedos, steps and fernox power flows


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Robbie.G wrote: »
    Hey lads you's need to get out more there are very strange fetishes going on here we won't mention speedos, steps and fernox power flows

    Hmmmm.... Haven't thought of that one, Powerflushing whilst in a pair of Speedos.
    Thanks Robbie!


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Robbie.G wrote: »
    Sure you can try that next week using a fernox and see then wtf Charlie says then
    Even metac don't teach that
    Erm.. perhaps we should keep that to ourselves


  • Registered Users, Registered Users 2 Posts: 1,884 ✭✭✭Robbie.G


    shane0007 wrote: »
    Erm.. perhaps we should keep that to ourselves

    Enough said