Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

63A Switch Fuse Melted

Options
  • 15-02-2013 8:33pm
    #1
    Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭


    A work colleague noticed a burning smell from his consumer unit. This was the culprit:

    MeltedSwitchFuse.jpg

    I have seen three of this type of switch fuse fail in a similar fashion.
    IMHO the design of the type shown below (this example is a Hager unit) is a far superior.
    It is safer / more robust design as there are less connections and it is less likely that the fuse will be loose.

    L71M.jpg

    As far as I recall a number of this type (as shown in the first picture) were recalled. Anyone else remember this?


«1

Comments

  • Registered Users Posts: 652 ✭✭✭Just An Opinion


    Yea I'm surprised these screw ins are still used in units today, far too common them coming loose.


  • Registered Users Posts: 3,544 ✭✭✭LeBash


    Yea I'm surprised these screw ins are still used in units today, far too common them coming loose.

    Probably because the drop in style caught fire a few years ago.


  • Registered Users Posts: 4,745 ✭✭✭meercat


    have come across this too ,a few times
    luckily there was nothing flammable close to it


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    fairly regular callout issue i'd say
    i've certainly seen loads of them


    funnily enough i don't recall too many issues with the 'recalled' drop-in types over the years:)


    i think some cases are overload related related-dunno how many?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    M cebee wrote: »
    i think some cases are overload related related-dunno how many?

    An overload should not be possible.
    If this unit was fit for purpose (and properly installed) the fuse should operate before the unit can experience an overload condition.
    funnily enough i don't recall too many issues with the 'recalled' drop-in types over the years
    I was referring to the type of switch fuse unit shown in the first picture as being recalled.


  • Advertisement
  • Registered Users Posts: 4,745 ✭✭✭meercat


    2011 wrote: »


    I was referring to the type of switch fuse unit shown in the first picture as being recalled.

    have to say i didnt know there was a recall on that type of fuse unit


  • Posts: 0 [Deleted User]


    Something like this happened in my parents' house many years ago, probably 1995 or so. Their 50A fuse blew after they went overboard with heavy appliances one night. It was one of the screw cap types. My dad replaced it with a 63A fuse from his toolbox but then the following morning we got a very strong smell of burning plastic from the consumer unit, turned out it was because of the fuse.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    meercat wrote: »
    have to say i didnt know there was a recall on that type of fuse unit

    ...as far as I remember. It was just a particular make of the type shown.


  • Registered Users Posts: 4,745 ✭✭✭meercat


    2011 wrote: »
    ...as far as I remember. It was just a particular make of the type shown.

    i thought it was a slide in type with a cover that flipped up but didnt engage properly causing arching


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    2011 wrote: »
    An overload should not be possible.
    If this unit was fit for purpose (and properly installed) the fuse should operate before the unit can experience an overload condition.


    I was referring to the type of switch fuse unit shown in the first picture as being recalled.



    they do seem to burn out, rather than blow in some cases where the installation load is excessive


    this wouldn't be the case in more expensive units with hrc blade fuses


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    EEC D02 63A AC 22B
    Gould 5861.063 DO63A AC22
    Lindner 5861.063 DO 63A AC22
    NES UE 440V 63A
    REGIS OSLF 63 1P
    Hi 240V/415V-63A
    Hi DO2 63A 5.5W ac 22B


    i was looking for info on that-i think those are the affected ones

    jeez that was a major hype for registered contractors a good few years back

    don't think i was called back to any that actually caused trouble


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    M cebee wrote: »
    they do seem to burn out, rather than blow in some cases where the installation load is excessive

    Only if the unit is faulty or not fitted correctly.

    The design intent is that a fuse should blow before the current exceeds the rating of the fuse holder.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    M cebee wrote: »
    EEC D02 63A AC 22B
    Gould 5861.063 DO63A AC22
    Lindner 5861.063 DO 63A AC22
    NES UE 440V 63A
    REGIS OSLF 63 1P
    Hi 240V/415V-63A
    Hi DO2 63A 5.5W ac 22B


    i was looking for info on that-i think those are the affected ones

    jeez that was a major hype for registered contractors a good few years back

    don't think i was called back to any that actually caused trouble

    Yes, you are correct.
    Here is a link to it.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    2011 wrote: »
    Only if the unit is faulty or not fitted correctly.

    The design intent is that a fuse should blow before the current exceeds the rating of the fuse holder.

    not so sure about that ime


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    M cebee wrote: »
    not so sure about that ime

    There is little point in having an over current protective device that is prone to melting if it experiences an over current.

    Why do you think there was recall by Director of Consumer Affairs?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    Why do you think there was recall by Director of Consumer Affairs?
    Main switch fuses that are badly designed or have a problem, can likely burn out when well below the fuse rated current.

    It does not mean they are burning out only at the overloading stage, as if to indicate that this proves ones not involved in recalls, wont burn out when loaded at 60 or 70 amps.


  • Closed Accounts Posts: 14,158 ✭✭✭✭hufpc8w3adnk65


    I've replaced 3 of those types in 15/16 years and 2 of the hager type in the second pic.The hager ones are sturdier I think!more common you'd have too replace them as a result of a loose connection


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    An overload should not be possible.
    If this unit was fit for purpose (and properly installed) the fuse should operate before the unit can experience an overload condition.

    Yea if the switch fuse is fit for purpose, it shouldnt be possible to overheat due to overload, as long as the fuse is properly fitted.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    I've replaced 3 of those types in 15/16 years and 2 of the hager type in the second pic.The hager ones are sturdier I think!more common you'd have too replace them as a result of a loose connection

    Probably loose fuses is another main factor. Recalls are probably down to the fuse contact mechanism not working reliably.

    Once overheating starts, oxidation begins, likely making the problem worse, accelerating the failure process.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    the different types of neozed fuse unit should work reliably under overload conditions

    i'm not convinced they always do


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    the different types of neozed fuse unit should work reliably under overload conditions

    i'm not convinced they always do
    No id be doubtful myself if all switch fuse units continuously loaded at 70 amps for example, would reliable work for its expected lifespan, or very long at all.

    If it was loaded at 80 to 90 amps, the fuse would probably operate reasonable quickly. But at just over the fuse rating regularly, and sustained, a fair bit of heating would seem likely.

    If it is designed for 63 amp fuses and is supposed to be fit for that purpose, the housing should be rated for 100 amps or something of that sort possibly, as they could be overloaded well into the 80+ amps for sustained periods without the fuse going.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    Bruthal wrote: »
    If it is designed for 63 amp fuses and is supposed to be fit for that purpose, the housing should be rated for 100 amps or something of that sort possibly, as they could be overloaded well into the 80+ amps for sustained periods without the fuse going.
    Well put.

    The manufacture should to look at the fusing characteristics and design the switch fuse accordingly.

    If it could guaranteed that the unit would never experience an over current condition then it would be possible to argue that a switch fuse is not required in the first place.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    If it could guaranteed that the unit would never experience an over current condition then it would be possible to argue that a switch fuse is not required in the first place.

    The fuse/holder would be more to protect the busbars and link wires more so than itself really. But with 63 amp MCBs protecting the tails to the MCB board, the board itself would only seem to need a switch alright.

    If a new meter is staying beside the MCB board in an installation in a rewire these days, is the MCB required then? I thought it might only be a requirement when the meter goes out into an outside box, rules wise anyway.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    Bruthal wrote: »
    The fuse/holder would be more to protect the busbars and link wires more so than itself really. But with 63 amp MCBs protecting the tails to the MCB board, the board itself would only seem to need a switch alright.

    If a new meter is staying beside the MCB board in an installation in a rewire these days, is the MCB required then? I thought it might only be a requirement when the meter goes out into an outside box, rules wise anyway.

    -no i don't think you need to protect tails if main DB and meter are side by side



    if the main ocpd(10ka 63amp mcb) is fitted in the cabinet then i think a 'main isolating switch' should suffice in the main DB

    can't see the benefit of 2 63amp ocpd's in series unless i'm missing something obvious


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    Bruthal wrote: »
    The fuse/holder would be more to protect the busbars and link wires more so than itself really. But with 63 amp MCBs protecting the tails to the MCB board, the board itself would only seem to need a switch alright.
    Yes.

    If a new meter is staying beside the MCB board in an installation in a rewire these days, is the MCB required then?
    Not sure. I am not a fan of these MCBs TBH.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    M cebee wrote: »
    -no i don't think you need to protect tails if main DB and meter are side by side



    if the main ocpd(10ka 63amp mcb) is fitted in the cabinet then i think a 'main isolating switch' should suffice in the main DB

    can't see the benefit of 2 63amp ocpd's in series unless i'm missing something obvious

    The only benefit I see was you can completely disconnect the MCB board, and also possibly avoid operating the ESB cutout if there was a short.

    I was thinking it is a rule requirement only if out in an outside box alright, more than a couple of meters away.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    Bruthal wrote: »
    The main benefit I seen was you can completely disconnect the MCB board, and possibly avoid operating the ESB cutout if there was a short.
    Is there not an isolation switch on the ESB meters though?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    Not sure. I am not a fan of these MCBs TBH.

    No, nor am I to be honest.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    Is there not an isolation switch on the ESB meters though?

    Yes, so there is even less benefit to having them. Pointless really, apart from maybe avoiding blowing the main cutout fuse in a short.

    Not really worth the hassle.


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,593 Mod ✭✭✭✭2011


    Bruthal wrote: »
    Yes, so there is even less benefit to having them. Pointless really, apart from maybe avoiding blowing the main cutout fuse in a short.

    Even at that there is every chance that the cut out fuse would blow first if there was a short.
    Not really worth the hassle.

    Sometimes there just seems to be a policy to make up rules for the sake of being seen to do something.


Advertisement