Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

How to calculate BTU output?

  • 24-07-2013 12:46am
    #1
    Registered Users, Registered Users 2 Posts: 1,836 ✭✭✭


    I have worked out how to convert 50 delta to 60 delta so I can get the radiators on a level playing field. but now how to calculate the BTU... I ahve looked at 3 different online caluculators and they all come up with a different measurement for the same room

    e.g. 4 x 4 x 2.5 m3 room. One calcultors says 3338, another 4500, another 5200. Approx)

    What is the most accurate way?

    Thanks


Comments

  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    The 50 delta & 60 delta refers to the delta T & the 50 or 60 refers to the return temperature depending on the delta T.
    50 delta is referring to condensing boilers which require a delta T of 20 so if 70 being the flow temperature, you would end up with a return of 50. You will notice rad size being larger on the 50 than the 60 to give the 20 DT. On the 60 delta it is working of circa 10C DT so return of 60 from a flow temperature of 70. This would be for standard efficiency boilers.


  • Registered Users, Registered Users 2 Posts: 1,791 ✭✭✭LIFFY FISHING


    For years the rule was ; lenght x breath x height x 6 = your btu requirements & its as accurate as will ever be required and then crossreferance your figures against the rad charts.


  • Registered Users, Registered Users 2 Posts: 1,836 ✭✭✭tea and coffee


    Thanks Shane. Yes the European rads are in 50 delta and the sizes I need are bigger anyway as they arent as efficient a radiator.
    My issue now is trying to work out which actual radiator i need for which room. Every online calculator is giving me a different figure of btu needed to heat my room so I dont know which one to trust.
    They are all wildly different numbers.


  • Registered Users, Registered Users 2 Posts: 1,836 ✭✭✭tea and coffee


    Thanks LF. Some calculators were asking about dbl glazing, north facing walls, french doors and how warm do I like my house?!?!?!?!
    I will see what figures i get now using your method. Cheers


  • Registered Users, Registered Users 2 Posts: 7,516 ✭✭✭Outkast_IRE


    Thanks LF. Some calculators were asking about dbl glazing, north facing walls, french doors and how warm do I like my house?!?!?!?!
    I will see what figures i get now using your method. Cheers
    That's because a radiator is sized to cover the heat losses from that room, the amount of glazing, insulation etc etc makes a massive difference in the size of rad needed.