long power run

Options
  • 26-01-2014 8:17pm
    #1
    Registered Users Posts: 606 ✭✭✭


    Hi all,

    I have a shed that is approx 250m away from the main distribution board. Max load is going to be 20A..
    any ideas on a cost effective solution?!

    Cheers.


«1

Comments

  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    i doubt it for 250m at 20amps


    what's the loading comprised of?


  • Registered Users Posts: 378 ✭✭frankmul


    It's a vy long run. The voltdrop in the cable will cause the cable to be large.


  • Registered Users Posts: 606 ✭✭✭larthehar


    Load would comprise of 10 double fluorescent lights.. a 500w halogen.. I would be using a 2200w angle grinder and maybe an inverter welder.. obviously not all at the same time..
    if I had the lights it would be the most important element.
    so maybe 10A for this..
    16sq cable would probably do?

    Are transformers a viable option?


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    new supply from esbn

    cable for that would be prohibitively expensive


  • Registered Users Posts: 606 ✭✭✭larthehar


    new supply from esbn

    cable for that would be prohibitively expensive

    Surely €1200 euro would cover it? New connection would be €1.5-2k and standing charge on top of that..


  • Advertisement
  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    250m of 16sq is showing up as 1700 euro on meteor online

    and that will exceed the allowable voltage drop at 20amps


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    you'd prob need the 25 costing 2000 euro or more

    + 250m of trench


  • Registered Users Posts: 378 ✭✭frankmul


    Allowing 3% volt drop for the cable run, you have to use 35 mm sq for 20 amps!


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    frankmul wrote: »
    Allowing 3% volt drop for the cable run, you have to use 35 mm sq for 20 amps!
    Yes, aligns with my calculation.

    Here is what I get for XLPE armoured cable:

    Conductor Size, (mm^2) mV/A/m Design Current, (A) Length of Run, (m) Vlot Drop, (V) % Volt Drop
    1.5 29.00 20 250 145.0 63.0
    2.5 18.00 20 250 90.0 39.1
    4 11.00 20 250 55.0 23.9
    6 7.30 20 250 36.5 15.9
    10 4.40 20 250 22.0 9.6
    16 2.80 20 250 14.0 6.1
    25 1.75 20 250 8.8 3.8
    35 1.35 20 250 6.8 2.9

    Method of installation C, E, F, G.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    larthehar wrote: »
    Load would comprise of 10 double fluorescent lights.. a 500w halogen.

    Why?
    This does not make sense.
    Use more energy efficient lighting.
    if I had the lights it would be the most important element.
    so maybe 10A for this..

    So this is ½ of your design current? :eek::eek::eek:
    Are transformers a viable option?

    What do you plan to do with a transformer?


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »



    What do you plan to do with a transformer?

    Transform up to 10kv close to DB, 1.5 square to shed, 10kv back to 230v at shed. A couple of mini pylons for the 10kv run, and job done.*







    *Not a serious recomendation


  • Registered Users Posts: 606 ✭✭✭larthehar


    2011 wrote: »
    Why?
    This does not make sense.
    Use more energy efficient lighting.



    So this is ½ of your design current? :eek::eek::eek:



    What do you plan to do with a transformer?

    Ok.. so it is a shed used for agricultural purposes.. I would like to be able to do repairs/improvements requiring power tools but I can resort to the gene.. leaving only the lights..
    I will do some research into the most energy efficient lights... hence the drop to 10A..

    Out of curiosity, how much is 35mm sq cable per metre..

    Transformer I was considering stepping down to 110v..


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    larthehar wrote: »

    Transformer I was considering stepping down to 110v..

    If you step down to 110v for the cable run, it would be 70 square needed for the run:eek:


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    Bruthal wrote: »
    If you step down to 110v for the cable run, it would be 70 square needed for the run:eek:

    I think he means that he would like to use a 110V traffo in the shed for power tools. At least I hope that is what he means :)


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    I think he means that he would like to use a 110V traffo in the shed for power tools. At least I hope that is what he means :)

    That wont reduce the load anyway.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    Bruthal wrote: »
    That wont reduce the load anyway.

    I know, but I am guessing that it will suit the 110V power tools such as the aforementioned grinder :)


  • Registered Users Posts: 606 ✭✭✭larthehar


    Of course it is at the shed end I was considering the transformer.. allows more current draw...

    So no ideas on price of the 35sq cable?!


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    larthehar wrote: »
    Of course it is at the shed end I was considering the transformer.. allows more current draw...

    What do you mean "allows more current draw" ??
    So no ideas on price of the 35sq cable?!

    No idea.


  • Registered Users Posts: 1,111 ✭✭✭freddyuk


    larthehar wrote: »
    Ok.. so it is a shed used for agricultural purposes.. I would like to be able to do repairs/improvements requiring power tools but I can resort to the gene.. leaving only the lights..
    I will do some research into the most energy efficient lights... hence the drop to 10A..

    Out of curiosity, how much is 35mm sq cable per metre..

    Transformer I was considering stepping down to 110v..

    LED tubes are about 65% of the wattage of 240v florescent tubes. DC 12v/24v tubes are available depending on your daily usage you can run lights off Solar battery system and have genny as standby. As you may need genny anyway for short bursts of high power for the tools the solar option becomes quite viable for lighting which is low power and intermittent.
    Do the math on the cable option and go from there.


  • Registered Users Posts: 625 ✭✭✭E. Fudd


    Do like they do on the railway; step it up to 650vac and back down at the other end! (Again, not a serious recommendation)....


  • Advertisement
  • Closed Accounts Posts: 460 ✭✭Cogsy88


    2011 wrote: »
    Yes, aligns with my calculation.

    Here is what I get for XLPE armoured cable:

    Conductor Size, (mm^2) mV/A/m Design Current, (A) Length of Run, (m) Vlot Drop, (V) % Volt Drop
    1.5 29.00 20 250 145.0 63.0
    2.5 18.00 20 250 90.0 39.1
    4 11.00 20 250 55.0 23.9
    6 7.30 20 250 36.5 15.9
    10 4.40 20 250 22.0 9.6
    16 2.80 20 250 14.0 6.1
    25 1.75 20 250 8.8 3.8
    35 1.35 20 250 6.8 2.9

    Method of installation C, E, F, G.

    If 3% of 230v is 6.9 volts would 16sq cable not be within the regulations.


  • Banned (with Prison Access) Posts: 1,288 ✭✭✭sawdoubters


    why use so many lights get efficient ones ,your not using the power all the time,
    t5 fluorescents are good,
    T5 fluorescent lights use special ballasts – the device that limits the amount of current passing through the tube to stop it from overloading. Additionally, these special ballasts enable T5 fluorescent lights to work at frequencies above 20kHz, giving you features such as instant start, rapid start and programmed start


    the halogen you could swap with led spotlight,your grinder will use 10 amps but will only run a bit,put your lights on a few switches,you should only need 4 lights how big is the place,i would not worry about volt drop,you could run 2x20 amp circuits,you could run a 20 amp ring circuit 2.5mm don't forget rcd protection

    http://www.etci.ie/docs/ET214.pdf


  • Registered Users Posts: 2,637 ✭✭✭brightspark


    Cogsy88 wrote: »
    If 3% of 230v is 6.9 volts would 16sq cable not be within the regulations.

    Regulation 525.2 allows 4% so 9.2V allowed.

    Regardless 25sq is needed according to 2011's table


  • Closed Accounts Posts: 460 ✭✭Cogsy88


    So y is everybody saying 35sq?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    the halogen you could swap with led spotlight

    Yes, more efficient lighting has already been suggested.
    your grinder will use 10 amps but will only run a bit
    True, but a large volt drop will mean that it will be seriously lacking in power.
    i would not worry about volt drop
    You should, it can cause a lot of problems.

    In addition high volt drop can will also mean a high earth fault loop impedance.
    you could run 2x20 amp circuits

    It is expensive enough running one 20A circuit !
    Why are you suggesting running a 2nd? :confused:
    you could run a 20 amp ring circuit 2.5mm don't forget rcd protection
    250m on a 2.5 sq. mm cable is a volt drop of 90 volts. So if it was wired in ring this would reduce to 45 volts :eek:
    Not good!


  • Registered Users Posts: 9,605 ✭✭✭gctest50


    Cogsy88 wrote: »
    So y is everybody saying 35sq?

    Cos saggy power isn't nice when you're welding ?

    Lights go a bit dim / fluctuate esp. if you like cutting rods etc


  • Closed Accounts Posts: 460 ✭✭Cogsy88


    Am I missing something in the regs. Is there different voltage drop aliowences for different cable installation methods?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    Cogsy88 wrote: »
    So y is everybody saying 35sq?

    You need to look at the overall volt drop and ensure that this is not excessive.

    This will mean adding the following volt drops:
    1) Volt drop to the main distribution board.
    2) Volt drop from the main distribution board to the shed.
    3) Volt drop on the final circuit in the shed.


  • Closed Accounts Posts: 460 ✭✭Cogsy88


    gctest50 wrote: »
    Cos saggy power isn't nice when you're welding ?

    Lights go a bit dim / fluctuate esp. if you like cutting rods etc

    What about a 16sq supply and wire lights in 2.5 and sockets in 4sq.


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    Cogsy88 wrote: »
    Is there different voltage drop aliowences for different cable installation methods?

    Yes.
    Have a look on pages 289 to 292, Annex 52E.

    Different installation methods can effect how easily a cable can cool.
    The hotter a copper conductor is, the higher the resistance, the higher the volt drop for a given current.