  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    Cogsy88 wrote: »
    What about a 16sq supply and wire lights in 2.5 and sockets in 4sq.

    The volt drop on the 16 sq. mm cable alone will be excessive (if you take a design current of 20A).

    The solution is either:
    1) Lower the design current - Consider energy efficient lighting.
    2) Larger cable - Expensive
    3) Shorter run - Different cable routing perhaps? Or move the shed?


  • Closed Accounts Posts: 460 ✭✭Cogsy88


    Sorry man read your calculations table wrong (Must book an eye test). So would have to be at least 25 but 35sq would be ideal but expensive.

    Maybe a generator would be his best bet.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    Cogsy88 wrote: »
    Sorry man read your calculations table wrong

    No problem.


  • Registered Users Posts: 9,605 ✭✭✭gctest50


    Cogsy88 wrote: »
    What about a 16sq supply and wire lights in 2.5 and sockets in 4sq.

    It might draw about 8 to 9 k ? be like someone turning on and off a small shower


  • Closed Accounts Posts: 460 ✭✭Cogsy88


    Does anybody have any estimates on what the esb would charge him for a supply into the shed?