Fire Alarm installation query

Options
  • 21-02-2014 7:12pm
    #1
    Registered Users Posts: 4,076 ✭✭✭


    295171.JPG
    295173.jpg


    Could I get some comments on the fire alarm panel installation as per the attached photos. (I've edited out the installer name on the panel photo)
    Should the Fire Alarm have its own RCD on the circuit board, marked as such.
    It would appear that it's more than likely powered off the socket circuit.
    BTW, this is an installation under 6 months old.
    Would it fall under IS3218:2009 or is the IS3218:2013 the standard it would need to be under.
    I'm under the belief that the Fire alarm system needs to have a certified design, Fire risk assessment carried out prior to installation?
    I would welcome some guidance and/or links to relevant legislation/ guidelines etc.


Comments

  • Banned (with Prison Access) Posts: 509 ✭✭✭bertie1


    You have not said what type of building it is. Is it in an apartment block & if so it is most likely off the landlords supply?

    The building if it is apartment of some sort should have a fire cert. When you say it was installed 6 months ago , is it a replacement job or brand new?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    For a start the fire alarm should not be fed from an RCD.
    It should be on a dedicated circuit.


  • Registered Users Posts: 4,076 ✭✭✭gman2k


    bertie1 wrote: »
    You have not said what type of building it is. Is it in an apartment block & if so it is most likely off the landlords supply?

    The building if it is apartment of some sort should have a fire cert. When you say it was installed 6 months ago , is it a replacement job or brand new?

    It's rented accommodation.
    A renovated two story building, kitchen living and bathrooms at GF,
    With 2no. rooms at first floor level- One room is a bedroom for the person being cared for, the other room is a bedroom/ office for the staff.
    In essence a stand alone dwelling.
    The tenant is a care organisation, who then home one person under their care on the property, and the building is staffed with 1-3 staff (one at night on a sleeping basis).


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    it should be dedicated circuit (no rcd)anyhow... which it doesn't look to be

    it shouldn't be spur off lights or sockets circuit


  • Registered Users Posts: 4,076 ✭✭✭gman2k


    2011 wrote: »
    For a start the fire alarm should not be fed from an RCD.
    It should be on a dedicated circuit.

    Thank you. Should this dedicated circuit be marked on the board? How would I recognise it?
    All the other circuits are clearly labeled, so I presume the fire panel is fed off one of the as is!


  • Advertisement
  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    an mcb marked fire alarm


  • Registered Users Posts: 4,076 ✭✭✭gman2k


    an mcb marked fire alarm

    Thank you Tom.
    Since this marked MCB is missing from this board, what regulation/ standard can I say the installation is in contravention of?


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    gman2k wrote: »

    I would welcome some guidance and/or links to relevant legislation/ guidelines etc.


    Have you an official fire certificate of commissioning for this installation?


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    gman2k wrote: »
    Thank you Tom.
    Since this marked MCB is missing from this board, what regulation/ standard can I say the installation is in contravention of?

    ET101: 2008 563.1

    "circuits of safety services shall be independent of other circuits"


  • Registered Users Posts: 4,076 ✭✭✭gman2k


    From the manufacturers installations instructions -

    "Mains wiring
    The requirement for the Mains supply to the fire panel is fixed wiring, using three core cable (no less than 1mm2 and no more than 2.5mm2) or a suitable three conductor system, fed from an isolating switched fused spur, fused at 3A. This should be secure from unauthorised operation and be marked ‘FIRE ALARM: DO NOT SWITCH OFF’. The Mains supply must be exclusive to the fire panel.
    (As an alternative to a switched fused spur, a double pole isolating device may be used providing it meets the appropriate national wiring regulations - see diagram below.)"
    (I've not linked the diag referenced)

    So does the above mean that you should not not spur off a lighting or socket circuit?
    Sorry for all the questions, I'm not an elec, although I have a construction background!


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    Tomdempsey has quoted the relevant regulation in his last post.


  • Registered Users Posts: 4,076 ✭✭✭gman2k


    2011 wrote: »
    Tomdempsey has quoted the relevant regulation in his last post.

    Thanks 2011 & Tom for your patient help:)
    To wrap it it, I presume I should just test the existing circuits one by one at the board and switch them off. The one that sets off the fire panel will let me know for sure.
    Thanks again.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    gman2k wrote: »
    The one that sets off the fire panel will let me know for sure.

    I bet the first one on the top row will isolate it ;)


  • Registered Users Posts: 4,076 ✭✭✭gman2k


    WikiHow wrote: »
    I bet the first one on the top row will isolate it ;)

    It's wired into the lighting circuit....


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    gman2k wrote: »
    It's wired into the lighting circuit....

    not great

    the etci rules cover that issue


    the actual fire alarm installation will be covered by the IS 3218 standard

    the last few systems i wired i had them designed and commisioned separately

    i wonder is joe bloggs electrician allowed to work on systems anymore without specific standards training


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,594 Mod ✭✭✭✭2011


    i wonder is joe bloggs electrician allowed to work on systems anymore without specific standards training

    It is only the designer of the fire alarm system and the certifier that needs to be up to speed with the standards.

    Specialist fire alarm companies frequently employ the services of electrical contractors that would not have specific fire alarm training.