cable glanding

Options
  • 11-04-2014 9:08pm
    #1
    Registered Users Posts: 1,051 ✭✭✭


    What's the better practice or the norm? When cable glanding into a panel or trucking header i usually place the earth ring (banjo) on the outside with a bolt. Recently in a large MV switch room I've seen 3 types. Banjo on the inside with bolt and linked out with others in 10/6mm^2 down to the earth bar (not very tidy at all)

    I only ask because were fitting a new panel i like to keep some sort of pattern. If it was painted id most likely link them out?


Comments

  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    if I was glanding swa into galvanised steel I'd stick the banjo on the inside... no earth flylead needed I would say

    painted metal and the like I'd use a flylead.... not too sure about linking them up?

    pvc panels... banjo and flylead inside


  • Registered Users Posts: 1,051 ✭✭✭Tuco88


    if I was glanding swa into galvanised steel I'd stick the banjo on the inside... no earth flylead needed I would say

    painted metal and the like I'd use a flylead.... not too sure about linking them up?

    pvc panels... banjo and flylead inside

    Cheers tom, honestly the switch room is very poorly done early 90s. Its a large chemical plant, is it normal practice to use flyleads on each. There all lined in one and 1 fly lead down to the bar but its very messy. I was told that the banjos were to go outside for inspection on metal surfaces?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    I put them outside anyway. Better contact with the glands as well.


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    Bruthal wrote: »
    I put them outside anyway. Better contact with the glands as well.

    yes I think i was wrong there