Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Changing pull shower switch

Options
  • 22-04-2014 8:10pm
    #1
    Registered Users Posts: 45


    I am changing a shower double pole pull switch but I am not sure of the wiring, the old one uses L1 and L2 for the two live wires. On the new switch it is marked Supply and Load, Question: does L1 go to the Supply or Load live contacts?
    Any advice would be appreciated


Comments

  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    bigears1 wrote: »
    I am changing a shower double pole pull switch but I am not sure of the wiring, the old one uses L1 and L2 for the two live wires. On the new switch it is marked Supply and Load, Question: does L1 go to the Supply or Load live contacts?
    Any advice would be appreciated

    If L1 was correctly the supply cable on the old switch, it goes to supply on the new switch.

    If you have the cable into the wrong side, the neon light will simply stay on all the time.

    As would usually be said here, its not as simple to do properly as people think. And that is besides getting the cable into the correct terminals.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Bruthal wrote: »

    If you have the cable into the wrong side, the neon light will simply stay on all the time.

    Unless the neutrals get mixed up. :)


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Unless the neutrals get mixed up. :)

    It might possibly still stay on then as well, just dimmer, with the pullchord off, since the second leg of the neon will be a floating connection to the isolated shower, enough to light it dimly with the other leg of the neon connected to the Live continuously.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Bruthal wrote: »
    since the second leg of the neon will be a floating connection to the isolated shower

    Why are you referring it to as a floating connection?


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Did you mean that the neutral from the neon has a floating ground?


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Did you mean that the neutral from the neon has a floating ground?

    When the pull chord is switched off, the shower neutral from pull chord to shower, is now a floating conductor connected to nothing except the shower, so the shower and its live and neutral wires are all isolated, so are floating in terms of the neon connected to it.

    So the neon with one leg connected to live from feed being connected to the load terminal, and the other leg of neon now connected to the load neutral if neutrals are mixed up. So the leg of the neon connected to the shower neutral is connected to an isolated shower unit.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Bruthal wrote: »
    So the leg of the neon connected to the shower neutral is connected to an isolated shower unit.

    I would call that a floating ground.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    I would call that a floating ground.

    Why?

    Its academic anyway. Its a floating connection, or a floating ground. Not really that important to argue over it.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Bruthal wrote: »
    Why?

    Its a floating connection.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Bruthal wrote: »

    Its academic anyway. Its a floating connection, or a floating ground. Not really that important to argue over it.

    True.


  • Advertisement
  • Registered Users Posts: 10,024 ✭✭✭✭dodzy


    OP asked a simple question. Why the need for 11 posts ??

    Supply = side from where the power comes
    Load = Side to the device that requires the power ( the shower in this case )

    Obviously OP, you will need to isolate the power from the consumer unit. Following that, is is not nearly as difficult as some would have you believe.


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    dodzy wrote: »

    Obviously OP, you will need to isolate the power from the consumer unit. Following that, is is not nearly as difficult as some would have you believe.

    except for the fact that the OP appears to have no training or experience

    i'm sure FAS wouldn't recommend apprentices be sent out out to replace shower pull cord switches on their first day at work


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    dodzy wrote: »
    OP asked a simple question. Why the need for 11 posts ??

    If the op is unsure about his phase connections one can deduce he is equally unsure where to put the neutral connections, gauging that the light on in the switch if wired incorrectly would not be an approved method of knowing that your switch would be wired backwards correctly.
    The switch can be potentially wired 24 different ways yet only one way is the correct way.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    dodzy wrote: »
    OP asked a simple question. Why the need for 11 posts ??

    OP got a simple answer in post #2. They should have mod application forms for posters like yourself.


  • Registered Users Posts: 10,024 ✭✭✭✭dodzy


    Not taking away from the safety aspect, but you are over complicating this. OP simply asked about SUPPLY and LOAD as the existing switch was L1 and L2. I think it's fair to assume that the OP will see two cable groups going into the existing switch. The close proximity to the shower will easily indicate which cable group are going to the shower (Load), leaving the other group being the (supply)

    Given the likely colour coding of the cable insulation, it really is not that complex a task. Surely you could not dispute this?

    And your "mod application" remark is childish, but I'm sure you know that.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    dodzy wrote: »
    The close proximity to the shower will easily indicate which cable group are going to the shower (Load), leaving the other group being the (supply)

    Are you saying that you can deduce that the cable in the ceiling closest to the shower is the switch wire (load) ?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    dodzy wrote: »
    Not taking away from the safety aspect, but you are over complicating this.
    You are reading too much into it. Have a read of post #2 and tell me if you think its complex.

    The following posts were a discussion, you know, it happens sometimes.
    Given the likely colour coding of the cable insulation, it really is not that complex a task. Surely you could not dispute this?
    Point out where I said fitting a shower switch was complex.

    Dont forget though, not complex does not always = simple. Shower switches can be a nuisance even for experienced people to fit. You never experienced simple tasks that become horrendous awkward im guessing though.

    And your "mod application" remark is childish
    You seem bothered by 2 posters posting a bit of banter, complaining the OP asked a simple question, yet the question was answered in the first reply. You then answer it again, while complaining the thread has too many posts.


  • Registered Users Posts: 10,024 ✭✭✭✭dodzy


    Are you saying that you can deduce that the cable in the ceiling closest to the shower is the switch wire (load) ?
    No, I'm saying that the cable which runs from the pull cord switch to the shower will be the load wire. Establishing this fact is made even simpler if the shower is upstairs in a 2 story dwelling with no attic conversion. My money is on this being the case in the majority of situations.

    Look, I'm not disputing either your knowledge or that of Bruthal. I'm well aware that you both contribute greatly around various fora on boards.ie, but it would be nice for once if the OP was not assumed as incapable.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    dodzy wrote: »
    No, I'm saying that the cable which runs from the pull cord switch to the shower will be the load wire.

    Im not disagreeing with you there.
    Establishing this fact is made even simpler if the shower is upstairs in a 2 story dwelling with no attic conversion.

    As in if the wiring is on surface visible from the shower to the switch?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    dodzy wrote: »
    but it would be nice for once if the OP was not assumed as incapable.

    Thats fair enough, but as said, I had given a simple outline in post 2. After that myself and arthur just had a bit of banter, which was not making any reference to the abilities of the OP.

    It was described how the neon would indicate a correctly wired switch and all in post 2.


  • Advertisement
Advertisement