LED lighting circuits Breaker type

Options
  • 23-09-2014 10:47am
    #1
    Registered Users Posts: 10,952 ✭✭✭✭


    Has anyone notice an increase in the amount of LED strip fittings tripping type B and even Type C MCBs.

    We've seen it on a couple of jobs where after a period of time (not on initial inrush current) the MCBs are tripping.

    Have you guys seen this, these are not cheap fitting either,



    Type B devices are designed to trip at fault currents of 3-5 times rated current
    Type C devices are designed to trip at 5-10 times
    Type D devices are designed to trip at 10-20 times

    The loop impedance test would need to be carried out again when moving from B to C to D


Comments

  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    What is the prognosis on the tripping, overload or short circuiting? Often good products have their flaws.


  • Registered Users Posts: 566 ✭✭✭adrian92


    Possibly due to the presence of harmonic currents . I am speculating - I do not even know if MCBs only sensitive to 50 Hz. Just a thought.


  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    adrian92 wrote: »
    Possibly due to the presence of harmonic currents . I am speculating - I do not even know if MCBs only sensitive to 50 Hz. Just a thought.

    i think mcbs are sensitive to harmonic currents


  • Posts: 5,238 ✭✭✭ [Deleted User]


    I've run them on DC MCB's to the driver, no transformer, no problem.


  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    I've run them on DC MCB's to the driver, no transformer, no problem.

    aren't the drivers fed from the mains?
    http://www.meteorelectrical.com/36w-driver-for-led-under-cabinet-strip-light.html

    where does the DC mcb fit into that scenario?


  • Advertisement
  • Posts: 5,238 ✭✭✭ [Deleted User]


    That's a power supply not a driver, the driver is the PWM dimming unit.

    images?q=tbn:ANd9GcR0T74Ukwz08kZSUcaCfcIQZ8ackaOMAZQQi5CtOjw8T0cHc9k-OQ

    Mine are 12VDC-24VDC. I don't have mains. So Batteries -> DC MCB -> driver -> strip lights.

    The usual setup is Mains -> MCB-> AC-DC 12V/24V switch mode power supply -> driver -> strip lights.

    Then they've isolated data control for colour mixing.


  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    no bother

    i thought they would be all one


    electronic power supply and driver


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,595 Mod ✭✭✭✭2011


    adrian92 wrote: »
    Possibly due to the presence of harmonic currents

    Yes, I was thinking this myself.
    Harmonics distortion can be caused by nonlinear loads such as VSDs or UPS.
    I rang Stoner & suggested this to him, but he explained that these types of loads are not present in this installation.
    We both concluded that this issue is most likely the LED driver.

    A bit of Goggling and I found the following:

    Issues caused by harmonic distortion include:
    ● Erratic operation of breakers and relays.
    ● Overheating in neutral conductors, transformers and motors.
    ● Deterioration or failure of power factor correction capacitors.
    ● Pronounced magnetic fields local to transformers and switchgear.
    ● Problems with microprocessor-based equipment.

    I saw a power factor correction (PFC) unit go on fire in a plant recently because multiple DOL motors (over time) were replaced with VSD fed motors. The VSDs caused harmonic issues which in turn caused the PFC to overheat. We had to replace the burnt out unit with a new "detuned" version. These are designed specifically to work with nonlinear loads.


  • Moderators, Recreation & Hobbies Moderators Posts: 10,435 Mod ✭✭✭✭Mr Magnolia


    2011 wrote: »
    I saw a power factor correction (PFC) unit go on fire in a plant recently because multiple DOL motors (over time) were replaced with VSD fed motors. The VSDs caused harmonic issues which in turn caused the PFC to overheat. We had to replace the burnt out unit with a new "detuned" version. These are designed specifically to work with nonlinear loads.

    I've heard of this happen myself. What brand of VSD were they?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,595 Mod ✭✭✭✭2011


    I've heard of this happen myself. What brand of VSD were they?

    Mainly ABB but also some older Loher units.
    In addition there are a lot of UPS.


  • Advertisement
  • Registered Users Posts: 1,136 ✭✭✭maxamillius


    That's interesting,we have 2 Pfc units in our building one of such went on fire a month ago,capacitor blew in it!we had about 10 vsds installed in the building last year for the ahu's,wonder did that have an effect?or is a year to long to keep it as a valid reason?


  • Registered Users Posts: 10,952 ✭✭✭✭Stoner


    we are going to plot the load over a few days, I'll get back with the results, overall we are not happy with the response the suppliers have been giving us on it, very wishy washy.