Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

cable size from meter to consumer Unit?

Options
  • 23-09-2014 10:18pm
    #1
    Registered Users Posts: 42


    Has there been a change in the regs on the size of the cable from the meter box to the consumer Unit. Heard someone say it has to be 25mm square now. Anyone know if this is the Case?


Comments

  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    i dont think there's been any change for 12kva

    i've used 25s and 80amp main ocpd with the the enhanced 16kva


  • Registered Users Posts: 42 eoin8


    i dont think there's been any change for 12kva

    i've used 25s and 80amp main ocpd with the the enhanced 16kva

    Thanks, mine will be a 16kva supply, as we will be installing a heat pump. I thought it would still be 16 square but maybe it would be best to uprate it.


  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    for 16kva nightsaver with heat pump

    i would fit 80 amp main ocpd in meter cabinet and 25sq tails


    that's the way i did them anyhow


    you're not making use of the higher capacity that you applied for if you fity 16sq and 63amp


Advertisement