    Lads,

    Where is best place that I could buy 300m 16z armoured cable & deliver to cork?


Comments

  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    grange mac wrote: »
    Lads,

    Where is best place that I could buy 300m 16z armoured cable & deliver to cork?

    do you mean 300m 16sq 3 core?

    What's it for?


  • Registered Users Posts: 878 ✭✭✭grange mac


    do you mean 300m 16sq 3 core?

    What's it for?

    Replacing wiring to a shed.


  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    grange mac wrote: »
    Replacing wiring to a shed.
    You'd price around all of that for that amount of cable
    Make sure you get from a reputable supplier

    Any of the wholesalers would deliver

    16sq is big money seems to be up around 7/8euro a meter if I'm not mistaken

    Have you calculated your cable size and explored other options such as new connection?


  • Registered Users Posts: 878 ✭✭✭grange mac


    You'd price around all of that for that amount of cable
    Make sure you get from a reputable supplier

    Any of the wholesalers would deliver

    16sq is big money seems to be up around 7/8euro a meter if I'm not mistaken

    Have you calculated your cable size and explored other options such as new connection?

    Would have gone down new connection road only low usage charge makes it viable as low power usage. But at moment served by 2.5 which putting it mildly is v dangerous due to long draw. So looking at better option at best price.


  • Registered Users Posts: 842 ✭✭✭65535


    You could try dwyers electrical up the airport road (forge hill)
    They should have what you are looking for


  • Advertisement
  • Registered Users Posts: 566 ✭✭✭adrian92


    16 sqmm. I assume that you are using this size for voltage drop reasons, given the distance. Is it necessary, I wonder, to have to use such a large cross sectional diameter?


  • Registered Users Posts: 378 ✭✭frankmul


    adrian92 wrote: »
    16 sqmm. I assume that you are using this size for voltage drop reasons, given the distance. Is it necessary, I wonder, to have to use such a large cross sectional diameter?

    The voltdrop for 10 amps is over 7 volts for 300 meters. That only leaves about 2 volts for either side of the cable?


  • Registered Users Posts: 566 ✭✭✭adrian92


    Point taken Frankmul. Yes, even with the proposed cable only about 2kW possible in the shed.


  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    crazy money for a 10 amp supply


  • Registered Users Posts: 707 ✭✭✭jeepers101


    crazy money for a 10 amp supply

    Crazy distance in fairness


  • Advertisement
  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    jeepers101 wrote: »
    Crazy distance in fairness

    it's too far with the price of cable now

    if it was just for lighting and you could use a smaller cable maybe


  • Registered Users Posts: 878 ✭✭✭grange mac


    it's too far with the price of cable now

    if it was just for lighting and you could use a smaller cable maybe
    Not a good idea as voltage drop too much on 2.5 wire


  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    grange mac wrote: »
    Not a good idea as voltage drop too much on 2.5 wire

    bigger than 2.5 smaller than 16


  • Registered Users Posts: 878 ✭✭✭grange mac


    bigger than 2.5 smaller than 16


    Sparky came out told me if want future proof do once and right so 16mm required


  • Banned (with Prison Access) Posts: 700 ✭✭✭mikeyjames9


    grange mac wrote: »
    Sparky came out told me if want future proof do once and right so 16mm required

    I was referring to lighting only ,it may have been possible to calculate something slightly smaller

    even 16sq is undersized for lighting and power